Fixed APC Back UPS RS 1500 LCD (BR1500LCD) w/ 1 bad 22uF 400V cap
  • dchang0
    • Jun 2014
    • 33
    Successful fix report!
    I've got an APC Back UPS RS 1500 LCD (model BR1500LCD) UPS that has served me well for many, many years. My area's known for having bad electrical power that routinely damages computer equipment, so it's been a fantastic investment.
    Over the past few months, I've been hearing the relays click on and off maybe once a day, but since the unit did not actually switch over to battery power, I assumed it was just a typical power cut-out.
    But, finally, it did switch over to battery power on a stormy day when power lines were getting blown down all over the region.
    Unfortunately, it did not come back up when AC power was restored! Other devices were working fine, and no room lights were flickering. One other UPS did also switch over to battery, but it came back up on its own when power was restored. I went through the UPS' LCD display's readings and found that the RS 1500 LCD thought that it was receiving around 77VAC from the wall outlet, even though I could measure the wall voltage as a typical 118VAC.
    The UPS was still supplying the connected computer equipment 115VAC, so I knew that circuit was okay.
    Knowing that if I left this UPS to drain the battery, I could damage the battery permanently, so I shut it down, removed all attached equipment, and removed the battery.
    Then, I opened it up. Remove four Phillips screws from the back panel, and it slides out about 2in. The front panel snaps off--use a plastic spudger to pry it off. It is pretty firmly snapped on.
    Hidden under the front panel are three Phillips screws. In the battery compartment there are two, and that's all of them. The right side (when facing the front of the unit) lifts off.
    On the mainboard, there are roughly a dozen electrolytic caps, most of them small and low-voltage. Nearly all of the ones in my unit were Jamicon, but three were CapXon.
    Yup, sure enough, one of the CapXon caps, the physically biggest one that is marked C69, 22uF 400V, had vented its top. The other two tiny 4.7uF 25V ones looked okay, but I don't trust the CapXon brand, so I went ahead and replaced them too.
    All in all, these are the parts I ordered:
    1x Panasonic EEU-EE2G220S 22uF +/-20% 400V 105C
    2x Nichicon UPW1E4R7MDD 4.7uF +/-20% 25V 105C
    NOTE, I do not know if these caps are the "best" to buy or how long they will last. They seemed to have high enough ripple current ratings and were inexpensive and in-stock, so I ordered them.
    I soldered them in easily, put the UPS back together, and it began working immediately without any trouble.
    For less than $3 in parts, I got my >$150 UPS working again, probably for another many years and saving this from the landfill.
    I did not replace any of the Jamicon caps since they did not seem to have vented and there were so many of them.
  • cyjun1990
    • Jan 2016
    • 16
    • Philippines
    Re: Fixed APC Back UPS RS 1500 LCD (BR1500LCD) w/ 1 bad 22uF 400V cap
    congrats
    • japlytic
      • Oct 2005
      • 2086
      The 400V capacitor was most likely to be working in a hot enclosure, despite the fitted cooling fans.
      • dchang0
        • Jun 2014
        • 33
        Thanks--yes, the unit seems to be poorly-ventilated inside. The fans are all the way at the back, and the vented capacitor is near the middle of the unit. I guess they are counting on a chimney effect when the fans pull air through, but given how little dust was inside the unit after so many years in use, it basically means there is no airflow at all.
        Last night provided a real-world test of the repair. The power went out for about 30min, and the RS 1500 LCD did its job perfectly.
        • Nw8r
          • Feb 2017
          Same problem with mine! Bad 400v 22uf cap and swollen batteries!
          I did some work on the side and top vents. They are molded in the bottom sides near the transformer and on the top. Very fine slots! Little air flow. Reason for little dust. They are so fine, dust will plug them up. I took a broken coping saw blade and cut them open about a 16th of a inch. You get ten times the convection air flow through the unit. It runs a lot cooler!
            Lift Master Garage Door wall switch display / motion sensor controller display disappeared no back light
            by sam_sam_sam
            This happened last Saturday and today I finally had time this morning before I went to work to replace two non brand capacitors
            I will let you be the judge weather or not these are bad or not according to the blue ESR meter that I am using
            I am comparing them to a brand new one that I installed
            The display came back on and the programming was not lost which I was surprised by I would have thought that when the display went blank that so did the memory as well
            I going to let it run for several days before I remount back on the wall next to the...
            09-05-2024, 06:48 PM
            HP ProDesk 600 G5 + APC Back-UPS 700VA ProDesk 600 i5-9500 Specification for Upgrade or Repair
            This specification for the HP ProDesk 600 G5 + APC Back-UPS 700VA can be useful for upgrading or repairing a desktop PC that is not working. As a community we are working through our specifications to add valuable data like the ProDesk 600 G5 + APC Back-UPS 700VA boardview and ProDesk 600 G5 + APC Back-UPS 700VA schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant badcaps forum. Please note that we offer no warranties...
            09-12-2024, 02:30 PM
            HP ProDesk 600 G5 + APC Back-UPS 700VA ProDesk 600 i7-9700 Specification for Upgrade or Repair
            HP ProBook 430 G7 + APC Back-UPS 700VA Notebook 400 Specification for Upgrade or Repair
            This specification for the HP ProBook 430 G7 + APC Back-UPS 700VA Notebook can be useful for upgrading or repairing a laptop that is not working. As a community we are working through our specifications to add valuable data like the 430 G7 + APC Back-UPS 700VA boardview and 430 G7 + APC Back-UPS 700VA schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant badcaps forum. Please note that we offer no warranties that...
            09-06-2024, 08:10 PM
