ground falt
  • skystormfarms
    Banned
    • Mar 2011
    • 160
    ground falt
    i have just ben blown acros the room by a psu i have photos but the psu still works so y wold the psu throwme acrose the room but still work ?
  • Mad_Professor
    A Mech Warrior
    • Feb 2011
    • 1587
    Re: ground falt
    Get your meter and test your ground to neutral on your outlets and see if any voltage exist, if it does then you got Line *hot* grounding out in a J-box or circuit *known in the trade as a hot ground* and the ground wire is disconnected or nonexistent somewhere on it's way back to the load center and not tripping the breaker. It could also be a mis-wire, someone accidentally wired Line to the ground screw on the outlet. The third photo looks like it did trip, but arc quite a bit on the first before tripping which might still mean an improper grounding and that the breaker did it's job tripping when the circuit exceeded it's amps limit.
    If you don't see anything interesting on the house electrical then suspect the PSU. I'm curious as you are.
    You're lucky that you didn't die.
    • skystormfarms
      Banned
      • Mar 2011
      • 160
      Re: ground falt
      well i am wondering 110v sparks and tingels but 240v blows u acrose the room and some times threu walls but my psu is 110v so it had to be no ground and after the pumping transforer?
      • Mad_Professor
        A Mech Warrior
        • Feb 2011
        • 1587
        Re: ground falt
        Yep that sounds like 120v.
        Remember it's not the volts that will kill you, it's the load being pass through you.
        edit: in the first picture, I see the GE logo, is this a power strip?
        • skystormfarms
          Banned
          • Mar 2011
          • 160
          Re: ground falt
          the load pasd thru you what do you mean?
          • Mad_Professor
            A Mech Warrior
            • Feb 2011
            • 1587
            Re: ground falt
            Load = amps
            Say you connect you're self in series with the circuit. You got Line *hot wire* coming from the load center *breaker box* going through a device *ie your PSU* then you got load going back to the breaker box via the Load *neutral wire.* Should you intervene between the load or line, you become part of the circuit, with that any amps traveling that came from other devices or any amps you're creating via resistances. Doing so will put alot of current across your heart enough to make it stop beating completely. GFCI outlets and GFI Breakers trip at I think 5 milliamps.
            Most residential and commercial A/C Circuit wiring are done parallel and daisy chained therefore only devices that are connected via receptacle work in series but will not run in series with other devices connected to the same outlet, but anything traveling down the neutral return carries amps from all the devices that are in parallel of each other. So basically if you grab the neutral wire of a circuit at the panel then ground yourself to the neutral bus bar you get all current from all the devices in that circuit. Where as at a receptacle you may just get the current from the device or devices via a power strip that are plugged into the receptacle.
            • skystormfarms
              Banned
              • Mar 2011
              • 160
              Re: ground falt
              no gfci's here to old still how did it blow me acros the room it did just that
              • Mad_Professor
                A Mech Warrior
                • Feb 2011
                • 1587
                Re: ground falt
                The only way I see you getting blown across the room is if something backfed into the hot Line and then arc to ground on the plug causing that familiar tingle and spark sensation usually something holding a charge. I'm no electrician, I may have apprenticed for year and half, but I don't know everything. Like I said earlier perhaps that one outlet is a hot ground.
                Looking at the picture it looks like it started from the ground prong so perhaps a short in the PSU.
                • skystormfarms
                  Banned
                  • Mar 2011
                  • 160
                  Re: ground falt
                  i will look at the psu should i have manigement look at the pannel? ok i looked at the filter bord and it is black with soot
                  • Mad_Professor
                    A Mech Warrior
                    • Feb 2011
                    • 1587
                    Re: ground falt
                    First You will have to flip the breaker back on to do the test. I would look at the receptacle in question and take a reading with a multimeter. Neutral is on the left, hot is on the right, ground is on the bottom.
                    Just do a Neutral to ground on the A/C setting of your DMM, You should get 0 - 0.05 depending on how good your DMM is. If you get anything other then that like a normal 120 then you got a problem.
                    After that I wouldn't worry about your house electircal and focus on your PSU. I never did ask what brand PSU and what is it used for?
                    • skystormfarms
                      Banned
                      • Mar 2011
                      • 160
                      Re: ground falt
                      neutral to gnd no volts psu antec re cap'd used for a vidio and gaming computer
                      • Mad_Professor
                        A Mech Warrior
                        • Feb 2011
                        • 1587
                        Re: ground falt
                        Then something on the psu failed and grounded out or backfed. I'm not sure what tho since I'm inexperience in that field.
                        You said the main filter cap was black with soot?
                        • skystormfarms
                          Banned
                          • Mar 2011
                          • 160
                          Re: ground falt
                          yes but i desided to test the power strip hot is neutral
                          • Mad_Professor
                            A Mech Warrior
                            • Feb 2011
                            • 1587
                            Re: ground falt
                            Interesting... it's reversed that would totally cause the PSU to ground out and discharge heavily blowing you across the room. Damn if the power strip is recently new, you could call GE and threaten to SUE for damages.
                            • skystormfarms
                              Banned
                              • Mar 2011
                              • 160
                              Re: ground falt
                              man i shold have not boght ge's crap can i sue fore the loss of a computer apower strip and boddley harm
                              • Mad_Professor
                                A Mech Warrior
                                • Feb 2011
                                • 1587
                                Re: ground falt
                                Depends on if the strip was repaired. If it's new then it was a manufacturing defect. You also gotta prove that recapping your PSU was not the issue. Is it like that for all the outlets on the strip or just one? You could call GE and see what they have to say about this, if they agree to compensate for your lost and reimburse you for damages to property and health you could do that. Or consult with a lawyer to see if you have a case, because to me it sounds like you could have been killed by this defect, and how many GE power strips out there that may have this defect.
                                • skystormfarms
                                  Banned
                                  • Mar 2011
                                  • 160
                                  Re: ground falt
                                  well like an idoyt i wanted to test the psu and i did a bench test and it works some how
                                  and onley one cable wase pluged in to the surge strip
                                  • daRk_Kon
                                    • Apr 2007
                                    • 109
                                    Re: ground falt
                                    if your power supply works, you can test it with your multimeter to see if each wire reads the voltage its supposed to.
                                    in order to do this, take your multimeter, switch it to DC 12v take your grounded wire into a black wire on the molex pins and the hot wire to the yellow, should read very close to 12v.
                                    keep your lead in the black pin still and switch your hot wire lead out of the yellow and into red and it should read either 5 or 7 v i forget which.
                                    • skystormfarms
                                      Banned
                                      • Mar 2011
                                      • 160
                                      Re: ground falt
                                      ok idi that and red 5v yellow 12v it hade to be sumthing
                                      • daRk_Kon
                                        • Apr 2007
                                        • 109
                                        Re: ground falt
                                        how long did your power strip work for before it blew you across the room?
                                        • mkdj
                                          Acer TravelMate P214 - N19Q7 main power rail shorted to ground
                                          by mkdj
                                          Dear all,
                                          I have taken out the motherboard of a Acer TravelMate P214. There is a short to ground on the main power rail (19V). I don't have the schematics or boardview for this board (DAZ8IMB1AA0 REVA). But I have found 4 MOSFETS close to the main power rail : 2 N-Channel and 2 P-Channel.
                                          I have checked resistance across each of the 4 MOSFETS. I have the following readings:
                                          Both N-Channel Mosfets: nothing odd
                                          P-Channel MOSFET number 1:
                                          source - drain : 117 kOhm
                                          source - gate: 96 Ohm
                                          gate - drain: 117 kOhm
                                          P-Channel MOSFET...
                                          08-20-2025, 06:08 AM
                                        • barry101
                                          Apple 820-3662 VCore shorted to ground.
                                          by barry101
                                          Hi, Would appreciate some help.
                                          I have an Apple Late 2013 15" A1398 MacBook Pro with Logic Board 820-3662.
                                          Get charger light but no fan spin or chime. No liquid damage.
                                          Found PPBUS and VCORE both shorted to ground. Other rails were ok.
                                          Removed VCORE MOSFETS U7310, U7320 and U7330. Found U7330 was in fact shorted.
                                          With the 3 MOSFETS removed, get PPBUS and fan spin. VCORE is still hard shorted to ground (0 ohms).
                                          Attempted voltage insertion on VCORE to locate short using bench supply set at 1.0 VDC and 4.95 Amps (max current for my...
                                          06-24-2025, 07:34 AM
                                        • Chaks
                                          Ground Plane For 5dBi ISM Band 865-870Mhz Embedded Ceramic Antenna
                                          by Chaks
                                          TAOGLAS ANTENNA MODEL: ISPC.86A.09.0092E
                                          The specs says ...
                                          High antenna efficiency 868MHz ISM Band
                                          5dBi Peak (when placed on 30cm x30cm ground plane) - Broadside to Zenith Radiation Pattern
                                          The antenna is 50x50 mm square and How do I fix it on the Ground Plane of 300 x 300 mm (aluminium sheet 3mm thick).
                                          1. Should I Fix it with a glue.
                                          2. Should I fix it with a double side adhesive tape
                                          3. Should I fix it with Screws (the screw head may just clamp the antenna to the aluminium...
                                          12-09-2024, 11:06 AM
                                        • Leefreeman97
                                          Diagnosing short to ground issue. pcb from an e scooter
                                          by Leefreeman97
                                          Hello, I have a pcb from an e scooter which had a faulty diode but even after removing it from circuit, it still has a short to ground on the three components circled. I have removed every cap on the board and tested one by one and the short is still there and all the caps test ok. Could this be because I haven’t put a diode back on it yet or where do I go next please?
                                          09-19-2025, 03:33 PM
                                        • Rolin
                                          Dell Laptop - over 14V between Chassis Ground and Circuit Ground?
                                          by Rolin
                                          Someone brought me a Dell laptop that had a loose power jack inside (power jack on a cable, not soldered to motherboard). Once disassembled found one of the wires was broken off the power jack. I replaced the jack and it won't turn on, but the metal shell of the jack inadvertently touched the metal hinge and suddenly it got power. I checked voltage from the metal chassis ground and the circuit ground and I get over 14V ? Has anyone seen this before? Typically is it some kind of filter cap that shorted? Very strange...
                                          10-30-2022, 10:18 PM