Cyberpower 1500AVR UPS repair
  • quickname
    • Nov 2023
    • 3
    I'd like to start out by thanking this forum for providing the info to be able to repair my 15 year old CP1500AVRLCD UPS. Here is all the info I gathered during my trouble-shooting and re-capping.
    Like clockwork, I've had to replace the SLA batteries every 4 years. It was about that time and the UPS was acting like it needed new batteries... randomly shutting off with AC present, not being able to charge fully, and poor runtime when AC was removed. So, I replaced the batteries but noticed that it was not charging properly.
    I decided to verify that the batteries were okay. So, I removed them and charged them individually and used a DC electronic load to test their capacity. They were 7.6-7.9Ah and 6.9-7.1Ah across several cycles at a 0.05C discharge rate to an 11V cutoff. They're rated as 9Ah but since they were cheap and I was testing them at about 65 degF it seemed fine. I also tested them at 0.5C discharge and saw 5.4 and 5.9Ah of capacity which was within expectations.
    I then stumbled upon this forum and found very helpful threads such as
    https://www.badcaps.net/forum/showth...ght=cyberpower
    and
    Upon inspection I did not notice any leaking capacitors or burned ICs. However, since the successful repairs focused on the recharging circuit and my device was not charging properly I though I'd see if I could confirm my device's issue.
    I connected a PSU to the battery connection terminals (without a battery present). With the AC cord disconnected I supplied 25V and the UPS was able to turn on. The UPS was drawing 0.71A from the PSU but there must have been a very large variation in the current draw because the PSU was voltage limiting and reporting an average output voltage about 0.5V below the setpoint even though the current limit was set to 5A. An AC voltage reading at the battery terminals reported 0.67Vrms. This confirmed that the current draw was very irregular. I didn't bother checking it out on a scope.
    Next, I attached the DC electronic load in parallel with the PSU and set it to draw 0.5A. The PSU happily supplied this extra current. I then plugged in the AC cord of the UPS and was expecting to see the PSU load current decrease as both the UPS would switch to AC and the charging circuit would attempt to charge the "batteries". If the charging circuit supplied more current than my load was set to I would expect the voltage to float up above the PSU's 25V setting. If it could not, I expected by be able to lower the DC load current and at some point the voltage would go above 25V.
    Once plugged into AC I did not observe any charging current and the PSU still had to supply 0.2-0.3A or else the unit would turn off. This confirmed to me that the charging circuit was not functioning.
    Based on the posts mentioned earlier, the first thing I did was desolder C1 and C3 and measure them with my LCR meter. They pretty obviously needed replacement. I also validated that U2 phototransistor was okay. It had a forward diode voltage of 1.05V on the side away from the board corner and the resistance of the other side was high by itself and about 1K when the other side was forward biased by my other multimeter. I purchased a replacement for U3 (Viper22A) but only planned to replace it if all the other changes failed since it seemed fine (no shorts between terminals with a meter). I desoldered the shunt voltage reference U1 and attempted to measure its expected reverse breakdown of 2.5V with the cathode and reference pins tied together and was unsuccessful so I added it to my list of parts to replace. The exact part was not available so I just chose one of the many other TL431* choices with 0.5% tolerance.
    Since the C1 and C3 capacitors were bad I decided to desolder and document the dimensions and type of all of the electrolytic caps as show below.
    Capactor Series Observed
    Su'scon SK Standard 105C 2000hr (Black)
    Su'scon SD Low Impedance 105C 2000hr (Brown)
    Su'scon MK One rank smaller than SK 105C 2000hr (Black)
    Refs; uF, V, SxDxH(mm), Series, Ripple+ESR Rating
    C1,10,12,18,19,22,23; 22u, 50V 2.5x5x10, SK, 83mArms @ 120Hz
    C3,6; 33u, 200V 5x10x20, MK, 157mArms @ 120Hz
    C2,14; 33u, 100V 5x10x17, SD, 450mArms 0.46Ohm @ 100KHz
    C8; 470u, 50V, 5x13x21, SD, 1.45mArms 0.09Ohm @ 100KHz
    C9; 47u, 63V 3.5x8x11, SK, 163mArms @ 120Hz
    C20; 1.0u, 50V, 2.5x5x10, SK, 15mArms @ 120Hz
    C21; 0.22u, 50V, 2.5x5x10, SK, 11mArms @ 120Hz
    FYI the dimensions are listed as lead-spacing x diameter x height. Most of these capacitors have no space to support a larger diameter substitution. All of these caps can safely support taller capacitors.
    Removing and measuring all of these caps gave the following results. Rather than tan-delta, dissipation factor, or ESR I am reporting the phase angle. A perfect capacitor would be -90 degrees but, depending on the capacitor value, lower readings at 10kHz are normal.
    Ref, uF, @10KHz, @1kHz, Condition
    C1, 22, bad, 11.1u -21deg, BAD
    C3, 33, 19.9u -20deg, 26.9u -66deg, BAD
    C6, 33, 13.9u -14deg, 23.1u -50deg, BAD
    C2, 33, 29.3u -52deg, 30.9 -83deg, GOOD
    C14, 33, 29.8u -55deg, 31.2 -84deg, GOOD
    C8, 470, NA, 356u -51deg, BAD
    C9, 47, 40.5u -38deg, 43.6u -80deg, GOOD
    C10, 22, 12.6u -33deg, 16.6u -73deg, BAD
    C12, 22, 12.9u -36deg, 16.8u -74deg, BAD
    C18, 22, 0.63u -18deg, 0.50u -24deg, BAD
    C19, 22, 10.4u -24deg, 15.8u -65deg, BAD
    C20, 1.0, 0.40u -43deg, 0.52u -71deg, BAD
    C21, 0.22, 0.18u -83deg, 0.20u -86deg, GOOD
    C22, 22, 6.5u -19deg, 13.0 -51deg, BAD
    C23, 22, 2.3u -18deg, 6.6u -33deg, BAD
    Ultimately, I replaced all of them based on their age. The following parts were purchased and installed. I was able to find cost effective replacements that met the specs of the original parts but had significantly higher lifetime ratings at 105C.
    Ref, Qty, $/ea
    C3,6, 2, 0.86 https://www.digikey.com/en/products/...E2D330/1245959
    Chose long-life, high ripple rating even though original was General Purpose (almost no cost difference)
    C2,14
    2, 0.64 https://www.digikey.com/en/products/...2A330B/9597100
    5x8x13mm rather than 5x10x17 of original (smaller diameter is fine). Even at 160V rating I did not find
    an in-stock cap that met the ripple rating and had low enough ESR for 10mm diameter.
    490mArms @ 100Khz exceeds original and 0.16ohm ESR is much better
    C8, 1, 0.82 https://www.digikey.com/en/products/...2-5X20/3564059
    22mm tall, long life high ripple
    C9, 1, 0.35 https://www.digikey.com/en/products/...774002/5727468
    C1,10,12,19,22,23
    7, 0.21@10 https://www.digikey.com/en/products/...15X11/11312828
    12.5mm tall rather than 10mm of original, 10000hr@105C
    C20, 1, 0.14 https://www.digikey.com/en/products/...672002/5727810
    12.5mm tall rather than 10mm of original 4000hr@105C
    C21, 1, 0.28 https://www.digikey.com/en/products/...MDD1TD/4342067
    Could only find an "obsolete" part
    U1, 1, 0.42 https://www.digikey.com/en/products/...AplgMYogC6AvkA
    After installing these parts, I performed similar testing to what I described before. With the AC removed, the PSU only had to supply 0.5A at 25V. There was no current limiting or noisyness observed like before and the voltage at the battery terminals had only 0.045Vrms of AC content.
    Then, I attached the DC electronic load in parallel and plugged in the AC to determine the battery charging capability. By changing the electronic load current and then adjusting the PSU voltage until it was just low enough that it didn't need to supply any current I captured the IV curve of the charging.
    Charging current versus output voltage
    A V
    0.02 27.25
    0.10 27.14
    0.20 27.01
    0.30 26.77
    0.40 26.10
    0.42 25.50
    0.44 25.00
    0.45 24.50
    This provides a 0.05C initial charge rate which then tapers off to become a trickle charge at about 13.65V per SLA battery.
    So, everything seemed to be working perfectly and there was no need to replace U3 in my instance.
  • quickname
    • Nov 2023
    • 3
    Re: Cyberpower 1500AVR UPS repair
    The time window to edit seems to have passed so here is a correction to a typo
    C8 470u 50V 5x13x21 SD 1.45Arms 0.09Ohm @ 100KHz
      Texas Instruments bq24745 bq24745RHDR bq24745RHDT Battery Charger IC for Laptop Computers Datasheet
      The bq24745 bq24745RHDR bq24745RHDT is a high-efficiency, synchronous battery charger with an integrated input-current comparator, offering low component count for space-constrained, multi-chemistry battery-charging applications. The input-current, charge-current, and charge-voltage DACs allow very high regulation accuracies that can be easily programmed by the system power-management microcontroller using the SMBus interface. The bq24745 charges two, three, or four series Li+ cells, and is available in a 28-pin, 5-mm x 5 mm QFN package.
      The bq24745 features dynamic power management...
      10-23-2024, 02:50 AM
      Is there any high current pouch battery that are size 60mmX80mm maximum thickness 21mm for a battery operated tab welder
      by sam_sam_sam
      I have a battery operated tab welder and the battery does not have enough current for the battery tab welder because after about 30 welded it does not have the same current output it voltage has gone down by at least 0.500 volts or maybe a more than that
      I can fit 21700 battery cells in the enclosure it is very tight fit for four of them that are 35 amp high current capacity 35X4=140 high current output this should work a lot better than what is installed right now
      I tested the battery cells there are installed right now and they are testing good with no issues that I...
      02-04-2025, 08:08 PM
    • pete_c
      CyberPower 1350AVR and 1500AVR - Repair
      by pete_c
      Both are older than years old now.
      Pooling info here from what I have read.
      Cyberpower 1500AVR takes 4-5 days to charge batteries after test depletion.
      Made an RPi Nutserver for the rack and using PFSense for the telco area with an APC.
      Using Nutserver with Home Assistant.
      Last week ordered
      33uF 200v Rubycon Electrolytic Radial Lead Capacitors
      22UF 50V Electrolytic Radial Lead Capacitors
      VIPer22A "Original" ST 8P DIP IC 2 pcs
      Noticed that the old Cyberpower UPS's output...
      05-06-2022, 04:10 PM
    • AJ847.63e
      Testing ATX PSUs under load - Does loading the ATX 24 pin also load EPS & PCIE?
      by AJ847.63e
      Hi Folks,
      Just wanted to clear up a misunderstanding of mine (or what I expect is one). Isn't the 12V rail from the 24 pin, EPS and PCIE separated? IE if I put a power resistor on the ATX 12V pin that is not going to load, thus tell me if the EPS or PCIE rails are fine?
      I was recently watching ArIs from Hardware Busters video on how to properly test ATX PSUs without using 5 figure Croma substations.
      The PCB adapter he used breaks out the 12, 5 and 3.3V pins from the 24 pin and gives you banana plugs to connect to. That is a bit useless is it not? Aren't...
      05-06-2025, 10:37 PM
      NVDC charger configuration...
      11-05-2024, 03:28 PM
