Allen-Bradley SLC 500 PLC —> CPU fault what does mean
    • Jul 2011
    • 6045
    If you do not have the E-rom chip it gives you this error light ON
    If you put the E-rom chip in the unit the run light come on and CPU fault light is on
    This PLC is outside of the machine when testing it
    Does this matter if outside of the machine to get this CPU fault light to be ON
    • Jul 2011
    • 6045
    Re: Allen-Bradley SLC 500 PLC —> CPU fault what does mean
    I found out why the CPU fault light is on
    Look at the picture of the ic chip
    • Topcat
      The Boss Stooge
      • Oct 2003
      • 16958
      I dont think that one is going to make it. Going to attempt to find a replacement?
      <--- Badcaps.net Founder
      Badcaps.net Services:
      Motherboard Repair Services
      http://folding.stanford.edu/
      Team : 49813
      Join in!!
      Team Stats
        • Jul 2011
        • 6045
        Re: Allen-Bradley SLC 500 PLC —&gt; CPU fault what does mean
        You are so very right about this
        So far I have not much luck yet still working on it
        • R_J
          • Jun 2012
          • 9557
          I don't think you will find a replacement ic, easier to find a used SLC500
          It might be a OKI M82C55A-2 ; MSM82C55A-2 QFP44.
          or AT89S52-24AU
            • Jul 2011
            • 6045
            or AT89S52-24AU
            I trying to find a used one that does not have a CPU fault error
            I am just going to use it for parts
            Thanks for the information
            • Curious.George
              • Nov 2011
              • 2305
              • Unknown
              I'd be looking to see what has caused this. The chip, on its own, would hardly experience such a fault.
              Does this connect to the field or any "high-er voltage/power" devices, elsewhere?
                • Jul 2011
                • 6045
                This machine has it own 24 volt power supply ( transformer type ) that is not regulated and has 120 volt transformer that is step down from 480 volt main power supply to the machine
                I have try to figure out what part of the switch controls to this part of the circuit board and see if one the 24 volt transformer is having some type of issue before I put in another PLC unit
                This area where I work the power company has issues with power brown outs on one or more phases not a total brown out but a phase in balance of any where from 3 to sometimes more than 8 % enough to see light dim
                It is not unheard of us losing a phase for some time and then we have to call the power company and let them know that we lost a phase
                • redwire
                  • Dec 2010
                  • 3910
                  The site's dirty power could make a big surge between two phases, or to ground. You might have an issue with bad grounds between mains power, the PLC and the I/O.
                  The control transformer (480-120V) primary could be wired Delta or Wye, and a Delta could go overvoltage if one phase got lost. NEC requires a control transformer (480-120V) secondary to be grounded, so the PLC power should have a neutral/ground there.
                  The 24VAC transformer I would see if the secondary is grounded somewhere or it is floating?
                  I would find out why the chip blew up on the CPU module. That looks like a good surge hit it.
                  If an I/O card got zapped or is shorted, it could put high voltage on the backplane back to the CPU module.
                  It's something I would also check, so the replacement CPU card doesn't get damaged.
                    • Jul 2011
                    • 6045
                    The power company sends power that sometimes is not very good
                    Here is why I say it not unheard of that you will hear a jack fuse blow down the street and we loose a phase of our incoming power from the power company
                    Down the street there are automatic feeders that switch from one feeder line to another we have had where it has gone crazy and put us in dark brown out to no power right back to power and may do this 3 or times in a row
                    I have had to call the power company about this before
                    I have even have had this happen at my house
                    Now do not get me wrong it does not happen very often but it has happened before
                    But what happens more often is that I have work at night when the power has brown out but where does not go out completely it does not do this on all phases at the same time
                    It has happened in daytime as well and it might do a few times in a row then settle down for awhile and do samething again some time later in day again
                    I have sat in the break where there drink machines are and I can tell when the power is not stable because the compressor motor start changing pitch and sometimes it does for few minutes to sometimes for hours this not all the time but it happens
                    Today I was in the main office and I sitting at the computer and could hear the transformer for the battery back up unit humming a lot more than normal most of the time I do not hear it
                    I actually got up and went to where the battery back up unit to if I could hear it changing pitching which it sometimes it has done before
                      • Jul 2011
                      • 6045
                      My luck finding a good working PLC is not very very good
                      I have one more of them coming and then I have to go different route
                      Two for less than $30.00 each two at about $55.00 each
                      One of the $50.00 I returned to the seller for a refund
                      The last one that I bought was $75.00 the seller tell me that this one the CPU fault light is not ON or flashing so we will see what happens with this one
                      There is a company called OneStop that I used them before and they were able to help with another PLC for one of our other machines
                      That had a very unusual fault it would run for a while and then just shut down then when power cycle the machine it might come right back ON and sometimes it would take a while for it to come back ON
                      I had to change the power supply board and the PLC has been working very good for at least 3 years now
                      But the problem with using them is that it takes a while to get the remanufactured PLC and I will have to send them the E-Rom chip to make sure that it works correctly or not
                      It would take about 10 working days before I would have one that if the they get a working one or not
                      The cost of a remanufactued is about $400.00 plus the fee for making sure that the PLC works with the E-Rom chip plus the cost of the E-Rom chip from the machine manufacturer will cost any where from $200.00 to 400.00 so maybe for about $1000.00 compared to $6000.00 for a retro fit PLC plus installation cost could be any where $2000.00 to $4000.00
                      The power supply board seems to have a shorted rectifier and seems to have a shorted switching power regulator ic chip and what else I do not know yet I have not gotten that far yet
                      So I do not trust weather or the E-Rom chip is good or not
                      This machine was made in 2008
                      • TechGeek
                        Computer Geek
                        • Jan 2015
                        • 2254
                        While you're at it, PLEASE install some kind of filtering device between the AC powerline and the PLC.
                        Permanently Retired Systems:
                        Kooky and Kool Systems
                        sigpic
                        • eccerr0r
                          Solder Sloth
                          • Nov 2012
                          • 8701
                          That's weird, never thought to see of low power CPU chips blow chunks. The bond wires are much thinner than of power transistors and die bonds will fail fairly readily?
                          But anyway, chances of finding a replacement IC is going to be problematic because it looks like it indeed is a QFP 8051 OTP/mask programmed microcontroller and not an 8255.
                          Time to redesign the whole system ... ?
                          • redwire
                            • Dec 2010
                            • 3910
                            If a power suppy and CPU are dead from some thunderbolt, it's time to add transient protection.
                            If the PLC is powered from one phase and any inputs are off another phase, that can cause the same damage and kill input/output cards.
                            You can get SPD's (surge prot devices) which are MOV's as 480V 3-phase Wye power protectors, they are not super rugged, just ordinary MOV's with fuse and LED's to go in the panel. Better than nothing.
                            Schneider SDSA4040
                            Eaton surge protection
                              • Jul 2011
                              • 6045
                              This is an interesting point and this might be the case It would not be easy to change it because not every thing is in one cabinet
                              There was no thunder storm that day so I do not know what happened to the PLC
                              However the week before I had some problems getting the PLC to come on I do not know if this is related or not
                              However that chip that has the hole in it seems to control the outputs on main part of the PLC because all the output LED lights are all ON
                              Not only that the POWDER light the RUN light the CPU light the FORCED I/O light are all ON
                              When you first turn on the PLC light and CPU light are on then the other two comes a few seconds later ( this is with out the E-Rom chip in it but it does the same thing with it in there )
                              I am also thinking that the auxiliary output card may have a problem as well because one or two of output LEDs lights are also and it did not matter which PLC I put it in but even those PLCs had the CPU was on so it might not mean anything but we will have to wait until I have a working PLC unit to see what other damage was done
                              One more thing is that the switching power supply the switching power regulator ic chip was shorted on the output pins to the transformer which could have power surge the voltage on the power supply
                              I replaced the switching power regulator ic chip and the optic sensor and the power supply came back to life and I also recapped the board I ran the power supply for at least 2 hours with no problems
                              • redwire
                                • Dec 2010
                                • 3910
                                By thunderbolt I meant a big mains transient, as if Zeus tossed a thunderbolt.
                                I think it's worth it to look at the aux output card, if it's damaged then for sure you need some transient protection. The surge could come in there or on AC power.
                                Note Allen Bradley 1992 changed the SLC 500 series chassis wiring, series A had smokable resistor, series B has a 1MEG so the 24VDC side is almost floating. AB recommends DC Neutral connected to earth ground.
                                  • Jul 2011
                                  • 6045
                                  Do you have a website link where they talk about these changes that were made and why I would be interested in reading this
                                  Thanks for for sharing this information
                                  • redwire
                                    • Dec 2010
                                    • 3910
                                    It was in Allen-Bradly backplane documentation but I forgot it. https://ab.rockwellautomation.com/Pr...#documentation
                                    SLC 500 Modular Hardware Style user manual, Grounding guidelines
                                    SLC 500 Fixed Hardware Style install and operation manual, Grounding guidelines
                                    They have an entire doc 1770-4.1 on grounding PLC's. That has a lot of MOV's too.
                                      • Jul 2011
                                      • 6045
                                      I did get a PLC that seems to work but I do not know what is on the E-Rom but it power ON and turn on 3 relays and I put it in 2 other PLC and it does get the same exact results all three of them
                                      So I have come to the conclusion that the E-Rom ic chip has something wrong with and another PLC E-Rom ic chip does not work correctly either
                                      So now I have to request a new E-Rom from the machine manufacturer
                                      The auxiliary input and output cards might not be good either but I do not have a definite answer to this question until I have a new E-Rom chip
                                      One note
                                      In the manual it does mention that if the CPU fault is ON that you might have a bad E-Rom chip
                                      But the way it worded it says control chip I am wondering if it the same thing
                                        • Jul 2011
                                        • 6045
                                        Ouch this hurts
                                        I got in touch with the machine manufacturer and when I saw this quote I almost fell over
                                        $1200.00 something for E-Prom ic chip
                                        I wonder if this is because it is obsolete item and they know it and we are paying it
                                        I have bought E-Rom ic chip before for there micro computer boards and there prices where a little high but not this bad
                                          Lithonia Lighting versus Light of America Compact Fluorescent product quality
                                          I have a Lithonia Lighting 65-Watt Gray Hardwired Compact Fluorescent
                                          I also have back when Light of America had these light bulbs available for yard lights
                                          The issue with Light of America was the blast boards had all most certain board failure while bulbs hardly ever fail
                                          While the Lithonia lighting fixture has all most certain bulb failure
                                          So I have modified the Lithonia lighting fixture to accept the Light of America light bulb and see how long this will last
                                          I have only had this light fixture for not more than a year if it...
                                          07-02-2023, 03:45 PM
                                          LG Gram Ultra-light Weight Notebook Specification for Upgrade or Repair
                                          This specification for the LG Gram Ultra-light Weight Notebook can be useful for upgrading or repairing a laptop that is not working. As a community we are working through our specifications to add valuable data like the Ultra-light Weight boardview and Ultra-light Weight schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant badcaps forum. Please note that we offer no warranties that any specification, datasheet,...
                                          09-07-2024, 03:40 AM
                                          LG Gram Ultra-Light Laptop Notebook Specification for Upgrade or Repair
                                          This specification for the LG Gram Ultra-Light Laptop Notebook can be useful for upgrading or repairing a laptop that is not working. As a community we are working through our specifications to add valuable data like the Ultra-Light Laptop boardview and Ultra-Light Laptop schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant badcaps forum. Please note that we offer no warranties that any specification, datasheet,...
                                          09-06-2024, 09:10 PM
                                          09-06-2024, 08:40 PM
                                        • serious_electron
                                          Strange! Acer laptop not powering on but charging the battery (orange light on when charger and battery plugged in).
                                          by serious_electron
                                          Hello Everyone!
                                          I have an Acer Aspire A315-42 laptop. I generally leave it on for long time by closing down its lid (so it enters the sleep mode). Recently, it rained quite heavily in out area. And the humidity and moisture seem to be high. So one late evening, after I opened the lid and turned on the laptop, it did power on as the blue light turned on but after it booted to the desktop screen, just 5-10 seconds after both the screen and blue light went out and laptop shut down (the blue power light turned orange). And after 2-4 seconds that orange light went off and the laptop died.
                                          06-28-2025, 02:57 PM