    It'll be 240VAC in reference to L1 and L2 so the load will be the same on L1 and L2.
    -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

    Comment

    • Spork Schivago
      Badcaps Legend
      • Mar 2012
      • 4734
      • United States of America

      #82
      Re: Need help wiring up 240VAC.

      If they cannot accept the return because I installed it, it might be worth it to open up the PDU and try to install the double pole breakers. I don't know how easy that will be
      -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

      Comment

      • budm
        Badcaps Legend
        • Feb 2010
        • 40746
        • USA

        #83
        Re: Need help wiring up 240VAC.

        "I wired one of the 1400 watt PSUs up to one of my NEMA L6-30P's and plugged it in. Fired right up." I am NOT surprised that it works, the PSU is connected to L1 and L2, the center tab of you house wiring is not being used for your 240V load so as far as the power supply (or any 240V Loads) is concerned it is seeing incoming 240V and that is all it cares, but since you are using L1 AND L2 from your panel then you need dual breakers so if one of the L1 or L2 is shorted to GND it will pop both breakers (they are mechanical linked).
        That PDU you have should have been equipped with dual breakers to begin with but they are able to get away with it by specified the incoming as 1-phase only.
        All the products I designed for export (TuV is compliance tester) are spec in with dual breaker, and double pole switch due to the fact that some products have harmonized Schuko plug/receptacle which can be connected in either directions.
        Last edited by budm; 05-19-2018, 09:24 PM.
        Never stop learning
        Basic LCD TV and Monitor troubleshooting guides.
        http://www.badcaps.net/forum/showthr...956#post305956

        Voltage Regulator (LDO) testing:
        http://www.badcaps.net/forum/showthr...999#post300999

        Inverter testing using old CFL:
        http://www.badcaps.net/forum/showthr...er+testing+cfl

        Tear down pictures : Hit the ">" Show Albums and stories" on the left side
        http://s807.photobucket.com/user/budm/library/

        TV Factory reset codes listing:
        http://www.badcaps.net/forum/showthread.php?t=24809

        Comment

        • goontron
          5000!
          • Dec 2011
          • 4108
          • US

          #84
          Re: Need help wiring up 240VAC.

          ^ And the distribution panel doesn't already do this?
          Things I've fixed: anything from semis to crappy Chinese $2 radios, and now an IoT Dildo....

          "Dude, this is Wyoming, i hopped on and sent 'er. No fucking around." -- Me

          Excuse me while i do something dangerous


          You must have a sad, sad boring life if you hate on people harmlessly enjoying life with an animal costume.

          Sometimes you need to break shit to fix it.... Thats why my lawnmower doesn't have a deadman switch or engine brake anymore

          Follow the white rabbit.

          Comment

          • Spork Schivago
            Badcaps Legend
            • Mar 2012
            • 4734
            • United States of America

            #85
            Re: Need help wiring up 240VAC.

            Originally posted by budm
            "I wired one of the 1400 watt PSUs up to one of my NEMA L6-30P's and plugged it in. Fired right up." I am NOT surprised that it works, the PSU is connected to L1 and L2, the center tab of you house wiring is not being used for your 240V load so as far as the power supply (or 240V) is concerned it is seeing incoming 240V and that is all it cares, but since you are using L1 AND L2 from your panel then you need dual breakers so if one of the L1 or L2 is shorted to GND it will pop both breakers (they are mechanical linked).
            That PDU you have should have been equipped with dual breakers to begin with but they are able to get away with it by specified the incoming as 1-phase only.
            All the products I designed for export (TuV is compliance tester) are spec in with dual breaker, and double pole switch due to the fact that some products have harmonized Schuko plug/receptacle which can be connected in either directions.
            Yes, I think the problem was I was too technical when asking their supposed tech support the questions. I think they heard split phase, didn't know what I was talking about or just references the datasheet and said no. The only way it might matter is if I had the psu hooked to an "intelligent" PDU. For each PSU, there's not just three prongs for input, but also four PCB pads that communicate with intelligent PDUs that HPE sell. I like the PDU and like the idea of just wiring the European connector to my double pole breaker, but the internal breakers inside, as you mentioned are single pole, which is why we need the one phase 240VAC. How hard do you think it'd be able to source the double pole breakers and install them, if it's even possible. Granted, warranty would be over with I'd imagine, but would that be doable do you think? I can't crack it open to take a look unless they say I cannot send it back...but if it's as easy as just buying the proper breakers and soldering them in or wiring them up, I think I might rather do that.
            -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

            Comment

            • Spork Schivago
              Badcaps Legend
              • Mar 2012
              • 4734
              • United States of America

              #86
              Re: Need help wiring up 240VAC.

              Originally posted by goontron
              ^ And the distribution panel doesn't already do this?
              What do you mean the distribution panel? My breaker panel? Yes, that should trip, but might not. The internal ones are 16 Amp each (derated, so essentially the 20 amp). Its a 7.3KVA PDU. I think we determined we needed double pole to 30 AMP breaker, maybe 40
              -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

              Comment

              • budm
                Badcaps Legend
                • Feb 2010
                • 40746
                • USA

                #87
                Re: Need help wiring up 240VAC.

                Can I see good clear pictures of your PDU? I like to see what the two 16A breakers look like from outside.
                Never stop learning
                Basic LCD TV and Monitor troubleshooting guides.
                http://www.badcaps.net/forum/showthr...956#post305956

                Voltage Regulator (LDO) testing:
                http://www.badcaps.net/forum/showthr...999#post300999

                Inverter testing using old CFL:
                http://www.badcaps.net/forum/showthr...er+testing+cfl

                Tear down pictures : Hit the ">" Show Albums and stories" on the left side
                http://s807.photobucket.com/user/budm/library/

                TV Factory reset codes listing:
                http://www.badcaps.net/forum/showthread.php?t=24809

                Comment

                • Spork Schivago
                  Badcaps Legend
                  • Mar 2012
                  • 4734
                  • United States of America

                  #88
                  Re: Need help wiring up 240VAC.

                  Originally posted by budm
                  Can I see good clear pictures of your PDU? I like to see what the two 16A breakers look like from outside.
                  Yes sir. I will show you them tripped and not tripped. It's a type of rocker switch, but is flush (doesn't look like a rocker) until you trip it. I will go take the pictures now for you.
                  -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                  Comment

                  • Spork Schivago
                    Badcaps Legend
                    • Mar 2012
                    • 4734
                    • United States of America

                    #89
                    Re: Need help wiring up 240VAC.

                    These three pictures of are the L1 top row (for the back of the PDU, there's two rows, a top row called L1, a bottom row called L2). There's two breakers, one called L1, one called L2. This is just one of the two breakers.

                    Keep in mind, the value shown is derated, so the American two-pole version should show 20-amp, not 16-amp.

                    I can provide measurements with my caliper as well, if need be. There's two screws / bolts per breaker. I was looking at E-T-A and although they have one that's close, because it doesn't have the screw holes, I think we can rule E-T-A out as a manufacturer.
                    Attached Files
                    -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                    Comment

                    • Spork Schivago
                      Badcaps Legend
                      • Mar 2012
                      • 4734
                      • United States of America

                      #90
                      Re: Need help wiring up 240VAC.

                      Hrmm, for some reason, they're sideways. That's not the way I took them. Sorry about that.
                      -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                      Comment

                      • budm
                        Badcaps Legend
                        • Feb 2010
                        • 40746
                        • USA

                        #91
                        Re: Need help wiring up 240VAC.

                        "Keep in mind, the value shown is derated, so the American two-pole version should show 20-amp, not 16-amp." That is correct for those IEC outlets, the large (IEC-320-C19) one is rated 20A US, 16A Euro, the smaller (IEC-320-C13) 15a us RATED, 10A Euro rated.
                        Hmm, I cannot tell if they are magnetic or thermal breakers type.
                        The breaker itself rating is real 16A. I spec in 16A for the products with IEC-320-C19.
                        I use Carling in most the products since they can custom made for us in our application.
                        Your looks SIMILAR to Carling B series or J Rocker actuator:
                        http://www.carlingtech.com/hm-cb-b-series
                        http://www.carlingtech.com/hm-cb-j-series
                        Last edited by budm; 05-19-2018, 11:06 PM.
                        Never stop learning
                        Basic LCD TV and Monitor troubleshooting guides.
                        http://www.badcaps.net/forum/showthr...956#post305956

                        Voltage Regulator (LDO) testing:
                        http://www.badcaps.net/forum/showthr...999#post300999

                        Inverter testing using old CFL:
                        http://www.badcaps.net/forum/showthr...er+testing+cfl

                        Tear down pictures : Hit the ">" Show Albums and stories" on the left side
                        http://s807.photobucket.com/user/budm/library/

                        TV Factory reset codes listing:
                        http://www.badcaps.net/forum/showthread.php?t=24809

                        Comment

                        • Spork Schivago
                          Badcaps Legend
                          • Mar 2012
                          • 4734
                          • United States of America

                          #92
                          Re: Need help wiring up 240VAC.

                          Originally posted by budm
                          "Keep in mind, the value shown is derated, so the American two-pole version should show 20-amp, not 16-amp." That is correct for those IEC outlets, the large (IEC-320-C19) one is rated 20A US, 16A Euro, the smaller (IEC-320-C13) 15a us RATED, 10A Euro rated.
                          Hmm, I cannot tell if they are magnetic or thermal breakers type.
                          The breaker itself rating is real 16A. I spec in 16A for the products with IEC-320-C19.
                          I use Carling in most the products since they can custom made for us in our application.
                          Your looks to be Carling B series Rocker actuator:
                          http://www.carlingtech.com/hm-cb-b-series
                          Holy cow! How did you find them so quickly?? You are amazing! Are you saying I'm correct in the sense that the double-pole ones I'd want would say 20A and not 16A on them?

                          How could I tell if they're magnetic or thermal? Would there be any tests I can perform without opening them to test?

                          Finally, do you think it very well might be possible to just switch out the 16A single poles for the correct double-poles? Which worries me is they don't make this 7.3KVA PDU for North America. They make ones half the size, but not this large. I wonder if I'm missing something more than just the breakers and receptacle....I purchased the double pole 40-amp breakers, but I might need 50-amp double-pole (for the mains panel).

                          The 7.3KVA appears that it might be derated as well, and that the PDU, according to one of the documents I found, supports up to 10KVA. With a power factor of .99, we're looking at ~42 amps (10,000 / 240). Not that I'd necessarily be having a power factor of .99, I just want to make sure I'm safe and don't do anything wrong here. Because their plug is showing a derated value of 32A, I think 40 amp is just right. What do you think?
                          -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                          Comment

                          • budm
                            Badcaps Legend
                            • Feb 2010
                            • 40746
                            • USA

                            #93
                            Re: Need help wiring up 240VAC.

                            Pure Thermal breaker will require derating based on ambient temperature, the higher the Ambient the less current it can handle. I doubt that HP will put in pure thermal breakers, they are thermal-magnetic has better derating than the pure thermal breaker.
                            You want 16A, not 20A on that PDU to maintain the same protection.
                            There is also more thing to consider for the replacement breakers, more likely to be made for high in-rush type, not fast tripping, the only way to find out is to look at the label on the existing breaker.

                            Your house panel breaker: you should consult your electrician and NEC rules.
                            It is not that simpe.
                            https://cdn.badcaps-static.com/pdfs/...459c54c49b.pdf

                            https://cdn.badcaps-static.com/pdfs/...4eacafa4c8.pdf
                            https://www.mikeholt.com/mojonewsarc...s~20030621.htm

                            Thermal-Magnetic breaker:
                            https://thegrid.rexel.com/en-us/prod...tic-protection
                            Last edited by budm; 05-19-2018, 11:31 PM.
                            Never stop learning
                            Basic LCD TV and Monitor troubleshooting guides.
                            http://www.badcaps.net/forum/showthr...956#post305956

                            Voltage Regulator (LDO) testing:
                            http://www.badcaps.net/forum/showthr...999#post300999

                            Inverter testing using old CFL:
                            http://www.badcaps.net/forum/showthr...er+testing+cfl

                            Tear down pictures : Hit the ">" Show Albums and stories" on the left side
                            http://s807.photobucket.com/user/budm/library/

                            TV Factory reset codes listing:
                            http://www.badcaps.net/forum/showthread.php?t=24809

                            Comment

                            • Spork Schivago
                              Badcaps Legend
                              • Mar 2012
                              • 4734
                              • United States of America

                              #94
                              Re: Need help wiring up 240VAC.

                              I'll read the articles first thing tomorrow morning, i'm going to bed. For me to read in the AM though, if I have the chance to send the PDU back and purchase a couple of the American versions (that provide less KVA per PDU), would you recommend I do that over modifying the existing one?

                              I'll go over the NEC rules a bit more, you can grab them for free off the government's website (or maybe it's a .org one?), I can provide the address if you want it.

                              Throwing in the double pole breaker in my pain, replacing the internal signal pole breakers with double pole breakers, and then wiring up the receptacle Stj linked to isn't all there is to modifying this PDU? Lot more to it? I was afraid of that.
                              -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                              Comment

                              • Spork Schivago
                                Badcaps Legend
                                • Mar 2012
                                • 4734
                                • United States of America

                                #95
                                Re: Need help wiring up 240VAC.

                                Originally posted by budm
                                "Keep in mind, the value shown is derated, so the American two-pole version should show 20-amp, not 16-amp." That is correct for those IEC outlets, the large (IEC-320-C19) one is rated 20A US, 16A Euro, the smaller (IEC-320-C13) 15a us RATED, 10A Euro rated.
                                Hmm, I cannot tell if they are magnetic or thermal breakers type.
                                The breaker itself rating is real 16A. I spec in 16A for the products with IEC-320-C19.
                                I use Carling in most the products since they can custom made for us in our application.
                                Your looks SIMILAR to Carling B series or J Rocker actuator:
                                http://www.carlingtech.com/hm-cb-b-series
                                http://www.carlingtech.com/hm-cb-j-series
                                If those pictures are the true pictures for the series, it's definitely not J series. With the button, it's not flat. It's more like this --_ if that makes any sense. I'm trying to explain the best I can in words. Right after the number 16, there's a small slope where it goes down to the OFF level.

                                To try and be a bit more clear on this, we'll look at the bottom as having two levels, the ON level, which if the breaker was removed, and sitting straight up, the ON level is physically higher than the OFF level. Only by a couple mm's.

                                The picture for the B and J series, neither of them appear to have the slop that I'm talking about. ON is level, then slopes down real quick like to the OFF label, which is level, but not at the same height as the ON level. It's recessed.
                                -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                                Comment

                                • budm
                                  Badcaps Legend
                                  • Feb 2010
                                  • 40746
                                  • USA

                                  #96
                                  Re: Need help wiring up 240VAC.

                                  You need to conform to your local code your local code beside the NEC. I do have have lots of NEC info at works for reference, there are tons of info but it still comes down to local codes.\
                                  BTW, did you get the user manual/wiring instruction, etc with that PDU?
                                  What compliance agency does it have on it?
                                  Last edited by budm; 05-20-2018, 12:26 PM.
                                  Never stop learning
                                  Basic LCD TV and Monitor troubleshooting guides.
                                  http://www.badcaps.net/forum/showthr...956#post305956

                                  Voltage Regulator (LDO) testing:
                                  http://www.badcaps.net/forum/showthr...999#post300999

                                  Inverter testing using old CFL:
                                  http://www.badcaps.net/forum/showthr...er+testing+cfl

                                  Tear down pictures : Hit the ">" Show Albums and stories" on the left side
                                  http://s807.photobucket.com/user/budm/library/

                                  TV Factory reset codes listing:
                                  http://www.badcaps.net/forum/showthread.php?t=24809

                                  Comment

                                  • stj
                                    Great Sage 齊天大聖
                                    • Dec 2009
                                    • 31199
                                    • Albion

                                    #97
                                    Re: Need help wiring up 240VAC.

                                    if you fit a double-pole 240v 32A RCD between the double breaker and the IEC socket, it solves the electrical problem
                                    not sure about this "code" crap though.

                                    in short, an RCD monitors the current on the 2 wires - if one is higher it assumes a problem and trips.
                                    if a single-pole breaker on the pdu trips, the rcd should trip.

                                    infact if your concerned about kids in the basement, an rcd on it is a good idea anyway.
                                    it will trip if it see's a difference of 30ma - that's good enough to save someone who touches a live terminal.
                                    Last edited by stj; 05-20-2018, 02:54 PM.

                                    Comment

                                    • Spork Schivago
                                      Badcaps Legend
                                      • Mar 2012
                                      • 4734
                                      • United States of America

                                      #98
                                      Re: Need help wiring up 240VAC.

                                      Originally posted by budm
                                      You need to conform to your local code your local code beside the NEC. I do have have lots of NEC info at works for reference, there are tons of info but it still comes down to local codes.\
                                      BTW, did you get the user manual/wiring instruction, etc with that PDU?
                                      What compliance agency does it have on it?
                                      There was no user manual / wiring instructions. Just some stupid pamphlet that seems to come with all of them. This one is a little different and says Important PDU User Documentation Download information

                                      To download the latest user documentation, see the Hewlett Packard Enterprise website ( http://www.hpe.com/support/mPDU_manuals ).

                                      For important safety, environmental, and regulatory information, see Safety and Compliance Information for Server, Storage, Power, Networking, And Rack Products, available at the Hewlett Packard Enterprise website ( http://www.hpe.com/support/Safety-Co...rpriseProducts ).

                                      There's another generic pamphlet as well but just talks about HPE servers, racks, etc. Could you give an example of what the Compliance Agency would look like? Maybe it's on the PDU or the plug itself?

                                      I contacted my Account Executive to see if I could return it. Sorry for the long delay in responding. I've been working on a long contract project with someone for the last couple years that I think I just finished (yay!!!!) and he had to come over and double check the code before taking it to his company and putting it into the test phase.
                                      -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                                      Comment

                                      • budm
                                        Badcaps Legend
                                        • Feb 2010
                                        • 40746
                                        • USA

                                        #99
                                        Re: Need help wiring up 240VAC.

                                        There should be logo or printing around the incoming AC connector.
                                        Never stop learning
                                        Basic LCD TV and Monitor troubleshooting guides.
                                        http://www.badcaps.net/forum/showthr...956#post305956

                                        Voltage Regulator (LDO) testing:
                                        http://www.badcaps.net/forum/showthr...999#post300999

                                        Inverter testing using old CFL:
                                        http://www.badcaps.net/forum/showthr...er+testing+cfl

                                        Tear down pictures : Hit the ">" Show Albums and stories" on the left side
                                        http://s807.photobucket.com/user/budm/library/

                                        TV Factory reset codes listing:
                                        http://www.badcaps.net/forum/showthread.php?t=24809

                                        Comment

                                        • budm
                                          Badcaps Legend
                                          • Feb 2010
                                          • 40746
                                          • USA

                                          #100
                                          Re: Need help wiring up 240VAC.

                                          The first link you provide I get the message below:
                                          HPE Metered and Switched Power Distribution Units
                                          Select an HPE product

                                          The page you requested has changed. Please select your product below to be directed to your product information. We recommend you bookmark the new page destination for future inquiries.
                                          No results
                                          Never stop learning
                                          Basic LCD TV and Monitor troubleshooting guides.
                                          http://www.badcaps.net/forum/showthr...956#post305956

                                          Voltage Regulator (LDO) testing:
                                          http://www.badcaps.net/forum/showthr...999#post300999

                                          Inverter testing using old CFL:
                                          http://www.badcaps.net/forum/showthr...er+testing+cfl

                                          Tear down pictures : Hit the ">" Show Albums and stories" on the left side
                                          http://s807.photobucket.com/user/budm/library/

                                          TV Factory reset codes listing:
                                          http://www.badcaps.net/forum/showthread.php?t=24809

                                          Comment

                                          Related Topics

                                          Collapse

                                          Working...