    #81
    Re: UPS and inverter questions

    Time to charge depends on a sundry of things.
    amp/hrs of the battery.
    How far down it is.
    The charger makes a big difference too.
    The charger you are using should take it to a predetermined voltage and then 'float' there to deepen the charge. It doesn't know it's not attached to a car battery.
    Mann-Made Global Warming.
    - We should be more concerned about the Intellectual Climate.

    -
    Be who you are and say what you feel, because those who mind don't matter and those who matter don't mind.

    - Dr Seuss
    -
    You can teach a man to fish and feed him for life, but if he can't handle sushi you must also teach him to cook.
    -

    Comment


      #82
      Re: UPS and inverter questions

      PCBonez answer the charger question but I'll leave the below for ref anyway
      (got 10 min then cant edit....post has moved on a bit since I wrote this)

      Well On the battery charger, here's the blurb....I dont see mention of Gell cell only automotive and vehicle battery
      So I suspect Not
      I dont know for sure either way
      chargers have moved on a lot these days

      6 Amp / 4 Amp / 2 Amp Continuous Charge Rates - Smart Battery Chargerâ„¢
      Model # VEC1086BBD
      3 stage, automatic, high-frequency charging technology
      More efficient charging than conventional model chargers
      Spark-resistant, reverse hook-up & overcharge protection
      Digital Smart Controlâ„¢ microprocessor
      Automatic float mode monitoring


      I'll let davmax answer this more in depth as he seems to familiar with the circuit and understand it a lot better then me

      Generally speaking, On the Relays its depending on construction of contacts.

      to put it simply
      (and I think your probably beyond this stuff but I'll start at the beginning anyway)

      Basically its a coil of wire that used magnetic force to switch physical contacts.

      The voltage for the coil can vary 12 V 24 V 48 V

      It I suppose you could call a digital action , it either ON or OFF.

      The amount of contacts can vary
      but it is more or less a "switch" of some kind
      Like a "toggle switch" and the switch sort of follows those layouts
      SPST SPDT DPDT (single pole /double throw etc)
      (of course it depends on who made and and it purpose too, so could have more or be configured differently)

      So you will have a "Control Circuit" that turns ON or OFF the voltage to the Coil (read as applies voltage across coil) this will then cause the switching action with the contacts.

      Now these can be made one of two ways
      "Normally open contacts" and "Normally closed"
      (in other words the coil isn't energized the contacts are closed etc)

      so the idea is its a "switch" and how it switches or how many isolated switchs can be in the relay depends on the relay

      so just like a light switch and you
      you are isolated from the mains but you switch on the light

      So the "coil control circuit" (you) is not normally part of the "Switch" contacts
      (light switch)

      I guess now (if you haven't) you need to identify whats being switched via the relay contacts.

      it appears you know that it "should switch" so therefore you need to check if this is happening on the coil

      If you can, you could remove the relay and check it functioning correctly.

      But possibly it not switching cause the "control circuit" is faulty or a signal it should receive to trigger the action is not being sent (or arriving where it should).
      relays can and do fail so it a suspect component.

      you may have to disconnect the coil to check the the voltage...also you will I suspect find a flyback diode near it across the coil, the idea being to suppress back EMF from the coil when the magnetic field collapses it generates a high voltage spike
      (if memory serves me)


      I think davmax is best to advise since he is more familiar with your problem

      Hope what I've posted is of some help anyway

      Cheers
      Last edited by starfury1; 01-24-2008, 10:45 PM.
      You step into the Road, and if you don't keep your feet, there is no knowing where you may be swept off to." Bilbo Baggins ...

      Comment


        #83
        Re: UPS and inverter questions

        K just looked at your attachment
        "seems you understand relays well enough"
        (so scratch the above)
        You step into the Road, and if you don't keep your feet, there is no knowing where you may be swept off to." Bilbo Baggins ...

        Comment


          #84
          Re: UPS and inverter questions

          Originally posted by starfury1
          K just looked at your attachment
          "seems you understand relays well enough"
          (so scratch the above)
          Everything helps.

          There are some SMD mosfets that are controlling these relays. The number on them is 702. I guess I need to check the one for the line switch over relay(RY4).

          Comment


            #85
            Re: UPS and inverter questions

            The mosfet for RY4 is shorted. Would this particular mosfet be controlled directly from the microcontroller?

            Comment


              #86
              Re: UPS and inverter questions

              Andrew.

              Re charging. What was temp 100C or 100F? The starting charge you quote is not dramatically too high, but above max. The important thing is that during charge this should drop right back to about 0.5 amp or less at full charge. The battery will be damaged if finishing current is too high. Heat is usually caused by finishing being too high, causes gas generation and internal damage. Strange that the two batteries were so different, on the face of it one appears to have had low charge, the cool one.

              Looking at your circuit. It is clear that RY4 changes over from input AC to inverter out. Inverter out being selected when power fails. The HOT out must pass through RY1 and RY2. RY1 is strange in that it does a tap change on the transformer. I assume the status of the relay connections shown is with inverter OFF and no external power. This shows RY4 by default taking power from the inverter. RY1 should should remain in the default state for both inverter and input AC. RY2 should move to connect the hot line to the output for both inverter and line power.

              Your drawing can be misleading re the tap on the transformer it can be either step up or down. This can be tested by running on battery and you need to measure the voltage between neutral and hot and then neutral and the tap connection. See if the tap voltage is higher or lower that Hot.
              Gigabyte EP45-DS3L Ultra Reliable (Power saver)
              Intel E8400 (3000Mhz) Bios temps. 4096Mb 800Mhz DDR2 Corsair XMS2 4-4-4-12
              160Gb WD SATAII Server grade
              Nvidia 8500GT 256Mb
              160Gb WD eSATAII Server grade for backup.
              Samsung 18x DVD writer
              Pioneer 16x DVD writer + 6x Dual layer
              33 way card reader
              Windows XP Pro SP3
              Thermaltake Matrix case with 430W Silent Power
              17" Benq FP737s LCD monitor
              HP Officejet Pro K5300 with refillable tanks

              Comment


                #87
                Re: UPS and inverter questions

                This does not make sense with your circuit where (no power connects to inverter output). With MOSFET a short the relay would move to connect line power.ie no output from inverter would reach the output. Something confusing here.
                Gigabyte EP45-DS3L Ultra Reliable (Power saver)
                Intel E8400 (3000Mhz) Bios temps. 4096Mb 800Mhz DDR2 Corsair XMS2 4-4-4-12
                160Gb WD SATAII Server grade
                Nvidia 8500GT 256Mb
                160Gb WD eSATAII Server grade for backup.
                Samsung 18x DVD writer
                Pioneer 16x DVD writer + 6x Dual layer
                33 way card reader
                Windows XP Pro SP3
                Thermaltake Matrix case with 430W Silent Power
                17" Benq FP737s LCD monitor
                HP Officejet Pro K5300 with refillable tanks

                Comment


                  #88
                  Re: UPS and inverter questions

                  Davmax the temp was 100F.

                  The relay states in the diagram are with the ups unpowered.

                  I measured power from the center tap on the AVR transformer and one side was 85 volts and the other was 75 volts.

                  Broken parts:
                  Q10 is the mosfet and the diode D7 is shorted also. It is driven by the microcontroller. The diode has KY3 on it.

                  Now we're really getting somewhere.


                  Here's a picture of both.
                  Attached Files
                  Last edited by andrew77; 01-24-2008, 11:59 PM.

                  Comment


                    #89
                    Re: UPS and inverter questions

                    I not sure that you have given the important voltage readings. You quote two sides. It is important that you measure and quote voltages with respect to neutral as previously defined.

                    I am glad the temp was 100F and not boiling.

                    D7 does not look like a diode compare with D6
                    Last edited by davmax; 01-25-2008, 12:09 AM.
                    Gigabyte EP45-DS3L Ultra Reliable (Power saver)
                    Intel E8400 (3000Mhz) Bios temps. 4096Mb 800Mhz DDR2 Corsair XMS2 4-4-4-12
                    160Gb WD SATAII Server grade
                    Nvidia 8500GT 256Mb
                    160Gb WD eSATAII Server grade for backup.
                    Samsung 18x DVD writer
                    Pioneer 16x DVD writer + 6x Dual layer
                    33 way card reader
                    Windows XP Pro SP3
                    Thermaltake Matrix case with 430W Silent Power
                    17" Benq FP737s LCD monitor
                    HP Officejet Pro K5300 with refillable tanks

                    Comment


                      #90
                      Re: UPS and inverter questions

                      problem what made Q10 and D6 blow???? Does this mean a shorted relay coil? Compare with other inverter.
                      Gigabyte EP45-DS3L Ultra Reliable (Power saver)
                      Intel E8400 (3000Mhz) Bios temps. 4096Mb 800Mhz DDR2 Corsair XMS2 4-4-4-12
                      160Gb WD SATAII Server grade
                      Nvidia 8500GT 256Mb
                      160Gb WD eSATAII Server grade for backup.
                      Samsung 18x DVD writer
                      Pioneer 16x DVD writer + 6x Dual layer
                      33 way card reader
                      Windows XP Pro SP3
                      Thermaltake Matrix case with 430W Silent Power
                      17" Benq FP737s LCD monitor
                      HP Officejet Pro K5300 with refillable tanks

                      Comment


                        #91
                        Re: UPS and inverter questions

                        Sorry, from neutral to the center is 75 volts. Wasn't using my brain, I put it back together to test it after realizing it says on the board "AVR CNTR" and "AVR TOP". The center one was obviously lower.

                        The relay is not shorted. I unsoldered it and tested it earlier.

                        Comment


                          #92
                          Re: UPS and inverter questions

                          I don't know if this leads you anywhere, but I am aware of one feature of the 7812:

                          These things are thermally protected and overload protected. If they get too hot or try to pass too much current, they will shut off..... check too see if the load on the 7812 is excessive. Check whatever circuit is being fed by its output pin.

                          In fact, all the 78xx and 79xx regs have this as far as I know.

                          Full output current of 1.5A needs a heatsink. The greater the input voltage, the more heat it will dissipate...... it is after all a simple but terribly inefficient linear regulator! (which is why they don't make high current ones...3A is the biggest linear reg IC I have seen!)

                          Comment


                            #93
                            Re: UPS and inverter questions

                            The cheap APC units are stepped square wave ("modified sine"), the SmartUPS is sine wave.

                            Oh.... I'm a night owl college student so I'll be up till 2:00am CST or maybe later...... no homework tonight so I guess I'll be on badcaps forums!
                            Last edited by hardwareguy; 01-25-2008, 12:36 AM.

                            Comment


                              #94
                              Re: UPS and inverter questions

                              Thanks Andrew. Well that is very interesting. It is a centre tapped transformer. As you show RY1 connected this means the following. In the default position the AVR transormer receives 115VAC from both line and the inverter. The other relay position places 115VAC on the centre tap doubling the output voltage to HOT and also the output of the transformer secondary (charging circuitry). Why is this? It defeats me right now. Are you sure these connections are traced correctly?
                              Gigabyte EP45-DS3L Ultra Reliable (Power saver)
                              Intel E8400 (3000Mhz) Bios temps. 4096Mb 800Mhz DDR2 Corsair XMS2 4-4-4-12
                              160Gb WD SATAII Server grade
                              Nvidia 8500GT 256Mb
                              160Gb WD eSATAII Server grade for backup.
                              Samsung 18x DVD writer
                              Pioneer 16x DVD writer + 6x Dual layer
                              33 way card reader
                              Windows XP Pro SP3
                              Thermaltake Matrix case with 430W Silent Power
                              17" Benq FP737s LCD monitor
                              HP Officejet Pro K5300 with refillable tanks

                              Comment


                                #95
                                Re: UPS and inverter questions

                                Originally posted by hardwareguy
                                The cheap APC units are stepped square wave ("modified sine"), the SmartUPS is sine wave.

                                Oh.... I'm a night owl college student so I'll be up till 2:00am CST or maybe later...... no homework tonight so I guess I'll be on badcaps forums!
                                Thanks for looking at the thread.

                                Originally posted by davmax
                                Are you sure these connections are traced correctly?
                                Only as far as I've taken components off that were in the way of the traces. And to the best of my ability, which isn't saying much.

                                Here's where I've been deciphering most of my SMD markings: link
                                Last edited by andrew77; 01-25-2008, 12:51 AM.

                                Comment


                                  #96
                                  Re: UPS and inverter questions

                                  Monitor the battery closely if using a car battery charger.... forget it and you will destroy the battery.

                                  How big are these batteries? The Smart UPS batteries (assuming you have a 1400 or more VA unit) can be charged with a car trickle charger. Watch the temps though, these AGM batteries do not have any way to replenish water in the electrolyte if you overcharge them.

                                  The 5-7AH units in small UPS units shouldn't be left on a car charger for long at all, 30mins tops at any given time or they get too hot.

                                  Comment


                                    #97
                                    Re: UPS and inverter questions

                                    Hardwareguy, it's a pair of batteries in series and they're 7.2AH.

                                    I'm too tired to do anything else, it's past my bed time.

                                    I'll be back at it in 8 or 9 hours.

                                    Comment


                                      #98
                                      Re: UPS and inverter questions

                                      Here's where I've been deciphering most of my SMD markings: link
                                      Funny I must be missing it. I could not pickup link to code book. Does one have to be a member?
                                      Gigabyte EP45-DS3L Ultra Reliable (Power saver)
                                      Intel E8400 (3000Mhz) Bios temps. 4096Mb 800Mhz DDR2 Corsair XMS2 4-4-4-12
                                      160Gb WD SATAII Server grade
                                      Nvidia 8500GT 256Mb
                                      160Gb WD eSATAII Server grade for backup.
                                      Samsung 18x DVD writer
                                      Pioneer 16x DVD writer + 6x Dual layer
                                      33 way card reader
                                      Windows XP Pro SP3
                                      Thermaltake Matrix case with 430W Silent Power
                                      17" Benq FP737s LCD monitor
                                      HP Officejet Pro K5300 with refillable tanks

                                      Comment


                                        #99
                                        Re: UPS and inverter questions

                                        I used to charge 7Ah batteries with a 6A trickle charger.... I left them on for 30 mins, let them cool and then put them on for another 30. I kept a close eye on them.

                                        You don't get full capacity with this fast charge (the rating is for a 20hr charge!), but it works if you want to jumpstart the UPS.

                                        Comment


                                          Re: UPS and inverter questions

                                          Originally posted by davmax
                                          Funny I must be missing it. I could not pickup link to code book. Does one have to be a member?
                                          No, let me give you some more links.

                                          http://www.tkb-4u.com/code/smdcode/indexsmdcode.php
                                          http://www.marsport.org.uk/smd/mainframe.htm
                                          http://www.the-foundation.be/smd_codebook.php