Beginner questions about unstable voltage in laptop
  • cook
    Quiet observer
    • May 2010
    • 100
    Re: Beginner questions about unstable voltage in laptop
    Ditto!!!!!
    • cook
      Quiet observer
      • May 2010
      • 100
      Originally posted by Spider1211
      Read post #24.
      When you measure continuity on PQ18 and ground, there was very low resistance. This means that something on that line is shorting to ground. When you checked continuity across the mosfet, the resistance were higher (meaning it could be a leaky mosfet).
      You said that PQ19 has no continuity between drain and ground. So we can conclude that PQ18 is no shorted. (If PQ18 was shorted, you would get continuity between both Drain and Source with respect to ground)
      This means we can narrow our search area to where the Drain of PQ18 is connect. However, this is connected to the main 19V supply which connects to other part of the board. (Which means the fault could be anywhere on that rail).
      Lucky for us, PJ14 is there. An analogy could be: Think of PJ14 as a circuit breaker in your electrical panel. You have a main feeder which branches off to different areas of your house.
      Now imagine you had only 1 main circuit breaker. After the breaker, you electrical cable goes to different area of your house (say you have 3 rooms). If there is a fault in room 1, you main breaker will trip and will keep tripping until you remove the fault. However, since there is only 1 main breaker, you have to assume the fault can be in any of the 3 rooms, which make it difficult and time consuming to narrow down.
      On the other hand, imagine you have the same setup but this time after the main circuit breaker each room gets their own individual circuit breakers. If there is a fault (Lets assume for sake of argument that the main circuit breaker has a lower rating than the individual room breakers), the main circuit breaker will trip. This time however, you can isolate the problematic area. You start by assuming the fault is it room 1. All you need to do is to trip/disconnect circuit breaker for room 1.
      When you reset the main breaker, power is restored to the room 2 & 3 but because room 1 is now isolated, the main breaker no longer sees a fault and therefore does not trip.
      Your job now is just to find the root cause of the fault in room 1. Once repaired, all you need to do is reconnect its circuit breaker.
      In laptop case, the 19V (+VBat) is the "Main feeder" and PJ14 is acting as a bridge (analogous to the room circuit breaker). When you disconnected PJ14, you isolated the "room" (+Vcore_IN, where PQ18, etc is located) from the "main"(+VBat) and managed to locate on which side the fault was (see post #26).
      Hope that somewhat helps
      Yes, that explains it. Very nice explanation.
      • cook
        Quiet observer
        • May 2010
        • 100
        The fact that its broken is already reason enough to remove it. Most of the time these caps short internally. Although not as common as internal short, they can also fracture/crack.
        Remove it and recheck continuity across its solder pads.
        Post a picture if possible.
        My phone does not do closeups very well but I will see if maybe we have a camera that will work.
        • Spider1211
          • Oct 2019
          • 532
          • Mauritius
          #44
          That's fine. Just remove the cap and check for short. DO NOT reconnect PJ14 until you are sure the mosfets (PQ18 & PQ19) are not leaky. (check if they still read 100 - 150ohm as was the case previously). If they are, replace them.
          • cook
            Quiet observer
            • May 2010
            • 100
            I am having issues with my soldering iron, so it will might be a few days before I can get that cap removed.
            • Spider1211
              • Oct 2019
              • 532
              • Mauritius
              #46
              Use your hot air station. Just mask off any plastic material nearby that could get blasted with hot air as well as covering the CPU (if its nearby and isn't already covered by the heatsink).
              Just practice on a scrap board if you are not feeling too confident yet then move to the actual motherboard.
              • cook
                Quiet observer
                • May 2010
                • 100
                Yes, I want to practice on a scrap board first, one that has lead-free solder on it. My practice thus far was using a leaded board, and that went well, but when I tried on lead-free, I could tell it was not working, and I think my hot air was not calibrated right. It was not hot enough. So I'm trying to 'calibrate' it just enough so that I can melt lead-free solder on a practice board. Tomorrow I will be practicing that, so hopefully I will have that cap off tomorrow.
                • cook
                  Quiet observer
                  • May 2010
                  • 100
                  I removed PC87!! Finally. It was shorted.
                  New values for PQ18 and 19 are below.
                  PQ18
                  In circuit testing of continuity showed no continuity at all.
                  In circuit testing of resistance...
                  +D -S = nothing
                  -D +S = 11Mohms
                  In circuit testing of continuity on PQ19
                  +D -S = 85 ohms
                  -D +S = 112 ohms
                  • Spider1211
                    • Oct 2019
                    • 532
                    • Mauritius
                    #49
                    PQ18 seems to test OK.
                    The low resistance continuity test on PQ19 could be due to the CPU (although I would expect lower resistance on that line due to CPU). Are you comfortable with removing PQ19 and testing out of circuit? If not, try removing PL7 and redo continuity test (DO NOT apply power to the board when any of the components are off the board)
                    If PQ19 still shows low resistance out of circuit, replace it.
                    Once you confirmed everything tests OK and is soldered back (pay special attention to position/orientation of the components when resoldering, especially the MOSFET) on the board, do another continuity check across them as well as with black probe on ground (as you did during initial troubleshooting). If everything checks out, reconnect PJ14 and turn on the laptop.
                    • cook
                      Quiet observer
                      • May 2010
                      • 100
                      I just now picked up 2 boards that I can use to practice my hot air soldering skills with. So hopefully between now and sometime tomorrow, I will remove PQ19 and test. PL7 is right next to the plastic connector for the battery, so I am thinking I will not remove that until my skills are better. I think PQ19 will be safer to remove.
                      • cook
                        Quiet observer
                        • May 2010
                        • 100
                        PQ19 removed from the board!! Testing of PQ19...
                        Continuity mode
                        +D -S = no continuity
                        -D +S = no continuity
                        Resistance mode
                        +D -S = Continually bounced between no continuity and 3.3 KOhms
                        -D +S = .73 KOhms
                        • Spider1211
                          • Oct 2019
                          • 532
                          • Mauritius
                          #52
                          Continuity mode
                          Resistance mode
                          -D +S = .73 KOhms
                          No continuity sounds good, but am not liking the resistance values (it could also be that you partially turned it on when handling the mosfet also). Make sure your probes are making proper contact with the pins as sometimes when you desolder there can be a thin film of flux that solidifies on its surface.
                          Do a check in diode mode. You should have no continuity on +D-S and a diode reading on -D+S. And also remeasure the resistance value (usually we do only continuity/diode and do not measure resistance, but they should have very high resistance in OFF state).
                          You should properly ground yourself when working with these components. MOSFETs fairly sensitive to ESD.
                          • cook
                            Quiet observer
                            • May 2010
                            • 100
                            After I removed the chip I cleaned the contacts with IPA, so we should be OK there.
                            For these measurements, I did ground myself taking the measurements. Also, I switched to better test leads on my DMM.
                            Some of my results are different than what I has originally posted.
                            Diode Mode
                            -D +S = .132
                            I waited about 5 minutes before testing resistance..
                            +D -S = 43K
                            -D +S = .732 K ohms
                            Then when I tested +D and -S again, the result was different and it continually bounced between no continuity and 3.3 K ohms
                            • Spider1211
                              • Oct 2019
                              • 532
                              • Mauritius
                              #54
                              Continuity and diode test looks good, but am a bit skeptical about the resistance value. I'ld rather change it (especially given its in the circuit generating CPU voltage).
                              Replace it with similar or an equivalent. Check on your scrap board (assuming they are laptop boards).
                              Try this:
                              Put your meter in diode mode.
                              (1) Put black probe on gate (G) of mosfet and Red on drain (D). You should not have continuity.
                              Now measure continuity/resistance at +D-S and -D+S (you should not have continuity)
                              (2) Next put Red probe on gate (G) of mosfet and Black on drain (D). You still should not have continuity.
                              But now you should have continuity across +D-S and -D+S. (also measure resistance while at it)
                              (3) Repeat step 1.
                              If you still have the kind of resistance you described, its better you change the mosfet.
                              • cook
                                Quiet observer
                                • May 2010
                                • 100
                                I got the same results, so I am looking for a replacement mosfet. I have already found the data sheet for the mosfet in my board. And I found the one for the mosfet in my scrap board too. They are from different companies, so I am studying their specs to be sure they are basically the same thing. My scrap board is another HP Mini, although a different model, it looks really similar to mine. I think it is a bit newer board, but the 2 mosfets are right there next to the battery connector just like they are on my board. As long as volts are the same, amps are the same or higher, and resistance is fairly close, is that all I need to be concerned with for these mosfets?
                                Original mosfet: 30V, 14.8A, 6.0 m-Ohm (FDMC 7672S)
                                Replacement: 30V, 24A, 24 m-Ohm (AON 7410)
                                • Spider1211
                                  • Oct 2019
                                  • 532
                                  • Mauritius
                                  #56
                                  AON 7410 should be fine
                                  • cook
                                    Quiet observer
                                    • May 2010
                                    • 100
                                    • cook
                                      Quiet observer
                                      • May 2010
                                      • 100
                                      After a bit more of practicing soldering, I replaced the bad mosfet PQ19.
                                      Testing at PJ14...
                                      Pin 1 to ground = 16 m-Ohms and climbing
                                      Pin 2 to ground = 12 m-Ohms and climbing
                                      Is it OK to test the power using the power charger to see if I have 19V at the power connector?
                                      • Spider1211
                                        • Oct 2019
                                        • 532
                                        • Mauritius
                                        #59
                                        Testing at PJ14...
                                        mOhm = milli Ohm
                                        MOhm = Mega Ohm
                                        I assume you meant 12 & 16 Mega Ohms?
                                        You mentioned in post #36 that the power light came on, so we already know there is power at the connector.
                                        Connect PJ14 and try with the adapter.
                                        • cook
                                          Quiet observer
                                          • May 2010
                                          • 100
                                          Sorry. Yes, I meant M, not m.
                                          I will reconnect PJ14 and test with adapter.
                                          • m1ch43lzm
                                            by m1ch43lzm
                                            05-12-2025, 08:37 PM
                                          • howardc64
                                            by howardc64
                                            07-24-2025, 05:17 PM
                                          • tvguy12012012120
                                            by tvguy12012012120
                                            02-07-2025, 05:13 PM
                                          • Hakuu
                                            by Hakuu
                                            Hi There,
                                            More Details
                                            TV Model - LG OLED77G1PUA
                                            07-12-2023, 02:37 PM
