    #61
    Re: APC UPS units - troubleshooting

    Also what can you guys say about

    CSB-HR1251WF2 - 12V 12.75Ah 51W Pb CSB - 37.36 €
    CSB-GPL12120 - 12V 12Ah F2 Pb CSB - 40.84 €
    CSB-EVH12150 (blue one) - 48.66 €

    I always thought that deep cycle is better hence the higher price for EVH version. Then how come they rate the HR 8 years (plain marketing nonsense ?), the

    The usual CSB-GP12120 is 37.50 € same as YUASA NP1212, but YUASA has additional membrane that prevents evaporation, CSB does not. Hmm....

    Is there some site where I could see dissembled new batteries from CSB, YUASA etc. and to see that it's really different products, not just marketing nonsense.....

    Comment


      #62
      Re: APC UPS units - troubleshooting

      i find that Yuasa Batteries specially the NPX series are higher quality than the batteries offered by CSB.
      the NPX series from Yuasa are made for higher depth of dicharge and oftimized for standby use.
      the equivalent to a NP9-12 (12v9ah) is a NPX35
      Last edited by sadeoo7; 03-03-2016, 01:43 AM.

      Comment


        #63
        Re: APC UPS units - troubleshooting

        Deep cycle, or cycle-use batteries are better for different kind of use, especially for different kinds of go-carts (like golf carts, baby cars etc. etc.) where you regularly do full discharge and full charge cycle.

        For UPS I'd take if any, than high-rate. Those are usually of higher quality and should provide higher currents - neccessary for high-loads of the UPS when there is often as much as 40 A draw.
        Less jewellery, more gold into electrotech industry! Half of the computer problems is caused by bad contacts

        Exclusive caps, meters and more!
        Hardware Insights - power supply reviews and more!

        Comment


          #64
          Re: APC UPS units - troubleshooting

          i said that they where optimized for a higher depth of discharge but the NPX series are in fact high rate. sorry for my mistake.
          here is the datasheet if you want to check them out
          https://cdn.badcaps-static.com/pdfs/...f090d72a8a.pdf

          Comment


            #65
            Re: APC UPS units - troubleshooting

            Originally posted by smile View Post
            I found pcb schematic, the battery is charged by LM78M15, 0.5A max.
            The schematic shows 2 diodes (D18 and D2) that are connected to OUT pin one after another. This lowers voltage as diodes have voltage drop.

            I added third diode (in a row to them) and now I have steady 13.00 - 13.09 Volts varies with AC voltage.
            So now my batteries will no longer dry out !
            I think this may be the key to a problem I'm having with the charging circuit on an APC BE500R. I've taken this device on as a science experiment rather than to save it; it's a mostly worthless device but what better to learn on? I'm $25 into this.

            I'd surmised that charging wasn't derived from the switching supply; the inverter is working fine with an externally charged battery. I'm very excited to learn that this positive regulator is likely a place to begin looking! Nothing on the board looks blown, but the LM78M15 looks like it has been hot at some point!

            Do you guys generally make extensions to the connectors to work these devices live? Given the short leads, this may be my only option.

            I will next probe the VR and I'm still waiting for a 220uF 50v cap which lives nearby and looks to be relevant.

            Any help full thoughts other than don't electrocute myself?

            Thanks, Paul
            Attached Files

            Comment


              #66
              Re: APC UPS units - troubleshooting

              This is some older design, the later CyberFort II units (Back-UPS something) used SMPS for charging. It has to take the voltage from the battery.

              In those newer designs the small caps almost always go bad. Check them too, there will definitelly be some feedback for the microprocessor.
              Less jewellery, more gold into electrotech industry! Half of the computer problems is caused by bad contacts

              Exclusive caps, meters and more!
              Hardware Insights - power supply reviews and more!

              Comment


                #67
                Re: APC UPS units - troubleshooting

                Thank you! Bhemot, I've replaced 8 of 10 electrolyics so far. I'll replace the last two in the next couple of days. It's good to know that some designs do charge from the SMPS. This unit was, in hind sight, probably a good starting point. At least I recognize the components in a full wave rectifier PS. SMT would seem to make repair considerably more challenging. I'm vaguely following so far. As long as I don't need to do anything with an SMT device, I'm happy.

                Comment


                  #68
                  Re: APC UPS units - troubleshooting

                  Sorry, I meant from the transformer, to feed the battery. Indeed, this linear regulator design is very ineffective (but easy and cheap). APC abandonded that very long time ago. Yet all the cheap plastic units of (most likely) Must Power origin use this in 2016. Sometimes the regulators overheat so badly they bake the board around them with all the caps. I think this is connected to particular revision/version of the board. They also use aluminium wires for the main transformer.

                  It was very pitiful display at CeBIT - there was like 6 to 8, companies, including Delta Electronics, some others calling themselves OEM supplier, and EVERY SINGLE ONE OF THEM had that thing in their portfolio. They are all the same (besides the configuration of sockets and the front panel - OFC every one has to look slightly "different", but you can recognize that on first look). So bad units and they even argue with you that they definitelly "design and manufacturer" that by themselves.

                  But somehow could not explain why 5 more companies around them have the same units and they don't make it for them And why all the other units in their portfolio - why I am positive actually aretheir own designs and made in their fabs - look completelly different I mean even low-end and high-end units from Eaton or APC share similarities among them. These chinese rebrands are completelly different than everything else they got. But they definitelly make that on their own

                  Well, I guess they can have it licensed…but than, another thing I noticed: all of them regardless the brand also have the same label sticker on the top-back part, which is the same style (color, font, layout, everything) for all, only the brand name is different. Yeah, they make it my ass As even Delta is just sourcing it from other fab as it makes more sense to buy this cheap crap and make high-quality units in their own tier 1 lines, those ppl either did not *really* know or they new but could not tell. But even arguing with me telling me those lies to my own face after SO MANY of them I have seen with my own eyes, man…

                  For example, check the Sweex http://www.sweex.com/nl/notebook-pc-...res/ups/PP200/

                  They are made both as off-line and line-interactive, this single-battery and also two-battery versions. 1500-2000VA models use small fan in the backside.
                  Last edited by Behemot; 03-17-2016, 11:53 AM.
                  Less jewellery, more gold into electrotech industry! Half of the computer problems is caused by bad contacts

                  Exclusive caps, meters and more!
                  Hardware Insights - power supply reviews and more!

                  Comment


                    #69
                    Re: APC UPS units - troubleshooting

                    I'm still waiting to receive the filter cap for the 15v linear supply but I have a question related to UPS design theory. I have 15.1v at the output of the 15v voltage regulator which is all good.

                    The positive battery lead comes from the transformer. As far as I knew, you can't use a transformer for DC. How is this part of the charging circuit working? I understand the basic linear supply with bridge rectifier/voltage regulator chip/blocking diode, but the transformer has me stumped.

                    The negative lead comes from the PC board.

                    Are they using a winding as a choke?

                    Thanks, in advance!

                    Paul

                    Comment


                      #70
                      Re: APC UPS units - troubleshooting

                      Isn't there some diode? BTW often there is separate winding just for some low voltage…you don't need much power from that, just like an amp or so.
                      Less jewellery, more gold into electrotech industry! Half of the computer problems is caused by bad contacts

                      Exclusive caps, meters and more!
                      Hardware Insights - power supply reviews and more!

                      Comment


                        #71
                        Re: APC UPS units - troubleshooting

                        I think I can answer my own question. It looks like it could be a center tap but I'm not clear why it would be on the positive lead.

                        Comment


                          #72
                          Re: APC UPS units - troubleshooting

                          Definitely no inline diode from the transformer. I'm certainly learning as I go.

                          Comment


                            #73
                            Re: APC UPS units - troubleshooting

                            After recapping I started wondering if I wasn't getting charging because of a flakey 7815 as the old one looked as though it had gotten hot. I replaced it and it's charging now! It gets pretty hot when it starts charging so I added a heat sink. As battery voltage comes up, it gets less hot. Still not clear if there is something defective upstream causing the heat other than the inherent inefficiently of these linear supplies, but I buttoned it back up and we'll see. You may be able to see the heatsink in the attached photo. Paul
                            Attached Files

                            Comment


                              #74
                              Re: APC UPS units - troubleshooting

                              What's its input voltage?
                              Less jewellery, more gold into electrotech industry! Half of the computer problems is caused by bad contacts

                              Exclusive caps, meters and more!
                              Hardware Insights - power supply reviews and more!

                              Comment


                                #75
                                Re: APC UPS units - troubleshooting

                                At 24v in, I thought it was a little high but within range of the regulator's capability. I have been learning how inefficient these chips are especially when the input and output voltage is large. I pretty much decided that there was a small on-board transformer supplying 4 diodes to rectify the AC and that was it. If there was a mechanism to reduce or fine tune the input voltage to the regulator, I couldn't figure out where it was. You mentioned how crude these things were in a previous post and I'm inclined to agree. (Which in my case isn't a bad thing or I wouldn't have a hope of shooting this thing!)

                                Should I be looking for something upstream of the regulator or does this sound like it's working as intended?


                                Thanks for your interest and comments.

                                Paul

                                Comment


                                  #76
                                  Re: APC UPS units - troubleshooting

                                  24Vin and 15Vout so the Vdrops on the regulator will be = 24V - 15V = 9V, so if the batteries is really low and being charged if the charging current is lets say 1A, the IC will have to dissipate 9V x 1A = 9W, so yes, it will get really hot at the beginning of the charging and may go into thermal shutdown, or if the batteries have shorted cells, that will be bad also.
                                  Heat sink needed and should drop the input Voltage.
                                  Never stop learning
                                  Basic LCD TV and Monitor troubleshooting guides.
                                  http://www.badcaps.net/forum/showthr...956#post305956

                                  Voltage Regulator (LDO) testing:
                                  http://www.badcaps.net/forum/showthr...999#post300999

                                  Inverter testing using old CFL:
                                  http://www.badcaps.net/forum/showthr...er+testing+cfl

                                  Tear down pictures : Hit the ">" Show Albums and stories" on the left side
                                  http://s807.photobucket.com/user/budm/library/

                                  TV Factory reset codes listing:
                                  http://www.badcaps.net/forum/showthread.php?t=24809

                                  Comment


                                    #77
                                    Re: APC UPS units - troubleshooting

                                    At 24 V, it has to burn down over 10 V (to about 13.8 V), at 1 A that equals 10+ W. With no heatsink you can imagine how hot the TO-220 package was getting.

                                    edit: yo bud, you pay the beer m8

                                    as soon as I get better, with my current headache that would kill me, oh my
                                    Last edited by Behemot; 04-06-2016, 10:28 AM.
                                    Less jewellery, more gold into electrotech industry! Half of the computer problems is caused by bad contacts

                                    Exclusive caps, meters and more!
                                    Hardware Insights - power supply reviews and more!

                                    Comment


                                      #78
                                      Re: APC UPS units - troubleshooting

                                      So sorry about the head ache. Take care of yourself. Absolutely will buy the beer when I get to Prague or you get to California. P

                                      Comment


                                        #79
                                        Re: APC UPS units - troubleshooting

                                        Nah it was for budm, there is this game when two ppl say the same at the same moment, the first one who calls the other to pay the beer should get one

                                        You can try dropping the voltage with a few diodes in series with the regulator input, though there is not too much space inside. And also I just realized there is no capacitor between the diodes and the regulator to smooth it's input? In that case the regulator is also stressed with smoothing the rectified spikes.
                                        Less jewellery, more gold into electrotech industry! Half of the computer problems is caused by bad contacts

                                        Exclusive caps, meters and more!
                                        Hardware Insights - power supply reviews and more!

                                        Comment


                                          #80
                                          Re: APC UPS units - troubleshooting

                                          My APC BE500R UPS is much smaller than some of those shown here... It has a single 7.2A 12 V SLA battery.

                                          It's been sitting unused since we moved house in June last year.

                                          I went to plug it in today and it shows no signs of life - the power LED doesn't come on.

                                          There's definitely power at the end of the lead, the thermal shut-off is closed and power gets to the main board.

                                          It was working when we packed it up, back in it's original box.

                                          The battery is toast - reading 4v. I will put it on my smart charger and see if I can resurrect it But...

                                          Shouldn't the LED light when power is on, even if the battery is done in?

                                          I'm new to this electronics lark, but know my way round a multimeter... and armed with 'How to Diagnose and Fix Everything Electronic', I'm willing to have a go - but if there are some FYIs with APC consumer UPS's, I'm all ears.

                                          Comment