    Skystorm - it sounds like you've been having issues with the wiring in your apt since joining this forum.

    My advice is this: get the landlord to have the ENTIRE service and electrical system in your apt completely inspected. By code, you're allowed to have +/- 10% of voltage (98 to 132 volts on a 120 line, etc). If you still have that Zinsco panel, it's trouble. Your service is at least 30 years old. Service cables and meter pans don't last much more than 35 years, especially those made of aluminum.

    I have seen the damage caused by bad neutrals in service equipment. It gets ugly fast and electronics and motors are the first victims.
    Stupidity should be a crime, especially for drivers. I have NO patience for them.

    Comment

    • kaboom
      "Oh, Grouchy!"
      • Jan 2011
      • 2507
      • USA

      #22
      Re: bad power

      Oil from tx, or creosote seeping out at the pole base?

      Is your apt a multi-unit building? Or just your one apt in that building?

      *Don't do the following unless you unplug any electronic equipment first!*
      Find two circuits, each on opposite sides of the service. Get two small lamps or nightlights. Plug them in, one into an L1 circuit, the other into an L2. Now get a hair dryer or space heater. While watching the bulb on L1, run the heater on L2. All that should happen is the bulb on L2 may dim -very- slightly, unless the heater is on the same ckt as the bulb. Now reverse things and put the heater on L1 and watch the bulb on L2.

      If the bulb on L2 gets brighter with the heater on L1 or the bulb on L1 gets brighter with the heater on L2, look at the neutral! If, however, there's only dimming, check the stabs on the bkrs, backstabbed receps, buried splices, etc.

      And trash the Zinsco!
      "pokemon go... to hell!"

      EOL it...
      Originally posted by shango066
      All style and no substance.
      Originally posted by smashstuff30
      guilty,guilty,guilty,guilty!
      guilty of being cheap-made!

      Comment

      • kaboom
        "Oh, Grouchy!"
        • Jan 2011
        • 2507
        • USA

        #23
        Re: bad power

        Originally posted by delaware74b
        Skystorm - it sounds like you've been having issues with the wiring in your apt since joining this forum.

        My advice is this: get the landlord to have the ENTIRE service and electrical system in your apt completely inspected. By code, you're allowed to have +/- 10% of voltage (98 to 132 volts on a 120 line, etc). If you still have that Zinsco panel, it's trouble. Your service is at least 30 years old. Service cables and meter pans don't last much more than 35 years, especially those made of aluminum.

        I have seen the damage caused by bad neutrals in service equipment. It gets ugly fast and electronics and motors are the first victims.
        Thanks for contributing (again). I hope it doesn't end with the noodle flapping in the breeze or the termination in the panel falling apart and burning everything up. And if there's no cold water GEC to 'mask' the neutral problem, some people 'put up with' replacing bulbs every 3 weeks. And a plumber could get electrocuted during a water meter change if the GEC is landed on the house side of the meter instead of the street side.

        No one 'suggest' that he needs 'more ground rods.'

        skystorm, your CATV and phone drops will burn up when the noodle completely lets go. But that will be the least of your troubles...
        "pokemon go... to hell!"

        EOL it...
        Originally posted by shango066
        All style and no substance.
        Originally posted by smashstuff30
        guilty,guilty,guilty,guilty!
        guilty of being cheap-made!

        Comment

        • kaboom
          "Oh, Grouchy!"
          • Jan 2011
          • 2507
          • USA

          #24
          Re: bad power

          Slightly OT...

          skystorm, I just saw that furnace video.

          What the hell is up with the landlord!? Renting out a firetrap like that! Inducer starts, ignitor heats up, you close ckt to open gas valve, ignition. Then rollout because IDM stops and restarts. You won't be ready with your '50 pound dry chem' at 2 in the morning...

          (Criminal) negligence!

          The two pix are from hvac-talk. Can anyone tell me what's missing in that 'vestibule compartment?'
          Attached Files
          "pokemon go... to hell!"

          EOL it...
          Originally posted by shango066
          All style and no substance.
          Originally posted by smashstuff30
          guilty,guilty,guilty,guilty!
          guilty of being cheap-made!

          Comment

          • skystormfarms
            Banned
            • Mar 2011
            • 160

            #25
            Re: bad power

            well i did that for the video defrint wires

            Comment

            • skystormfarms
              Banned
              • Mar 2011
              • 160

              #26
              Re: bad power

              oh and i just hit 75hz

              Comment

              • kaboom
                "Oh, Grouchy!"
                • Jan 2011
                • 2507
                • USA

                #27
                Re: bad power

                Don't brush something like that off casually.

                You better hope that thing has rollout switches on the burner box.

                Don't be ignorant and blow it off like, "Well it rolls out, but eventually the IDM stays on and the blower comes on."

                'Eventually,' all the wrongs will piss Murphy off and you'll have a fire or worse.

                For the sake of everyone in the place, FIX THE DAMN THING.
                "pokemon go... to hell!"

                EOL it...
                Originally posted by shango066
                All style and no substance.
                Originally posted by smashstuff30
                guilty,guilty,guilty,guilty!
                guilty of being cheap-made!

                Comment

                • kaboom
                  "Oh, Grouchy!"
                  • Jan 2011
                  • 2507
                  • USA

                  #28
                  Re: bad power

                  Originally posted by skystormfarms
                  oh and i just hit 75hz
                  Lights getting brighter with increasing freq?

                  You could even have bad connections in that Zinsco "making and breaking" and sending extra pulses into the meter. If it's filtered enough, shouldn't happen though.

                  PS- You shouldn't have the computer on if the neutral's going bad, UPS or otherwise. If something goes boom and the UPS bypasses, your computer will be connected right to the line.
                  Last edited by kaboom; 06-27-2011, 08:02 PM.
                  "pokemon go... to hell!"

                  EOL it...
                  Originally posted by shango066
                  All style and no substance.
                  Originally posted by smashstuff30
                  guilty,guilty,guilty,guilty!
                  guilty of being cheap-made!

                  Comment

                  • skystormfarms
                    Banned
                    • Mar 2011
                    • 160

                    #29
                    Re: bad power

                    and it has had a compleat over hull
                    t-former
                    t-stat
                    control bord
                    igniter

                    Comment

                    • skystormfarms
                      Banned
                      • Mar 2011
                      • 160

                      #30
                      Re: bad power

                      i smell sumthing burning

                      Comment

                      • kaboom
                        "Oh, Grouchy!"
                        • Jan 2011
                        • 2507
                        • USA

                        #31
                        Re: bad power

                        Originally posted by skystormfarms
                        control board
                        All it needed to resolve the starting & stopping IDM.

                        What about cleaning the blower wheel, oiling the blower motor, cleaning condensing unit & evap coil if you have A/C, replacing the filter, and checking the temperature rise? If the filter's horribly clogged, ducts too small or blower speed too low, your rise will be too high and you'll end up with a cracked HX.
                        "pokemon go... to hell!"

                        EOL it...
                        Originally posted by shango066
                        All style and no substance.
                        Originally posted by smashstuff30
                        guilty,guilty,guilty,guilty!
                        guilty of being cheap-made!

                        Comment

                        • skystormfarms
                          Banned
                          • Mar 2011
                          • 160

                          #32
                          Re: bad power

                          surge strip 15in lcd smart meter allup in smoke
                          40in plasma still alive

                          Comment

                          • kaboom
                            "Oh, Grouchy!"
                            • Jan 2011
                            • 2507
                            • USA

                            #33
                            Re: bad power

                            Originally posted by skystormfarms
                            i smell sumthing burning
                            Throw the main breaker. You DO have one, I hope???

                            WHY are you posting here?? If you got a fire someplace, call 911 already!

                            FYI- if the pole transformer shorts primary to secondary, there will be step potential around the pole ground- this is a shock hazard. Don't go near it!

                            Please be careful.
                            "pokemon go... to hell!"

                            EOL it...
                            Originally posted by shango066
                            All style and no substance.
                            Originally posted by smashstuff30
                            guilty,guilty,guilty,guilty!
                            guilty of being cheap-made!

                            Comment

                            • skystormfarms
                              Banned
                              • Mar 2011
                              • 160

                              #34
                              Re: bad power

                              fires allredy out and both v and hz have gone back to normal

                              Comment

                              • kaboom
                                "Oh, Grouchy!"
                                • Jan 2011
                                • 2507
                                • USA

                                #35
                                Re: bad power

                                Originally posted by skystormfarms
                                40in plasma still alive
                                Not for long! UNPLUG IT! NOW!

                                The neutral's letting go.

                                As the neutral path gets more and more compromised, the neutral point is floating to some high voltage. The MOVs in the surge strip vainly tried to clamp this voltage, but the fault energy is too much for them. So they burned up.

                                Keep waiting. More stuff will burn clear and the remaining items plugged in will get higher and higher voltages impressed upon them, until they too fail.
                                "pokemon go... to hell!"

                                EOL it...
                                Originally posted by shango066
                                All style and no substance.
                                Originally posted by smashstuff30
                                guilty,guilty,guilty,guilty!
                                guilty of being cheap-made!

                                Comment

                                • skystormfarms
                                  Banned
                                  • Mar 2011
                                  • 160

                                  #36
                                  Re: bad power

                                  pop and out gos the pole t-former
                                  i am on a lap top

                                  Comment

                                  • kaboom
                                    "Oh, Grouchy!"
                                    • Jan 2011
                                    • 2507
                                    • USA

                                    #37
                                    Re: bad power

                                    Originally posted by skystormfarms
                                    fires allredy out and both v and hz have gone back to normal
                                    Maybe the fridge came on if it wasn't damaged (yet), balancing the service. You'll be back in half an hour when your loads change again and the service once again become severely unbalanced w/o the neutral.

                                    Three words: Moores Mill Road

                                    Look outside at some other building serviced by this same transformer. Are they having problems too?
                                    "pokemon go... to hell!"

                                    EOL it...
                                    Originally posted by shango066
                                    All style and no substance.
                                    Originally posted by smashstuff30
                                    guilty,guilty,guilty,guilty!
                                    guilty of being cheap-made!

                                    Comment

                                    • skystormfarms
                                      Banned
                                      • Mar 2011
                                      • 160

                                      #38
                                      Re: bad power

                                      no i just watch the pole t-former go bang

                                      Comment

                                      • kaboom
                                        "Oh, Grouchy!"
                                        • Jan 2011
                                        • 2507
                                        • USA

                                        #39
                                        Re: bad power

                                        Originally posted by skystormfarms
                                        pop and out gos the pole t-former
                                        i am on a lap top
                                        Sounded like a shotgun blast, right? Cutout hanging in the breeze? The two in the pix are closed

                                        Go around the house and unplug everything. For equipment fastened in place, dump breaker. If the POCO refuses that cutout and the transformer goes pri to sec, you'll bbq your appliances and electronics, so unplug 'em now.

                                        Get a camera ready for when the POCO comes. If the tx blows its top when/if they refuse it first, you'll have a good one for youtube. Provided you dump your loads first...
                                        Attached Files
                                        "pokemon go... to hell!"

                                        EOL it...
                                        Originally posted by shango066
                                        All style and no substance.
                                        Originally posted by smashstuff30
                                        guilty,guilty,guilty,guilty!
                                        guilty of being cheap-made!

                                        Comment

                                        • skystormfarms
                                          Banned
                                          • Mar 2011
                                          • 160

                                          #40
                                          Re: bad power

                                          alredy done but the top of the t-former is 5 miles away now cus you can see the HV cabe hanging and sparking on the pole

                                          Comment

                                          Related Topics

                                          Collapse

                                          • Tynan Dill
                                            Vizio e601i-A3 - Has Sound and Display, But No Backlight - Bad Power Supply Board or Bad LED Bulbs ?
                                            by Tynan Dill
                                            I was given this TV from my great uncle. He said it just wouldn't turn on one day out of nowhere, replaced the TV, and gave it to me to possibly fix and use for myself.

                                            Upon bringing it home and plugging it up, it showed a standby light.

                                            I powered it on and without a flashlight, the display showed the "V" but the lighting is very dim, but visible.

                                            The screen seems to blackout and stay black, but with a flashlight I can see the display.

                                            With my Playstation 4 connected via HDMI, and running a game I can hear sound.

                                            Assuming...
                                            11-22-2024, 01:46 PM
                                          • PantherDave
                                            Microsoft Surface Pro (5th gen) model 1796 - no power
                                            by PantherDave
                                            Hi all!

                                            I'm trying to troubleshoot a Microsoft Surface Pro (5th gen) model 1796 that won't power on. Motherboard model is M1007506-015. My priority is retrieving data, but the SSD is integrated so it looks like if I can't repair it it'll need to go to a data recovery company. I've done a little basic board repair before, but nothing this advanced until now. So please forgive my ignorance in advance. 😅

                                            I found the boardview for this laptop in the forums here, and am able to open it on my PC with FlexBV.
                                            https://www.badcaps.net/forum/troubl...-hardware-devi...
                                            05-29-2024, 02:01 PM
                                          • GLISIT
                                            Asus Probook P5440UF-XB74 power issue
                                            by GLISIT
                                            Hi all,

                                            TL;DR - this laptop is driving me nuts with the oddball power-related behaviors. Appreciate any insight you can provide!


                                            I'm experiencing a power issue on an Asus Probook P5440UF-XB74. Although I've worked with electronics and computers for decades, this is my first attempt at getting into motherboard-level component troubleshooting. Any help the community can provide is greatly appreciated!

                                            A few weeks ago I was using the laptop (on battery power) for a Zoom meeting. The battery was running very low (long meeting) but I wasn't worried about...
                                            01-16-2025, 02:29 PM
                                          • sam_sam_sam
                                            Desoldering gun station modified to use a 18 volt @ 20 amp switching power supply
                                            by sam_sam_sam
                                            I have wanting to do this project for quite sometime now and I finally found a switching power supply that will work on this desoldering gun station ZD-915 that the original switching power supply took a shit and just was not worth trying to fix it because this switching power is not quite big enough to handle the heater element and the vacuum pump

                                            One note when I tested the switching power supply and the voltage control board I noticed that this desoldering gun heat up much faster than the original switching power supply which I was really surprised by to the point that I might buy...
                                            03-31-2024, 02:12 PM
                                          • Document Archive
                                            HP Pavilion Power Pavilion Power 15-cb009nl Notebook 15 Specification for Upgrade or Repair
                                            by Document Archive
                                            This specification for the HP Pavilion Power Pavilion Power 15-cb009nl Notebook can be useful for upgrading or repairing a laptop that is not working. As a community we are working through our specifications to add valuable data like the Pavilion Power 15-cb009nl boardview and Pavilion Power 15-cb009nl schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant badcaps forum. Please note that we offer no warranties that...
                                            09-06-2024, 05:59 AM
                                          • Loading...
                                          • No more items.
                                          Working...