APC Smart UPS SUA1500 does not detect AC / doesn't turn on
Did you remove both of the transformer from the board and did you notice anything unusual about either transformer winding connections to the pins on rare occasions I have seen bad soldering joints on the connections pins after removing the solder and reapplying solder to the joints corrected the issue I am not saying it the issue you have
I am not sure if they let me have that broken UPS or not, the manager went on vacation right after the event.Leave a comment:
Did you remove both of the transformer from the board and did you notice anything unusual about either transformer winding connections to the pins on rare occasions I have seen bad soldering joints on the connections pins after removing the solder and reapplying solder to the joints corrected the issue I am not saying it the issue you haveLeave a comment:
OK. not sure what went on here (it probably didn't help working on this only on certain days when I had time), but I verified T1 against T2 transformer again. T1 is making this sizzling sound and the I measure 1.7kOhm across the primary winding. It's game over with this, as I don't have a replacement transformer.Last edited by CapLeaker; 08-23-2024, 07:42 AM.Leave a comment:
AC-OK signal is asserted high, looks OK to me. The LED's coming on might be part of its power up/self-check sequence, an LED test then it sees something confusing with its inputs and shuts down.
If you hear something sizzling, I would go after it, it might be a poor connection on the transformer bobbin (crappy soldering) or just gently tap a plastic pen on things to see if you can flush it out. Even a relay could be fizzling inside.
I did think the AC-OK is good. I remember early on checking these little transformers and compare them to each other measuring resistance and they were identical. Anyway… I’ll see Friday if I can figure out where this noise comes from.
If you hear something sizzling, I would go after it, it might be a poor connection on the transformer bobbin (crappy soldering) or just gently tap a plastic pen on things to see if you can flush it out. Even a relay could be fizzling inside.Leave a comment:
The output relay is normally always on (R5/Q2) and the MCU gives the SHUTDOWN command (Q1) to turn it off.
So why is the MCU not enabling the mains output? What does AC-OK signal look like?Leave a comment:
You mention hearing a relay click for a second. It's doing a self-check. Relays off - no mains seen, relays on - mains seen etc.
The transfer relays seem weird - it's using two in parallel RY5, RY4 for Line, RY7, RY6 on Neutral. One must make, the other break or something, but the contacts are in series as well for safety.
I wonder how sophisticated the self-test is. Again, with mains applied and some kind of load, I would see why it's not making it through. Trace the path.
The blown diode might be from insulation failure or arc from contacts to coil on that relay. There are MOV's on either side but not in the middle, so a spike from the VR or UPS output maybe caused this. Just a guess.
As soon as I plug it in or turn the inverter on, I have 24V on the output relay coil. I also have AC waiting for it to be switched via the relay. The path of AC power through the relays isn’t the problem.
I am not sure why that diode D13 went totally open, maybe I damaged it myself when I tried to fire the relay up with 15V instead of 24V.
The main IC isn’t dead. After a brain dead, plugging in the battery and AC power, it beeps every time I press the ON button. It is some sort of a permissive problem or the MCU doesn’t see any AC mains and thinks it is unplugged all the time.
As a temporary measure I swap the diode out wit something more common over 100V rated and just solder it directly over the relay coil on the back of the board. A 1N4002 or better should be good just fine.Leave a comment:
scratch my last post. It is the nature of that beast. But my original blown diode D13 went again. but this time fully open.Leave a comment:
Hmm... not sure if I found something or not. The site fault wiring circuit works, but at the same time IC20 the opto gives weird readings if I poke around on it. Not sure if it is due to this specific optocoupler being used, but it doesn't react like a normal one.
SFH6156-4Last edited by CapLeaker; 08-13-2024, 04:34 PM.Leave a comment:
Or the sensing circuit has some kind of issue or the MCU has a issue that could be causing the issue but how to troubleshoot the issue is the real question I not even sure where to begin if I were doing this repair this is the reason I paying close attention to this post to see if he can figure out what wrong with itAnd exactly this is what I am afraid of a bad MCU, as I already went over the permissive circuits and detection circuits all the important diodes, transistors, Fet’s, and some resistors too. So far besides that SOT-23 diode I found squat.
I have always one thing going through my head: Why is it that there is a small beep when I short press the power button and absolutely no LED is working on the panel and the 120v sockets on the are disabled. Why is there nothing on that front display. I mean if it has a fault, it should display it. At the other end, the 12v should be
( I do not understand this part to why it would display the status when you do this part and not the other function )
OK because I can turn the inverter on and it works fine as kind, with display and all. Why no LEDs when on AC?
One question I have dose it charge up the battery because if it does then this really does not make sense at all unless it is a sensing issue or something wrong with the MCU programming issue or it corrupted some how
This might not be the same thing but we had a machine at work that it would boot up but it would not respond to switch commands or touch screen functions and come to find out from technical support they said that the Erom chip was corrupted somehow and once it was replaced and the parameters were reinstalled it was functioning again so I have to wonder if it could be something similar
if it does not charge up the battery then I would lean more to charging circuit issues
Dose this battery backup have the cue function on where you can see the status of the device and adjust settings and what not does this function correctly this might be one way to know if the MCU is functioning at all
Just keep in mind that I just thinking out loud and this is how I play out in my mind how and what to check sometimes I am on the right track and sometimes I just going down a rabbit hole and going nowhere and probably going nuts as well
I hope this helps youLast edited by sam_sam_sam; 08-11-2024, 08:53 PM.Leave a comment:
With mains present, I think the MCU is seeing something the firmware can't understand, undefined, or a safety-circuit has activated. Or it is a legal department reaction...
UPS auto-destruct is when mains is present yet the inverter starts up. That is very bad, if it were to do that backfeed into the inverter would blow it up. It would burn grandma's house down. I don't see fuses for that situation.
So to protect against that happening, I see it uses two transfer relays- one on Line RY5, other on Neutral RY7. It seems to be a redundant scheme so if one relay had welded contacts, it would not blow up.
Also the signals for the transfer relay coils has an extra safety circuit. XFR-GATE is an analog permissive that can override the MCU IC11.
It might be not permitting the line transfer relay (Line) to engage, the MCU sees this and shuts off. Or the H-FLT, ALL-EN2 are asserted?
"SMKLS" could mean smoke less lol.
You'll have to poke around and see which permissive saying no to the party.Leave a comment:
I usually follow signal verses testing parts when I'm kinda lost what is not working.
The MCU gets these signals (that I can see):
SITE-FLT is ground-fault, but I don't think it matters the UPS works anyway?
Analogs:
AC-IN is mains from voltage sense transformer T1.
AC-OUT is transfer bus from from voltage sense transformer T2.
I-OUT is load current from CT2.
I-CAP is PFC capacitor current from CT1.
I would put a small load like 25W lamp on it and plug it into mains and trace the AC path with a multimeter. It might be an open relay and they can carbonize and test good... but they aren't. Or the autotransformer is open for BOOST/TRIM etc.
Is the 12V rail ok, IC2 will stop it from transfer relay from activating I think. This thing has so many permissive signals. Some relays have a permissive on each coil wire, so like an AND gate both have to approve before the coil pulls in.
the transformer should be good, as it isn’t open. I had another look at this schematic and it always takes me a while to wrap my head around it. Since I can’t work on it every day at work, I might put it back together and bring it home next week.
I do understand what you’re saying with the 12v rail and all the permissive jazz. That’s why it is such a pain to work on after a few days, as I have to go through the schematic again. For sure I am at the end with it in this state and have to get it back together in order to power it up. The cables are too short to power it up while being apart. I can’t connect the transformer like that.
I have always one thing going through my head: Why is it that there is a small beep when I short press the power button and absolutely no LED is working on the panel and the 120v sockets on the are disabled. Why is there nothing on that front display. I mean if it has a fault, it should display it. At the other end, the 12v should be OK because I can turn the inverter on and it works fine as kind, with display and all. Why no LEDs when on AC?Leave a comment:
Analogs:
Is the 12V rail ok, IC2 will stop it from transfer relay from activating I think. This thing has so many permissive signals. Some relays have a permissive on each coil wire, so like an AND gate both have to approve before the coil pulls in.Leave a comment:
Went on this again today and chased things around checking diodes, transistors, fets and the transformer. I couldn't complete the AC-OK cirquit as there are a couple of IC involved, so I have to put this thing back together hook it up and check it from the backside.Leave a comment:
This specification for the HP EliteDesk 800 G5 + Fitbit Versa Smart Fitness Watch can be useful for upgrading or repairing a desktop PC that is not working. As a community we are working through our specifications to add valuable data like the EliteDesk 800 G5 + Fitbit Versa Smart Fitness Watch boardview and EliteDesk 800 G5 + Fitbit Versa Smart Fitness Watch schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant...09-12-2024, 02:30 PM
This specification for the HP ProDesk 600 G5 + Fitbit Versa Smart Fitness Watch can be useful for upgrading or repairing a desktop PC that is not working. As a community we are working through our specifications to add valuable data like the ProDesk 600 G5 + Fitbit Versa Smart Fitness Watch boardview and ProDesk 600 G5 + Fitbit Versa Smart Fitness Watch schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant badcaps...09-12-2024, 02:30 PM
by jamespeterhHi, all
I've posted a similar Q&A on alternative site but this site seems to be more focused in saving UPS.
The system is a SUA 2200XL Rev 7 230V 640-0800G Rev 7
I have UPS that has a strange fault, it does not show or indicate any load on the system, via display or internally coms, LED test front panel works all light up.
has anyone else seen a fault like this , operates but no load recorded, or just blown one of the important non replacable IC's
1. internal monitoring via cable direct into the CPU that no load is present even...06-21-2025, 06:19 PM -
This specification for the HP ProBook 430 G6 + Fitbit Versa Smart Fitness Watch Notebook can be useful for upgrading or repairing a laptop that is not working. As a community we are working through our specifications to add valuable data like the 430 G6 + Fitbit Versa Smart Fitness Watch boardview and 430 G6 + Fitbit Versa Smart Fitness Watch schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant badcaps forum....09-06-2024, 12:00 PM
- Loading...
