MacBook A1278 main 820-2530b not charge, it turns on only with battery
  • reset1986
    • 308
    • italia
    hi, I have this macbook that works correctly with battery inserted, if I connect the power supply the light turns green but it does not charge, if I disconnect the battery and connect only the power supply the light turns green and the mac enters the ignition loop 4/5 sec, turns off and repeats itself,
    on the motherboard there are no traces of liquid or damaged components,
    I tested the 3.42 and they are constant both with power supply and with battery,
    advice on what signs I can start checking?
    the power supply indicator light never turns orange,
    power supply working on other macs
    thanks a lot
  • mon2
    • Dec 2019
    • 13894
    Re: MacBook A1278 main 820-2530b not charge, it turns on only with battery
    hi.
    1) with the battery only - is the logic board able to report the battery status (value) ? If yes, then the SMBUS_I2C lines on the battery are working. Check for this.
    2) Try to do the PRAM reset to see if this fixes the issue.
    3) If the status of the battery is not being reported, then check & post the voltage readings on:
    a) SMBUS_BATT_SCL
    b) SMBUS_BATT_SDA
    4) Otherwise, study the power boot sequence showing on sheet # 3 / 81.
    The number inside each circle is the power on order that must be met to allow for the logic board to boot and operate normally.
    5) U7000 page should be studied which is the main charger and DC adapter power rail IC. It is possible that some component (mosfet?) is shorted. More on this after the above feedback is posted.
    • reset1986
      • 308
      • italia
      Originally posted by mon2
      hi.
      a) SMBUS_BATT_SCL
      b) SMBUS_BATT_SDA
      thanks, yes the battery percentage is managed and correct,
      Seeing the ignition sequence and with the battery inserted you go to bypass U7000,
      I check that air and post the results, thanks
      • reset1986
        • 308
        • italia
        hi.
        a) SMBUS_BATT_SCL
        b) SMBUS_BATT_SDA
        hi, I found Q7030 pin 123 CHGR_PHASE and pin 4 CHGR_UGATE measured in diode mode low value 10ohm
        q7030 tested looks ok, replaced U7000 ISL6258a,
        the value is back to high, given power to the motherboard with power supply, switching on and off in repetition,
        measured again CHGR_PHASE and CHGR_UGATE again low value 10/12 ohm,
        there are no short
        do you have any advice? thanks a lot
        • mon2
          • Dec 2019
          • 13894
          Review this webpage:
          https://www.badcaps.net/forum/showthread.php?t=90356
          Post the voltages on each pin of U7000 with the adapter and battery connected.
          Post voltages of U7000 without adapter but battery connected.
          • reset1986
            • 308
            • italia
            ok just measured
            with battery inserted and mac turned off
            1 0V
            2 0V
            3 0V
            4 3.44V
            5 0V
            6 3.44
            7 0
            8 0
            9 0
            10 3.42
            11 3.42
            12 3.44
            13 3.42
            14 0
            15 0.05
            16 3.75
            17 10.66
            18 10.66
            19 0
            20 0
            21 0
            22 GND
            23 10.66
            24 10.66
            25 10.34
            26 14
            27 13.90
            28 13.80
            29 GND
            with battery inserted and power supply, mac off with green led
            1 0V
            2 16.45
            3 3.92
            4 3.44V
            5 0.18
            6 3.44
            7 0.72
            8 1.76
            9 0.03
            10 3.42
            11 3.42
            12 3.44
            13 3.42
            14 3.30
            15 0.05
            16 3.22
            17 10.65
            18 10.65
            19 5.06
            20 5.06
            21 0
            22 GND
            23 10.66
            24 10.58
            25 10.13
            26 16.05
            27 16.30
            28 16.30
            29 GND
            thanks
            • mon2
              • Dec 2019
              • 13894
              1) What is the voltage of PPBUS_G3H with the adapter & battery ?
              2) What is the voltage of PPBUS_G3H with the adapter (only) & no battery ?
              3) Power down, remove adapter & battery.
              Meter in resistance mode.
              Post the resistance for the following:
              a) source (1-2-3) & drain (5-6-7-8) of Q7050
              b) source (1-2-3) & gate (4) of Q7050
              c) gate (4) & drain (5-6-7-8) of Q7050
              4) Are you using an original magsafe 85W power supply ? With the battery out, does the magsafe LED turn orange (amber) ?
              5) Can you test with another known good battery ?
              6) Place meter in diode mode and post the diode readings for the SCL / SDA lines for the battery interface.
              a) Red meter lead to ground. Black meter lead on SMBUS_BATT_SCL. Diode reading ?
              b) Red meter lead to ground. Black meter lead on SMBUS_BATT_SDA. Diode reading ?
              • reset1986
                • 308
                • italia
                Re: MacBook A1278 main 820-2936b not charge, it turns on only with battery
                PPBUS_G3H with power supply and battery 10.60
                PPBUS_G3H with power supply and without battery, goes into power on off, I measure 12.50V, then turns off I measure 3.5V
                PPBUS_G3H measured on F7040
                q7050 should be the q7055 on this main 820-2936b, my mistake, I correct the title , place schematic and brd
                q7055 measurements
                a) 123--5678 113Kohm, inverting the wires to infinity
                b) 123--4 1.4 Mohm by inverting the leads infinity
                c) 4 --- 5678 I have no 2K-200K-2M scale readings
                original power supply working on another 1278, new battery charged to 40%
                SMBUS_SMC_BSA_SCL and SMBUS_SMC_BSA_SDA
                measured in diode mode, 223 both
                thanks for your help
                • mon2
                  • Dec 2019
                  • 13894
                  1) What chip was soldered in @ U7000 ? It has to be the ISL6259.
                  2) Desolder D6950 and remove all power (no adapter / no battery) and check the diode readings again on the battery SMBUS_SMC_BSA_SCL and SMBUS_SMC_BSA_SDA lines.
                  Post the results.
                  • piernov
                    • Jan 2016
                    • 4435
                    • France
                    L2008-M2009 MacBooks use ISL6258 not ISL6259.
                    • mon2
                      • Dec 2019
                      • 13894
                      OMG. The 820-2530 uses ISL6258 @ U7000 ?
                      The 820-2530 schematic shows as ISL6259.
                      Noting this correction, to the OP, which part do you have @ U7000 ?
                      • reset1986
                        • 308
                        • italia
                        here I am, U7000 isl6259A,
                        I made a mistake in the title
                        the motherboard is 820-2936b, I posted the schematic, soon I will post measurements of SMBUS_SMC_BSA_SCL and SMBUS_SMC_BSA_SDA lines. without diode
                        thanks a lot
                        • mon2
                          • Dec 2019
                          • 13894
                          Ok. 820-2936b from schematics and Louis' forum notes U7000 as ISL6259. Be sure that it is soldered properly - 'make it dance' with the flux and hot air.
                          • reset1986
                            • 308
                            • italia
                            desoldered D6950
                            SMBUS_SMC_BSA_SCL and SMBUS_SMC_BSA_SDA 223 measured in diode mode, 223 both as when d6950 is soldered
                            but the q7030 123--4 10 Ohm is normal?
                            isl6259 welded correctly
                            thanks
                            • mon2
                              • Dec 2019
                              • 13894
                              Sounds low to me. Desolder it and check the resistance again on this mosfet when it is out of circuit.
                              Source - drain ?
                              Source - gate ?
                              gate - drain ?
                              Likely it needs to be replaced.
                              The diode values may be ok on the I2C lines but internet (Louis' forum) - states it should be about 0.4 - 0.45. For now, do not worry about these values.
                              The mosfet @ Q7030 is of concern.
                              See the tables here for guidance.
                              http://electronicsbeliever.com/how-t...-is-defective/
                              • reset1986
                                • 308
                                • italia
                                Source - drain ?
                                Source - gate ?
                                gate - drain ?
                                ok, unsoldered q7030, q7035, q7055
                                test with 200K scale
                                q7030, q7035 q7055
                                123 --- 5678 110K
                                tapping pin 4
                                123 --- 5678 76K
                                123 --- 4 0 Kohm
                                4 ---- 5678 0 Kohm
                                inverting the tips I have no measures, they seem ok
                                q7030 on the motherboard I still have 10 ohms between 123--4
                                desoldering U7000 the value increases,
                                i had tried to replace U7000 the value before power on was correct between 123--4 of q7030, then it decreased again
                                • lazaro.089
                                  • Jun 2014
                                  • 79
                                  • Mexico
                                  Hi! I have the same exact problem than you!
                                  Low resistance between Ugate and phase of U7000. (Like 4 to 10 ohms)
                                  Also "Looping" every 5 seconds in PPBUS_G3H with charger only.
                                  With battery works fine. Already replaced Q7030 and U7000 with brand new chips. Same problem
                                  This is PPBUS_G3H readings.
                                  I'm suspecting SMC but I want to discard everything before changing it.
                                  • lazaro.089
                                    • Jun 2014
                                    • 79
                                    • Mexico
                                    Ok, I think I'm getting closer.
                                    Please, take a reading at U7000 pin 26.
                                    Mine is around 18v. It should be 0 so Q7080 saturates through the voltage divider.
                                    I have changed U7000 several times. My thoughts are that the SMC isn't communicating to ISL through SMBUS_SMC_BSA_SCL & SMBUS_SMC_BSA_SDA correctly.
                                    I'll try and check the comunication.
                                    • mon2
                                      • Dec 2019
                                      • 13894
                                      U7000 is a delicate device. If you have not done so already, use lots of flux and dial up high heat with good air pressure.
                                      For our tool, 500C and 50-65 percent on the air around the ic. Then we wait till the chip dances around the pcb pads where it lives. Just be careful to not disturb nearby parts. Then we are confident the balls have aligned ok.
                                      Just did the same recently for an ipad TriStar repair.
                                      • lazaro.089
                                        • Jun 2014
                                        • 79
                                        • Mexico
                                        Thanks mon2 I'll try it again. Maybe is wrongly soldered.
                                        @reset86, any news?
                                        • judamex
                                          MacBook Air 820-00165 turns on But no green and orange light, not charge
                                          by judamex
                                          MacBook Air turns on without battery connected, no green or orange light comes on, I connect the battery and it shows battery with lightning and it restarts constantly.
                                          03-06-2025, 03:55 PM
                                        • Daniel M
                                          MacBook Pro M1 A2338 256/16 820-2020 Turns On but No Charge, stuck 5V
                                          by Daniel M
                                          Hello all,
                                          I bought this MacBook brand new at launch. I have taken care of it since new and it suddenly failed on me recently.. it began to refuse to charge.
                                          I first checked all the basic things before opening it, to no avail.
                                          I have now opened it and taken the logic board out. I did a visual inspection and found no visible liquid damage or corrosion, or exploded caps, burnt components, etc. Cleaned the usb c connectors.
                                          Here are my measurements thus far:
                                          PBBUS_AON: 12V
                                          PP5V_S2: 5.3V
                                          PP3v8_AON:...
                                          06-12-2024, 05:52 PM
                                        • Stephen
                                          MacBook Pro 14" M1 Pro Turns on functions then turns off when I plug in USB C cable
                                          by Stephen
                                          MacBook Pro 14" M1 Pro Turns on functions then turns off when I plug in USB C cable to reset the computer. I disconnect the battery fully and then reconnect it and it won't turn back on. After letting it sit for a day I plug the battery back up, and the MagSafe 3 cable and it powers on and stays ons, once I plug in a USB C cable into the port closes to the MagSafe port it turns off and the Amber light turns off and won't turn on. No water damage, nothing, I want to do a DFU restore to wipe the computer since the customer stated they did an update and ever since it just decided to not work...
                                          03-15-2024, 09:37 AM
                                        • tccyo22
                                          Macbook Pro A1278 intermittent orange charge light
                                          by tccyo22
                                          Hi there, I've got a Macbook Pro A1278 board code 820-2936-B in which I have a very strange charging issue.
                                          Backstory is when I plugged the charger in, it would give a green light and swap to orange like normal but after a few seconds would go off to no light, laptop still powered on and functioned fine.
                                          So naturally I replaced the ISL chip first which made no difference so I also removed and reballed the SMC. This seemed to fix the issue for about an hour until I was back to square one again.
                                          Decided to then take an SMC from another board, reball that...
                                          04-20-2023, 08:58 AM
                                        • Stephen
                                          A2141 MacBook Pro 16" Turns on but no life, holds charge.
                                          by Stephen
                                          Customer computer came in, did a DFU revive, no luck, gives error, swapped out battery with two known working batteries still no luck. Board gets 20Volts, raises up to 1Amp then restarts, track pad clicks etc. Tried DFU restore, informed the customer that data recovery is most likely not possible since it didn't give us a revive and DFU restore was the next method to save the board, however it looks like not even DFU Restore is working as well. What could be causing this? I am assuming this is the infamous A2141 flaw that has the flawed Data lines that fail? Any suggestions would be great...
                                          05-13-2024, 10:21 AM
