Looking to learn about troubleshooting my Lenovo L14 Gen 1
  • Lifeisfun
    • Apr 2025
    • 47
    Originally posted by mon2
    That is toasty. Chip was replaced? Was the chip soldered in the proper orientation on the board?
    Thanks for reply!
    I did not replace the BQ chip, only the EC chip and I'm pretty sure I did orient it correctly and did not overheat it.
    • Lifeisfun
      • Apr 2025
      • 47
      Originally posted by m1ch43lzm
      It's NVDC design (Narrow VDC), see https://www.badcaps.net/forum/troubl...arging-circuit
      I agree with mon2, the BQ25700A is too hot, it's available at mouser if its determined to be faulty
      So the main power rail and battery charge voltage is dependant on the battery configuration, so for 3S battery the fully charged voltage should be from 12.6v - 13v, similar as the Macbook charge circuit with the ISL chips
      With battery unplugged you should get 12.6 or 13v
      Could be the main rail (VSYS15) is unstable?, that may be the cause
      Without the battery connected there is only 9.4V or so, must be something wrong then.
      Will check the VSYS15
      Does the BQ chip only handle the battery charging and battery to USB-C switching? If so, can I remove it and try to power on without it?
      • m1ch43lzm
        • Mar 2019
        • 942
        • Peru
        #43
        tt won't work, as the BQ generates the main power rail, and charge the battery at the same time
        If working on battery only, the BQ connects the battery (BAT_PWR15) to the main power rail (VSYS15) by turning on PQ0201
        So it's an essential component on the board
        Do you still get the proper voltages at the 3.3v regulator?
        • Lifeisfun
          • Apr 2025
          • 47
          Oh, OK, thanks for the explanation, yes, the 3,3V rail is fine.
          Will swap the BQ chip and report back
          THANK YOU!
          • Lifeisfun
            • Apr 2025
            • 47
            Originally posted by Lifeisfun
            Another question, any reason for the BQ chip to be 49C when the battery is not even connected? The mosfets around tested OK and not shorted.
            When I connect the battery (12.6V charged to 11.35V) the charging voltage is only 12.4V not 15V and it's slowly dropping not going up.
            Could this be possible reason for the board not to post?
            Click image for larger version  Name:	image.png Views:	0 Size:	266.5 KB ID:	3635786
            I have another question about the VSYS15 voltage.
            Considering I get on the VSYS15 only 9.4V without battery connected and 12.4 with battery connected, is there any way to test if something is causing this drop?
            Can I inject voltage on the VSYS15 rail and see if anything is getting hot? If so what would be safe Voltage and Amp limit?
            The PR0201 coil is warm without battery and very hot with battery connected.
            UPDATE: Just tested VSYS15 resistance to ground and its about 5M+ so I presume there is no problem there.
            • m1ch43lzm
              • Mar 2019
              • 942
              • Peru
              #46
              Do you mean PL0201? (at the other side of the BQ, on the top side of the board) Measure resistance to GND, that coil shouldn't get hot at all, it's part of the input to the charge circuit
              You should have 20v there with the charger plugged in, and nothing (0v) with only the battery connected (charger unplugged)
              Check with thermal cam what else gets hot, could be a cap, the BQ itself, anything
              Something is really wrong in that area to make a coil get hot
              Or PR0201, the current sense resistor? (near the M.2 connector) Same, it shouldn't get hot at all
              • Lifeisfun
                • Apr 2025
                • 47
                Sorry, that was oversight on my part ( assumed and I was wrong)
                It is actually very strange, since even the board view doesn't ID that coil or the larger mosfet to the left above it.
                Click image for larger version  Name:	image.png Views:	0 Size:	94.2 KB ID:	3636748 Click image for larger version  Name:	coil2.jpg Views:	0 Size:	314.0 KB ID:	3636751
                The PL0201 is not present and the jumper is in place (jumper is 49K to ground) Yes there is 20V on that jumper and 20V on pin 1 of the BQ chip.
                Click image for larger version  Name:	coil1.jpg Views:	0 Size:	304.3 KB ID:	3636749
                PL0202 (I assume since is not marked anywhere) is the one getting hot when battery is connected and warm without battery. (1K to ground on that coil)
                The BQ chip is slightly above it on the other side of the board (BQ chip is definitely hot 50C or so)
                Click image for larger version  Name:	coil.jpg Views:	0 Size:	237.8 KB ID:	3636750
                Once again sorry for the wrong info before.
                Thanks!
                • m1ch43lzm
                  • Mar 2019
                  • 942
                  • Peru
                  #48
                  Get the board view from post #19 https://www.badcaps.net/forum/troubl...16#post3231416
                  You can open it with flexbv free
                  https://www.badcaps.net/forum/troubl...acos-and-linux
                  That will help identify those components
                  Anyway, from the resistance measurements, likely PU0201 is faulty (BQ25700A), according to schematics there shouldn't be a way to get 1k resistance to GND at PL0202 unless either PQ0204 and/or PQ0205 are faulty, or the BQ itself is faulty
                  Now remove the BQ and check resistance to GND at PL0202, you should get OL
                  Don't apply power to the board unless you replace the BQ
                  The charge circuit while in operation shouldn't get hot at all, at most around 30-35 deg C, I checked on my laptop (HP), while the charger IC is an ISL the topology is similar NVDC, i couldn't feel anything hot with my fingers while charging the battery (I don't have a thermal camera)
                  • Lifeisfun
                    • Apr 2025
                    • 47
                    You are great with all the hints and advice!
                    Thanks, will do!
                    • Sephir0th
                      • Oct 2020
                      • 1289
                      When the battery gets charged, the buck converter in NVDC designs can indeed get pretty "hot" till some extent. I won't agree with saying it is defective only from this observation. It's a common misunderstanding to think there is supposed to be 15V present just because there is "VSYS15" written. This is not true in any case. I can tell you that the engineers are just too lazy to change the rail designation...
                      In the end only the battery (nominal) voltage tells you how much voltage to expect on this raim
                      Also if with missing +VCCGFXCORE the internal graphics of the CPU is meant, it is absolutely normal for it not being present. This is not a issue per default. It will only come upnunder graphical load, at earliest in a Operating System environment.
                      From my understanding it's the point to check for picture/CapsLock response instead, before doing anything else.
                      FairRepair on YouTube
                      • Lifeisfun
                        • Apr 2025
                        • 47
                        In the end only the battery (nominal) voltage tells you how much voltage to expect on this rail
                        From my understanding it's the point to check for picture/Caps Lock response instead, before doing anything else.
                        Thank you very much for your time to respond!
                        There is something strange with the charging since the battery voltage is 11.35V but charging voltage is stuck on 12.4V and dropping.
                        Yes the coil is very hot when battery is connected but also warm without the battery when the voltage drops to the 9V range.
                        The BQ chip is also hot all the time.
                        There is no Caps LED lit and no response pressing the caps button (there is 3.3V on the keyboard)
                        I was all excited since I found YT video where someone is measuring resistance and voltages on this board but my happiness was short lived since the vide o is showing only last 3 digits of the multimeter
                        https://youtu.be/5gXg5LrUHjo?si=GX3GSHubjApvvMd_
                        • Sephir0th
                          • Oct 2020
                          • 1289
                          No, I am talking about the "Nominal voltage" of the battery, which is 11.1V when asking google.
                          For a LiPo battery with 3 cells in series (3S), nominally 11.1V, the full charging voltage is 12.6V. This is because each LiPo cell should be charged to 4.2V, and 4.2V * 3 = 12.6V.
                          So everything in specs here.
                          Also, when the board is full on up to even VCORE, then the charging controller can't be part of the issue. Seriously, it can't be. You can proof by testing with the main battery instead of the charger, this will most likely confirm that.
                          I'm sorry to tell that there is most likely a different issue way later in the power up sequence. With some luck it's "just" a BIOS issue. But unfortunately I fear something worse going on after the history. I suggest to start over with the troubleshooting, based on the current behaviour of the system. As much infos as possible and of course you can and you should simply share the values you wanted to compare with the video.
                          It could also be the case that the board is simply not charging the battery for whatever reason. But this has nothing to do with the power up, which the board does like you described, but a secondary issue which needs to be troubleshooted separately. The truth is that I did not understand im full what you explaining here and where you measured what. Thus is what it makes hard to respond something meaningful in this matter.
                          So questions here are:
                          Does it work from battery only?
                          Does it work from charger only?
                          dies the battery draw current when the board is NOT turned on?
                          Things like that, to at least roughly determine what is really going on in this section.
                          • Lifeisfun
                            • Apr 2025
                            • 47
                            Yes, you are correct the battery spec is NOM 11.1 / 4.08Ah
                            Just tried again and it will not power on with only battery connected, I have to have the USB-C power connected (it ramps up on connecting power to 20V and about 0.48A)
                            Tested again and now with battery connected the PL0202 coil has 9V with battery connected or disconnected.
                            CPU is warm
                            Only power button response is holding it for 10 seconds or so, on first attempt it will reboot and doing it second time it wit shut off but the board is still taking about 40mA.
                            I will start all over again.
                            Is there any risk to have it powered on for long time when measuring? Also should I measure with or without battery connected?
                            Board resistance and voltages
                            PL0701 2.5V 6Kohm
                            PL0601 1.19V 71ohm
                            PL0301 5.12V 400Kohm
                            PL0501 3.37V 151ohm
                            PL1003 0V 8ohm
                            PL0906/0903 0.96V 5.5ohm
                            PL1102 1V 25ohm
                            PL1403 1.05V 60ohm
                            PL0202 8.6V 61Kohm
                            Click image for larger version  Name:	Board coil resist.jpg Views:	0 Size:	402.9 KB ID:	3641665
                            • Sephir0th
                              • Oct 2020
                              • 1289
                              So it is most likely like assumed. A additional issue in the charging circuit. Battery could be simply locked in worst case.
                              But also 151 Ohms at the 3VALW, which is per 99% a partial short circuit of this rail. Something is faulty on this rail and we need to find out what it is. A almost impossible job without a thermal camera available.
                              • Lifeisfun
                                • Apr 2025
                                • 47
                                Thank you for the assessment!
                                I do have thermal cam, will look in to it!
                                Thanks!
                                EDIT
                                Interesting, this is the original problematic power supply where the LDO voltage to the EC chip was shorted, after replacement no longer shorted but perhaps some other issue
                                • Lifeisfun
                                  • Apr 2025
                                  • 47
                                  The only hot thing glowing is the BQ chip at 59C all other smaller chips are under 30C, and the EC chip has no longer hot spot on it but it's evenly distributed 28C.
                                  The replacement BQ chip should be here any day, I'll try to swap it to see if it will run cool.
                                  Once again thanks for your time and knowledge!
                                  • Lifeisfun
                                    • Apr 2025
                                    • 47
                                    I did unsolder the PJ0502 jumper to separate the rail from the power supply, and yes the partial short is there.
                                    What would be safe voltage and amperage to inject to find the problematic component?
                                    This rail feeds lots of stuff incl. the PCH, I just hope the PCH is not partially shorted, that would be the end
                                    • Sephir0th
                                      • Oct 2020
                                      • 1289
                                      This is what I would fear the most too...
                                      The track will with 150 Ohms not draw much current anyway. So no need to set it up higher than 1 Ampere. Regarding the voltage you probably need to move directly to 3 Volts. Less would most likely don't reveal anything. More will harm what is still healthy on this rail.
                                      • Lifeisfun
                                        • Apr 2025
                                        • 47
                                        Thank you!
                                        Will give it a shot today and report back
                                        • Lifeisfun
                                          • Apr 2025
                                          • 47
                                          Here are the results, I'm afraid it ain't good unless I see it wrong.
                                          @3V the rail takes 120mA, and the only thing that I see slightly glowing is the PCH (pics before and after injecting voltage)
                                          Makes me wonder what caused the damage, the EC chip was bad for sure since it was shoring the LDO 3V rail but why did it take out the PCH as well is beyond me.
ID:	3642027 Click image for larger version
                                          • coasterghost
                                            Lenovo T14 Gen 2 Type 20XK Model 20XK0069US Odd Charging Issues
                                            by coasterghost
                                            For Badcaps Readers, Please note that I am hopefully going to present this same message to Lenovo to see if they have any insight to the matter as well and figured to share the entirety here for clarification. The System is out of warranty as it is but does have the option to have it extended.
                                            Model Information: T14 Gen 2 (Type 20XK, 20XL) Laptop (ThinkPad) - Type 20XK - Model 20XK0069US
                                            Board: T14 Gen 2 (Type 20XK, 20XL) - Type 20XK.
                                            System Hardware:
                                            Processor: AMD Ryzen 7 PRO 5850U
                                            Memory: 1x 16GB DDR4 3200 (Soldered on Board); 1x Crucial 32GB DDR4...
                                            09-08-2025, 10:46 PM
                                            Lenovo 3000 Series Schematic
                                            Lenovo 3000 was a line of low-priced notebook and desktop computers designed by Lenovo Group targeting small businesses and individuals. It was replaced with the IdeaCentre and IdeaPad brands.
                                            3000 C100 laptop with Braille keyboard
                                            Lenovo 3000 C
                                            C100, C200 - 15-inch XGA screen
                                            Lenovo 3000 N
                                            N100, N200 - 14.1-inch- and 15.4-inch- WXGA models
                                            N500 - 15.4 inch screen.
                                            Lenovo 3000 V
                                            V100, V200 - 12.1-inch WXGA models
                                            Lenovo 3000 G
                                            G400, G410, G430, G450, G455, G510, G530, G550, and G560...
                                            10-04-2024, 06:05 AM
                                            Lenovo IdeaPad 120S Notebook 100 Specification for Upgrade or Repair
                                            This specification for the Lenovo IdeaPad 120S Notebook can be useful for upgrading or repairing a laptop that is not working. As a community we are working through our specifications to add valuable data like the 120S boardview and 120S schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant badcaps forum. Please note that we offer no warranties that any specification, datasheet, or download for Lenovo IdeaPad 120S...
                                            09-06-2024, 06:40 AM
                                            This specification for the Lenovo IdeaPad 320 Notebook can be useful for upgrading or repairing a laptop that is not working. As a community we are working through our specifications to add valuable data like the 320 boardview and 320 schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant badcaps forum. Please note that we offer no warranties that any specification, datasheet, or download for Lenovo IdeaPad 320...
                                            09-06-2024, 06:06 AM
                                          • derradji89
                                            Need help Lenovo MIX 320-10lCR domaine name SERCOL
                                            by derradji89
                                            Hi everyone 🤗
                                            I have a Lenovo MIX 320-10lCR computer.**
                                            1. **Operating System**: Windows 10 ** Education** 64-bit.
                                            2. **User Account Restrictions**: The account I'm using has heavily restricted permissions via **UAC** and **Group Policy**. This means I cannot install any software without admin rights, adjust system time, run Command Prompt as administrator, or modify the registry via Regedit—all are blocked.
                                            3. **BIOS Password Protection**: The BIOS is locked with a password, preventing me from installing a new operating system.
                                            4. **BIOS Chip Reflashing**: Currently,...
                                            04-19-2025, 03:04 PM
