Gigabyte GA-7DX+
  • JEWilson
    • Sep 2007
    • 369
    • Scotland, United Kingdom
    Re: Gigabyte GA-7DX+
    Ok
    I purchased a mobile Athlon XP with a Barton Core
    Model # - AXMA2600FKT4C
    Installed in the mobo and posts as a Mobile Athlon 800MHz
    The mobo auto detects the part at six times multiplier.
    The mobo has DIP switches for setting the FSB and the multiplier.
    see attached pdf
    The mobo is set a FSB 133MHz and the multiplier set at auto.
    Problem - When set as above, bios id's mobile athlon 800MHz
    If I manually set the jumper to x12 - the bios id's an Athlon XP 2100+
    Despite repeated attempts, the multiplier cannot synthesis a
    15x mult, that is, the actual multiplier for the Barton XP-M.
    As position 5 is used for auto, the DIP switch has a further position
    6 which appears to be unused. Position 1 is used for a 0.5 mult
    increase.
    So... positions 2, 3 and 4 determine the multiplier and being 8
    possible settings are available, the max. mulitplier on this mobo
    is 12 (plus 0.5 of course for position 1 on the DIP switch).
    This accounts for a mult of 5 to 12 inclusive.
    It appears the auto setting cannot ID the barton XP-M part.
    So... it appears, in order to get the XP-M to be correctly identified,
    I will require to add a microcode update to the BIOS to enable
    the BIOS to do this correctly and automatically
    Any comments to add?
    Thanks for your consideration
    • Scenic
      o.O
      • Sep 2007
      • 2642
      is there any option in the bios to set the FSB? or only by jumper/switch ?
      had those problems on another board.
      but instead of modifying the bios i just set the FSB higher and chose a multiplier that matches the original cpu speed with the FSB..
      example:
      if the Athlon XP-M has 2GHz as real speed (not the + rating):
      166MHz FSB and multiplier 12 -> 2GHz
      the BIOS will still detect the CPU wrong, but it will work at the standard clock speed..
      problem is that you'll need matching RAM for that (166MHz FSB -> DDR333 or DDR266 in async. mode to the FSB.. but this will reduce overall performance)
      BTW: i have lots of socket A boards here... so if u need another board
      edit: i had a board here that used a multiplier solution for multipliers higher than 12x
      for example.. if you set the multiplier to.. um.. 8x it would use a multiplier of 14x if a CPU with this multiplier is used...
      dunno how to explain this in english..
      maybe there's something similar on your board...!?
      edit2: lowering the multiplier will work on most boards allthough the multiplier is locked by the CPU as this lock is only for setting the multiplier higher... not lower..
      • JEWilson
        • Sep 2007
        • 369
        Hi
        Can only set the FSB by DIP switch
        It appears only allows max. of 12.5 per the diagram
        No options in the BIOS to set the multiplier
        Can set the FSB but this mobo is max. 133MHz so cannot
        overclock. Don't want to do that anyway!
        I acknowledge your advice in respect of weird multiplier settings.
        I am beginning to wonder if switch position 6 (not shown
        in the diagram), present in the mobo has something to do
        with a mult over 12.5.
        This is a new mobo but has remained unused for some time.
        I recently recapped it - is working perfectly ok.
        • kikkoman
          • Jul 2007
          • 691
          have you tried changing the multi via software?
          SoftFSB was a good tool. they stopped updating it a while ago, but you may be lucky. depends on the mobo.
          CPUMSR (http://www.cpuheat.wz.cz/html/CPUMSR_main.htm) works fine, too (I think it's a bit more universal).
          "Every normal man must be tempted at times to spit on his hands, hoist the black flag, and begin slitting throats." - H.L. Mencken
          • JEWilson
            • Sep 2007
            • 369
            I should add...
            This being a mobile Barton, it starts a 6x multiplier at POST.
            I believe alternatively, the issue may be Windows 2000 lacks the
            AMD PowerNow! driver and dashboard.
            I will try setting the SW multiplier back to auto, install
            the driver and determine if I can run the PC as always on
            with no battery saving measures.
            I will let you know how I progress.
            • JEWilson
              • Sep 2007
              • 369
              #26
              Update
              The PowerNow! driver require to access to a PowerNow! compliant
              BIOS as with a laptop. As this mobo does not have this feature,
              the driver will not install. So a solution via this route is not available.
              Also, the CPUMSR softFSB util came with a driver for WinXP, installed
              ok (apparently) but, I am using Win2K SP4.
              When I tried to raise the multiplier and apply it, the system locked
              up....
              Reset button and 2 hours of boot time chkdsk's and a boot time registry
              chk and I'm back up again.
              Any other suggestions?
              • zandrax
                Hit and miss
                • Dec 2007
                • 1157
                • Italy
                #27
                No luck: another owner tried to use a mobile Athlon and it booted always at lowest multiplier available (6x).
                My suggestion are updating bios to revision F7 and change the multiplier into OS: beware that most desktop boards aren't as flexible as mobile one and, since AMD specs didn't require a compatibility test, most mobos crash when changing multiplier. Moreover CPUs are unstable at some multiplier, so you have to test all possible combinations then exclude the dangerous ones.
                My favourite tool is RMClock, but CpuMSR is fine too (being Athlon oriented, it may be even better); SoftFSB is unsuitable because it changes the FSB, not the multiplier.
                Zandrax
                Have an happy life.
                • JEWilson
                  • Sep 2007
                  • 369
                  #28
                  I already have the latest BIOS at F8a
                  I also possess the last BIOS at F7 for this mobo
                  Q - If I manually set the DIP SW to a mult of 12 and
                  then I try to raise the mult to 15 - this all that is req'd
                  and AMD CPUInfo does state the max speed is 2.0GHz,
                  will any soft changes to the clock gen interfere with
                  the manual setting of 12?
                  Normally, the mobo is set to auto detect and with
                  the barton XP-M this defaults to a mult of 6 and a
                  speed of 800MHz, would it be better to leave at auto
                  and then attempt to raise the multiplier?
                  Only a guess all the same.
                  Even so, correctly the Barton XP-M is supposed to
                  default to a x6 mult at POST
                  see further http://fab51.com/cpu/guide/cpu_guide1-e.html
                  I'm going to contact Gigabyte on this one as well to establish
                  if a x15 mult or better can be established with the DIP SW.
                  Would appear odd it it were not to as Tbred on auto setting
                  can be detected up to a multiplier of 16x @ XP 2600+/133 or 2.1GHz
                  • zandrax
                    Hit and miss
                    • Dec 2007
                    • 1157
                    • Italy
                    #29
                    If I remember correctly, the multiplier shouldn't be a big issue since the cpu multiplies fsb internally (fixed multiplier for desktop Athlons, range for mobile ones).
                    Honestly I prefer to stictly follow specs on boot, so I'd set the autodetection and let the Athlon boot at 800 MHz (6x133): it shouldn't be too slow (my father owns a notebook with a Mobile Barton 2800+ and it boots at 800 MHz too).
                    Because it recognizes Thoroughbred' cpuid and it implies that switch settings are useful only for boot (internal multiplier).
                    Since you can't use Powernow driver (bios lack the voltage-multiplier table), then use cpumsr: this should work by directly programming both chipset and cpu.
                    Zandrax
                    Have an happy life.
                    • JEWilson
                      • Sep 2007
                      • 369
                      #30
                      I've set the DIP SW back to auto. Starts at x6 mult as expected.
                      I've tried CrystalCPUID and it will raise the multiplier to x15.
                      There is a feature to run it at boot and implement this change.
                      You suggest CPUMSR, is this a better option to follow for Athlons?
                      Please advise.
                      Thanks.
                      • zandrax
                        Hit and miss
                        • Dec 2007
                        • 1157
                        • Italy
                        #31
                        Years ago CPUMSR was the first (and only) solution available to manage Athlon's multipliers,but years passed and its developement stopped: if CrystalCPUID works for you, then keep it because it's more recent and (perhaps) has more features.
                        Zandrax
                        Have an happy life.
                        • JEWilson
                          • Sep 2007
                          • 369
                          #32
                          Y - agreed
                          Tried CPUMSR and killed the PC again.
                          Two hours later... got the PC back on line.
                          • JEWilson
                            • Sep 2007
                            • 369
                            #33
                            Using CrystalCPUID, after applying a mult of x15 by software,
                            I have a very slight overclock condition as with;
                            1. FSB 134.02 MHz as opposed to 133
                            2. DDR FSB 268.05 MHz as opposed to 266.67
                            3. Core speed 2010.4 MHz as opposed to 2000
                            CrystalCPUID reports an overclock of 0.52%
                            Should this be a concern?
                            • kikkoman
                              • Jul 2007
                              • 691
                              #34
                              not really. usually the XP-Ms can take a lot of abuse.
                              if the RAM timings are within specs, it shouldn't be a problem.
                              have you tried how high it goes before it becomes unstable?
                              good to hear that it's finally working. i take it that you didn't update the microcode?
                              • JEWilson
                                • Sep 2007
                                • 369
                                #35
                                The BIOS F8a correctly identifies the new XP-M Barton as
                                a Mobile Athlon at POST
                                F7 does not, it details Unnkown CPU at POST
                                They both support the CPU even so.
                                • JEWilson
                                  • Sep 2007
                                  • 369
                                  #36
                                  As to the matter of the o/c at 0.52%
                                  This system runs a matched pair of Infineon PC2100 ECC Reg
                                  Part # H7S72D64500GR-7-B
                                  The datasheet can be found at
                                  The datasheet details SPD programming at CL2, that is, as with
                                  these DIMMs an fck max. of 133MHz.
                                  Thus, I have had to manually set the CAS Latency to 2.5 in the
                                  BIOS. The datasheet details CL2.5 programming to have an
                                  fck max. of 143MHz.
                                  • JEWilson
                                    • Sep 2007
                                    • 369
                                    #37
                                    I've changed the O/P side of the VRM back to;
                                    10 of 1200uF 6.3V Panasonic FM
                                    The problems have disappeared.
                                    If I want to put polymers in this mobo, will have to consider
                                    installing higher capacitance values.
                                    • gdement
                                      • Jan 2007
                                      • 690
                                      #38
                                      No. Every motherboard is a little off the mark, and there is a reasonable tolerance built in to the specs. If you want to confirm that everything is stable, I'd set the FSB to 138-140MHz (3-5% over) and run stress tests at that speed. If it holds up, then you'll have nothing to worry about at stock speeds over the long term.
                                      fck max. of 143MHz.
                                      I doubt that's really necessary - it's only running very slightly above the 133MHz (I think actually 133.33) rating. See if it passes memtest at ~ 138-140MHz CL2. If it does, you have nothing to worry about.
                                      • DynaxSC
                                        GIGABYTE GA-H110M-S2 - Stuck at Debug Code C2 - don't like Patriot Viper Steel RAM but works with G.SKILL
                                        by DynaxSC
                                        I discovered a strange behaviour of GIGABYTE GA-H110M-S2 board.
                                        General test conditions:
                                        - Tested with Core i5 6500 and Core I7 6700K - no difference
                                        - Default BIOS settings, but tried also altering several memory setting - does not change anything
                                        What is wrong:
                                        With BIOS F1 and F2 the board normally POST's and boots to Windows 11 with 2 x Patriot Viper Steel PVS416G440C9K RAM (4400MHZ, Samsung B-Die chips)
                                        When BIOS upgraded to anything above F2 (ie. F20-F27b) the board POST stucks after 3 Debug Codes on Code C2
                                        03-21-2025, 06:23 PM
                                        Thermal pad thickness for various laptop GPU / Graphics Cards
                                        ASUS Dual RTX 2070 OC 8GB
                                        ASUS ROG STRIX RTX 3080 OC
                                        ASUS ROG STRIX RTX 3090
                                        ASUS TUF Gaming RTX 3080 OC Edition
                                        ASUS TUF GTX 1660 S-O6G GAMING
                                        EVGA RTX 3060 Ti XC GAMING 8GB
                                        EVGA RTX 3060 XC GAMING 12GB GDDR6
                                        EVGA RTX 3080 FTW3 ULTRA GAMING
                                        EVGA RTX 3080 TI FTW3 ULTRA GAMING
                                        EVGA RTX 3090 XC3 ULTRA GAMING 24GB
                                        Gainward RTX 2080 Phoenix GS Specs
                                        Gainward RTX 3070 Phoenix 8GB
                                        Gainward RTX 3080 Ti Phoenix
                                        GIGABYTE AORUS RTX 3080 MASTER 10G
                                        02-09-2024, 08:08 AM
                                        A Dead/DOA Gigabyte GP-P450b 450W ATX PSU
                                        by momaka
                                        More eBay specials: this time a Gigabyte GP-P450b 450W ATX PSU for $8 with free S&H. Listed “For part/not working”, as usual. Showed up in a beat up EVGA box without any padding… but that's understandable given the total price. PSU made it out fine without damage. It's a non-modular (yay!), pretty modern-day looking PSU with a black paint and all black cables (meh, not my favorite, but figure it's good to keep a few of these in case I do need one for a more modern PC build, just so my old gray boxes don't look too odd in there.)
                                        And a shot of the label:...
                                        01-26-2022, 03:26 AM
                                      • nikovmiroslav
                                        Gigabyte A5 X1 Need Bios
                                        by nikovmiroslav
                                        Hi Everyone,I need help with this strange Gigabyte laptop,it turns on with black screen and after 30sec fans on the Max for few seconds and it shuts down,I think the bios is bricked,They say it is Clevo under the hood,there is nowhere on motherboard what is the model which is strange,i will write S/N and P/N from the motherboard,thats only what is writen there and upload old bios,if anyone can help,Thanks!
                                        Gigabyte A5 X1
                                        From motherboard:
                                        S/N: 1TNH55ER1350895
                                        P/N: 6-77-NH55ERQY-D02-2CGB
                                        On sticker from the back of the laptop:
                                        S/N: SN21351J000657...
                                        08-24-2025, 09:15 AM
                                        ACER Veriton M6610G Veriton M i7-2600 Specification for Upgrade or Repair
                                        This specification for the ACER Veriton M6610G can be useful for upgrading or repairing a desktop PC that is not working. As a community we are working through our specifications to add valuable data like the Veriton M6610G boardview and Veriton M6610G schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant badcaps forum. Please note that we offer no warranties that any specification, datasheet, or download for ACER...
                                        09-12-2024, 03:36 PM
