Re: New electric panel.
You can use free schematic software for making the drawings.
http://www.digikey.com/schemeit/project/
or just search for 'free home wiring diagram software'
New electric panel.
Collapse
X
-
Re: New electric panel.
Budm, do you or anyone else know of any good free software to do that kinda stuff? I'll map it out on paper if I have to, but I thought it'd be nice to be able to have a digital layout of the house, with the wiring and stuff like that.Leave a comment:
-
Re: New electric panel.
You should map out your house wring so it will make it easier to see what you have an what you will want to have.
"On a kitchen circuit I would put the microwave on one circuit, the Refrigerator on another circuit and the counter plugs on another." That is good suggestion.Leave a comment:
-
Re: New electric panel.
I contacted the company again and asked them about their combination arc fault breakers and explained how a couple of people said they were tripping a couple times a week. The company responded and said their products go through rigorous testing and if they're tripping, it's more than likely because of too high a load.
So, what you say here Keeney123, to me, makes sense. If I'm understanding the company correctly, there's just too many loads on a circuit. If that is correct then, I might have a real problem. We have a two story house with a full unfinished basement and an attic but only 17 circuits. Our old one story house had a heck of a lot more. Every room minus the bathrooms and kitchen have a ceiling fan and there's at least one outlet per wall. There's 8 receptacles and 7 switches just in the kitchen. We have a microwave, a natural gas stove, a dishwasher and a refrigerator in the kitchen that all use electric. There's four lights in the kitchen. One of the switches also controls the backyard light. I'm wondering if the whole kitchen is hooked just to one breaker. If it is, I bet that would be enough draw to trip a combination arc fault breaker all the time.
If it is, how do I fix that? The previous owners took down the lathe and plaster and put up drywall. When we were running the various low-voltage wires to the baby's room, the fish line or whatever it's called got stuck. We had to go into the master bedroom and cut into the lathe and plaster there (the closest still have it, drywall everywhere else though). I noticed the electrical wire for the outlet has those white plastic staples. That means when they tore down the lathe and plaster and removed the knob and tube wiring and put in the Romex, they used the plastic staples. I'm assuming they used them in every room.
If I tried running new Romex for some of the outlets / receptacles / etc, can I just pull it through or would I need to use those white plastic staples every x amount of feet? You know, so if the kitchen is all on one breaker, I could split it and maybe have it on two or three breakers...Last edited by keeney123; 10-28-2016, 04:20 PM.Leave a comment:
-
Re: New electric panel.
So, what you say here Keeney123, to me, makes sense. If I'm understanding the company correctly, there's just too many loads on a circuit. If that is correct then, I might have a real problem. We have a two story house with a full unfinished basement and an attic but only 17 circuits. Our old one story house had a heck of a lot more. Every room minus the bathrooms and kitchen have a ceiling fan and there's at least one outlet per wall. There's 8 receptacles and 7 switches just in the kitchen. We have a microwave, a natural gas stove, a dishwasher and a refrigerator in the kitchen that all use electric. There's four lights in the kitchen. One of the switches also controls the backyard light. I'm wondering if the whole kitchen is hooked just to one breaker. If it is, I bet that would be enough draw to trip a combination arc fault breaker all the time.
If it is, how do I fix that? The previous owners took down the lathe and plaster and put up drywall. When we were running the various low-voltage wires to the baby's room, the fish line or whatever it's called got stuck. We had to go into the master bedroom and cut into the lathe and plaster there (the closest still have it, drywall everywhere else though). I noticed the electrical wire for the outlet has those white plastic staples. That means when they tore down the lathe and plaster and removed the knob and tube wiring and put in the Romex, they used the plastic staples. I'm assuming they used them in every room.
If I tried running new Romex for some of the outlets / receptacles / etc, can I just pull it through or would I need to use those white plastic staples every x amount of feet? You know, so if the kitchen is all on one breaker, I could split it and maybe have it on two or three breakers...Leave a comment:
-
Re: New electric panel.
You probably have no choice about using AFCI breakers if you replace the panel because the current electrical code (2014 NEC) requires them. Contact your local building inspector if you have questions about that.Last edited by Uniballer; 10-27-2016, 10:41 AM.Leave a comment:
-
Re: New electric panel.
The apartment I had in Seattle had arc fault breakers. Only time one trip is when I was working on a shop vac and forgot to unplug it. I felt the surge of current then it tripped.Leave a comment:
-
Re: New electric panel.
it wouldnt surprise me if psu PFC circuits could trip one.Leave a comment:
-
Re: New electric panel.
Is this with all AFCIs or just the Square D that go with the QO panels? Also, what's rfi and 40m? Thanks.Leave a comment:
-
Re: New electric panel.
the problem, is that they either trip, or they dont.
you cant "choose" which arc's they detect and which they ignore.
that's why we dont use them in Europe.
infact the only time i ever saw one was when an inline one was sent out by microsoft so they wouldnt have to recall combusting x-boxes!
i didnt use that either - i just resoldered the x-box psu instead.
btw, boiler ignition units will probably trip them!
I was thinking maybe if there's a rush of current or something, they might trip. Would my BGA rework station cause them trip? It demands a good bit of power. Do vacuum cleaners still cause them to trip? From the post I read, the guy was saying it was just the Square D that he was having issues with and was going to switch to another brand. I still haven't checked, but I might not have a choice and I might have to use arc-fault breakers.
I'm really leaning towards the Square D plug-on neutral ones but if they're still a bit buggy, I don't want to drop 1,500$ or so and then find out. I don't think I'll be able to return them after installing them.Leave a comment:
-
Re: New electric panel.
had lots of issues with afci here.
i tried a few that came with a qo panel.
rfi would trip them esp 40m at 100w.
my neighbor installed a new panel and i could trip his too.
they are far from ready for mainstream use.took em back out.
great idea thats not perfected yet.Leave a comment:
-
Re: New electric panel.
the problem, is that they either trip, or they dont.
you cant "choose" which arc's they detect and which they ignore.
that's why we dont use them in Europe.
infact the only time i ever saw one was when an inline one was sent out by microsoft so they wouldnt have to recall combusting x-boxes!
i didnt use that either - i just resoldered the x-box psu instead.
btw, boiler ignition units will probably trip them!Leave a comment:
-
Re: New electric panel.
It's a mega family of QO Load Centers and a bit confusing:
"Aluminum bus construction on fixed mains panels"
"Shielded one-piece plated copper bus construction on convertible mains panels"
Catalog Number-> Special Construction -CU "Copper Bussing" {option}
"Model # QO142M200PC Convertible Mains – Factory-Installed Main Circuit Breaker
QOM2 Main Frame Size – Convertible to Main Lugs or Lower Amperage Main Circuit Breaker – Copper Bus"
So it looks like a copper bus model. Confusing they have aluminum bus and optional copper bus in the same product family.
The Plug-on Neutral looks like a time saver but does it take that long to cut and strip a neutral connection? You have to cut and strip the hots. I don't see much of an advantage there, but I do like to wire things up...
I can understand maybe a halogen light or something tripping a breaker, but if our vacuum cleaner or my rework station or our PCs are going to trip them, that's going to be an issue. I need to see if arc fault are really required in this area or not. If they're not, maybe I'll just go for the GFCI breakers.Leave a comment:
-
Re: New electric panel.
It's a mega family of QO Load Centers and a bit confusing:
"Aluminum bus construction on fixed mains panels"
"Shielded one-piece plated copper bus construction on convertible mains panels"
Catalog Number-> Special Construction -CU "Copper Bussing" {option}
"Model # QO142M200PC Convertible Mains – Factory-Installed Main Circuit Breaker
QOM2 Main Frame Size – Convertible to Main Lugs or Lower Amperage Main Circuit Breaker – Copper Bus"
So it looks like a copper bus model. Confusing they have aluminum bus and optional copper bus in the same product family.
The Plug-on Neutral looks like a time saver but does it take that long to cut and strip a neutral connection? You have to cut and strip the hots. I don't see much of an advantage there, but I do like to wire things up...Leave a comment:
-
Re: New electric panel.
Schneider Electric has answered my e-mail. They say:
Code:...all of our QO load centers have a copper bus.
Thanks.Leave a comment:
-
Re: New electric panel.
Code:...all of our QO load centers have a copper bus.
Thanks.Leave a comment:
-
Re: New electric panel.
I do not think it was I who suggested about the panel sensing circuit. I would however contact these people before I made any decision on what to buy. http://ubicomplab.cs.washington.edu/Leave a comment:
-
Re: New electric panel.
I do not think it was I who suggested about the panel sensing circuit. I would however contact these people before I made any decision on what to buy. http://ubicomplab.cs.washington.edu/Leave a comment:
-
Re: New electric panel.
I think you will find that info here http://www.schneider-electric.us/en/...nt/0600DB0201/
I would call up Graybar tell them what your doing and see if they can set you up with a good price.
I'll look into Graybar as well. I'm waiting on Schneider Electric to get back to me. I asked them a question or two and want to see what they say first.
I wonder if I could install one of those BCMs (circuit breaker communications module). From the PDF you linked, if I understand it correctly, it'll hook the circuit breakers up to a network. I'm looking at them as kinda like a managed switch, where you can turn ports on and off, configure their speed, make them full duplex / half duplex, whatever.
It'd be cool if I could monitor the breakers, see which ones are active, which ones have tripped, how much amperage is being drawn, etc. For a fairly big two story house, we only have 17 circuits. To me, that just seemed a little small. Our old house, being single story, had a 40 space panel. All spaces were populated but a few breakers weren't being used. As far as I can tell, every wall in every room has at least one outlet on it. Excluding the basement and the attic, there's 9 rooms total. But there's also outlets in the attic, in the basement and in the hallway upstairs. Just about every room (except for the bathrooms and the kitchen) have ceiling fans. Every breaker is 20-amp, minus the one 60-amp.Leave a comment:
-
Re: New electric panel.
Keeney123, what's the difference between a circuit breaker and a miniature circuit breaker? I'm looking at the site you linked me too (I was searching it before I clicked your link).
I see stuff like this:
http://www.schneider-electric.us/en/...rcuit-breakers
Is that 480$ for just one 40-amp 2-pole breaker? That's really expensive. On HomeDepot, for the arc-fault / GFCI combo 30-amp, I think it was around 90$. I couldn't find any plug-on type arc-fault / GFCI 2-pole breakers though and I couldn't find anything higher than 30-amp for the dual pole arc-fault / GFCI combo breakers.
Also, what do you think the 10k and 22k AIR thing means? I just found this:
http://www.productinfo.schneider-ele...000056449.xml#
Which shows they don't make a dual-function plug-on neutral 2-pole breaker of any size. They do make a 15-amp and a 20-amp arc-fault with pigtails circuit breaker though, part numbers:
Code:QO215CAFI QO220CAFI QO215VHCAFI QO220VHCAFI
I would call up Graybar tell them what your doing and see if they can set you up with a good price.Leave a comment:
Related Topics
Collapse
-
by howardc6449UJ6500 LCD panel has a lighter band on top when first powered on. Goes away (or gets much fainter) after TV on for a few min. After powered off for awhile and power back on, same band appears. If powered on immediately after powering off, no or much fainter band. Running the latest firmware.
Disassembled the TV and lifted the LCD panel during testing. Band is on the LCD panel (can see the band on the panel as I lift it slightly) Backlight is perfectly even at the top edge. Double checked LCD panel alignment in the frame and is perfect but since band moved with the panel, its on... -
by triplefourTV flashes backlight then reboots over and over. no image. Client said it used to have image for a bit before rebooting. Got worse over time.
tcon is built into mainboard.
Only one cable goes to panel boards.
there is a cable from one panel board to the other that links them.
cost cutting measure that results in us having harder time to diagnose.
removing the link to the second panel board allows TV to stay on with stable backlight but no image.
used cut off tape method to mask 1 maybe 2 pins on the side of the cable that goes to that second panel board.... -
I had a the above tv qn55q60r that had a bad panel but everything else good. I had another panel here from un55nu6900 with bad leds and melted diffusers.
I put the nu6900 panel in and powered it up and it does work but there are lines vertical lines.
I was trying to change the panel type in the service menu but don’t see my exact panel. Anyway to fix this or someone have similar experience.
the clear picture is the panel type from the service menus on the nu6900. The other 1 is the panel type that was set for the q60r with the bad panel....01-13-2024, 01:57 PM -
I have a TCL 55P6US with sound and backlight but no picture. This model does not have a T-CON board, and the right (rear perspective) panel board is fed from the left panel board. I have not been able to induce any change by disconnecting the secondary panel board or the tape cut-off method on the primary board.
There are a bunch of voltages missing on the panel boards. I can't find any shorted caps of the panel boards, and all of the missing voltage rails read in the kiloohms, which leads me to suspect the issue may lie on the circuit board, rather than a short in the panel.
...11 Photos -
by howardc64
- Prior owner tried a replacement main board. No difference.
- Samsung 2x red blinking standby LED = panel fault
- Jumpered FB_TRDY_1 (pin 1 CN1300 left. main tcon->left side buffer boards) and FB_TRDY_3 (pin 95 CN1301 right. main tcon->right side buffer boards) This allows testing individual T-Con (on main board) connection to panel on this Samsung. Found fault on left side (viewing from rear of TV)
- Each side has 2 buffer boards, disconnected left side flex between 2 buffer boards. Fault is on the left most board.
- Tape masking eventually isolated to CN1300 pin 15 (CKV4_GOA) Display
- Loading...
- No more items.
Leave a comment: