New electric panel.

Collapse
X
 
  • Time
  • Show
Clear All
new posts

  • Spork Schivago
    replied
    Re: New electric panel.

    Originally posted by delaware74b
    Currently, SQ-D is the only manufacturer with the plug on bus. There is a down side to the arc fault breakers besides the cost. They are prone to nuisance trips. Items that cause false tripping are: vacuum cleaners (or any other brushed motor), switch-mode power supplies, fluorescent ballasts, dimmers, and some LED lamps.
    Brushed motors are the worst because they generate the exact signature of noise the breaker is monitoring the wiring. It is an ongoing problem and breaker manufacturers have improved breakers to some extent.
    Thank you. My neighbor seems to know a bunch about electricity and said arc-fault is now required here by code. Does that sound right? I've read about some of the issues with the false trips. I read certain lights could set them off. But I thought if we had that problem, we'd just replace that one breaker with a non-arc fault type. I see they make some breakers specifically for things like motors, halogen bulbs, etc.

    Now I'm looking at the GE breaker:
    http://www.homedepot.com/p/GE-PowerM...CCUP/202307120

    I guess it's down to what we really want....do we really want the no-pigtails or do we really want the copper bussbar? Could you help me out and give me some suggestions as to why we might go towards the copper bussbar instead of the no-pigtails? Thanks.

    Leave a comment:


  • delaware74b
    replied
    Re: New electric panel.

    Currently, SQ-D is the only manufacturer with the plug on bus. There is a down side to the arc fault breakers besides the cost. They are prone to nuisance trips. Items that cause false tripping are: vacuum cleaners (or any other brushed motor), switch-mode power supplies, fluorescent ballasts, dimmers, and some LED lamps.
    Brushed motors are the worst because they generate the exact signature of noise the breaker is monitoring the wiring. It is an ongoing problem and breaker manufacturers have improved breakers to some extent.

    Leave a comment:


  • delaware74b
    replied
    Re: New electric panel.

    SQ-D Homeline series has the plug-on bus (same as QO). The Homeline breakers actually have the same internals as the QO but in a more popular (cheaper) 1" width. The QO are 3/4" wide as are the Cutler Hammer CH series. However, CH/CH and SQ-D QO are not interchangeable.
    On a technical note, some brands will physically fit in other brand panels (CH/BR in a GE or Homeline) but will void the warranty and is a violation of code.

    At one time, SQ-D and CH had a series where they were compatible and were listed as such. I think it was the XO series from the 50's/60's. I have seen 1 panel in 12 years and was to be replaced.

    10K AIR is okay in residential branch circuit breakers. The main breaker is probably 22K. I know CH had upgraded their main breakers to equal GE.

    Leave a comment:


  • Spork Schivago
    replied
    Re: New electric panel.

    Originally posted by delaware74b
    Square D Homeline series is aluminum buss, as is Cutler Hammer/Eaton BR series. 10 year warranty for both series.

    GE is full copper buss flash tinned with anti-corrosive coating. Lifetime warranty on all breakers except plug-in panel surge protector. I got a great deal at a local supply house for the one I installed in my house.

    Square D QO series at Lowes and Home Depot are aluminum buss and still 10 year warranty. So much $$$ for a crappy panel, IMO.

    Cutler Hammer/Eaton CH series is copper buss, lifetime warranty, same cost as a QO.....

    Siemens is also a good panel if you can get the copper buss. Make sure the panel number ends in 'CU'. Warranty is only 2 years.

    Arc fault breakers are currently required for all new 120- volt circuits in a home under the 2014 NEC. Arc faults are not required for a panel replacement unless you move the existing circuit more than 6 feet. If you add to an existing circuit, arc fault required.

    Some people don't like GE gear but I don't have a problem with it.

    AIC = Amps Interrupt Capacity. It's the maximum amperage a breaker can handle and trip under a short-circuit condition. Be aware the breaker may self-destruct under that condition. I have seen breakers damaged from a customer trying to reset it under a bolted fault condition but not a catastrophic failure.
    Do they have the plug-on neutral breakers for the GE or the Cutler Hammer / Eaton CH series though or are we going to have to wire the pigtail to the bussbar? We're spending a lot of cash and I want it to look real nice but be done proper like. I don't want to cut any corners. It's the first time I've installed a panel before. I didn't want the pigtails but if I can't get the plug-on neutral and the copper buss, we might just have to go for the copper buss. If we go with the aluminum though, we'd just have t tighten the connections every year or so, right?

    Even if arc-fault aren't required, we wanted to use the combination arc-fault ones. I see they also make combination arc-fault / GFCI breakers. They might be what we'd go for. Now that we have a daughter, we don't mind spending the extra money to be a little bit safer, you know?
    Last edited by Spork Schivago; 10-24-2016, 08:16 PM.

    Leave a comment:


  • Spork Schivago
    replied
    Re: New electric panel.

    These are the breakers we were looking at:

    http://www.homedepot.com/p/Square-D-...PDFC/204844649

    They're combination arc-fault and GFCI, just not combination arc-fault. They're only 10K AIR though.

    Leave a comment:


  • delaware74b
    replied
    Re: New electric panel.

    Square D Homeline series is aluminum buss, as is Cutler Hammer/Eaton BR series. 10 year warranty for both series.

    GE is full copper buss flash tinned with anti-corrosive coating. Lifetime warranty on all breakers except plug-in panel surge protector. I got a great deal at a local supply house for the one I installed in my house.

    Square D QO series at Lowes and Home Depot are aluminum buss and still 10 year warranty. So much $$$ for a crappy panel, IMO.

    Cutler Hammer/Eaton CH series is copper buss, lifetime warranty, same cost as a QO.....

    Siemens is also a good panel if you can get the copper buss. Make sure the panel number ends in 'CU'. Warranty is only 2 years.

    Arc fault breakers are currently required for all new 120- volt circuits in a home under the 2014 NEC. Arc faults are not required for a panel replacement unless you move the existing circuit more than 6 feet. If you add to an existing circuit, arc fault required.

    Some people don't like GE gear but I don't have a problem with it.

    AIC = Amps Interrupt Capacity. It's the maximum amperage a breaker can handle and trip under a short-circuit condition. Be aware the breaker may self-destruct under that condition. I have seen breakers damaged from a customer trying to reset it under a bolted fault condition but not a catastrophic failure.
    Last edited by delaware74b; 10-24-2016, 08:05 PM.

    Leave a comment:


  • Spork Schivago
    replied
    Re: New electric panel.

    Originally posted by redwire
    Ensure that load center has copper busbars. Somehow manufacturers went cheap on home load centers using aluminum.

    Almost all of your cost is the circuit breakers. Price them out. You could get discounts on bulk packs, unless you are recycling the old ones?
    I would not use aged breakers, Federal Pioneer ones don't trip, even after a fire. old breakers are junk

    22,000 amp arc interrupt rating (22K AIR) I believe is the NEC since UL489 updated in 2000.
    Thank you. We did price stuff out a bit and know the money is in the breakers. I also found out what the air stuff was. Thanks for explaining that. I want to double check the NEC. I found the 10K CAFCI's listed on HomeDepot's website say: Combines CAFCI and GFCI protection in one device for NEC 2014

    I read what the interrupt rating is but the numbers don't mean a lot to me. If the fault is to big and the interrupt rating is too low, the breaker could explode or the equipment or person could get hurt. Okay, so it's kinda like a breakdown voltage or something but measured in amps? 22,000 amp or higher would damage the breaker....that's a lot of amperage. Would I ever need anything over 10K in a normal house?

    We don't mind spending the extra money and doing it right though. If 22K AIR rated ones could prevent an explosion or death or something, we have no problems forking out the extra cash. But if we're never going to run across a scenario where the breakers ever receive anything over 10K and the NEC says 10K is fine, does it make sense to go for the 22K rated ones? Thanks for taking the time to answer my questions.

    Leave a comment:


  • redwire
    replied
    Re: New electric panel.

    Ensure that load center has copper busbars. Somehow manufacturers went cheap on home load centers using aluminum.

    Almost all of your cost is the circuit breakers. Price them out. You could get discounts on bulk packs, unless you are recycling the old ones?
    I would not use aged breakers, Federal Pioneer ones don't trip, even after a fire. old breakers are junk

    22,000 amp arc interrupt rating (22K AIR) I believe is the NEC since UL489 updated in 2000.

    Leave a comment:


  • Spork Schivago
    replied
    Re: New electric panel.

    Is the Schneider Square D the way to go here? Because they don't make any dual pole combination arc-fault without the pigtails, I was thinking of maybe checking out another brand, like Murray or something. What do you think?

    Leave a comment:


  • Spork Schivago
    replied
    Re: New electric panel.

    Keeney123, what's the difference between a circuit breaker and a miniature circuit breaker? I'm looking at the site you linked me too (I was searching it before I clicked your link).

    I see stuff like this:

    http://www.schneider-electric.us/en/...rcuit-breakers

    Is that 480$ for just one 40-amp 2-pole breaker? That's really expensive. On HomeDepot, for the arc-fault / GFCI combo 30-amp, I think it was around 90$. I couldn't find any plug-on type arc-fault / GFCI 2-pole breakers though and I couldn't find anything higher than 30-amp for the dual pole arc-fault / GFCI combo breakers.

    Also, what do you think the 10k and 22k AIR thing means? I just found this:

    http://www.productinfo.schneider-ele...000056449.xml#

    Which shows they don't make a dual-function plug-on neutral 2-pole breaker of any size. They do make a 15-amp and a 20-amp arc-fault with pigtails circuit breaker though, part numbers:
    Code:
    QO215CAFI
    QO220CAFI
    QO215VHCAFI
    QO220VHCAFI
    Last edited by Spork Schivago; 10-24-2016, 06:53 PM.

    Leave a comment:


  • keeney123
    replied
    Re: New electric panel.

    Originally posted by Spork Schivago
    Hello,

    We currently have a 100 amp panel that feeds a 60-amp sub-panel. The idea is to do away with both and replace them with one 200-amp panel.

    This is the one I've been eying. What do you guys think?

    http://www.homedepot.com/p/Square-D-...00PC/204844633

    It's a plug-on neutral one. If I understand this correctly, what this means is when we install our combination arc-fault circuit breakers, we won't have to worry about the pigtail. They'll just plop right in and there'll be a neutral busbar that they snap into. We're planning on using combination arc-fault circuit breakers whenever possible. Currently, our house has 17 circuits. We have a couple breakers wired in tandem. We don't want any tandem breakers wired in on the new panel.
    Here you go read to your hearts content
    http://www.schneider-electric.us/en/...rcuit-breakers

    Leave a comment:


  • Spork Schivago
    started a topic New electric panel.

    New electric panel.

    Hello,

    We currently have a 100 amp panel that feeds a 60-amp sub-panel. The idea is to do away with both and replace them with one 200-amp panel.

    This is the one I've been eying. What do you guys think?

    http://www.homedepot.com/p/Square-D-...00PC/204844633

    It's a plug-on neutral one. If I understand this correctly, what this means is when we install our combination arc-fault circuit breakers, we won't have to worry about the pigtail. They'll just plop right in and there'll be a neutral busbar that they snap into. We're planning on using combination arc-fault circuit breakers whenever possible. Currently, our house has 17 circuits. We have a couple breakers wired in tandem. We don't want any tandem breakers wired in on the new panel.
    Last edited by Spork Schivago; 10-24-2016, 04:49 PM.

Related Topics

Collapse

  • howardc64
    LG 49UJ6500 LCD panel lighter band that goes away
    by howardc64
    49UJ6500 LCD panel has a lighter band on top when first powered on. Goes away (or gets much fainter) after TV on for a few min. After powered off for awhile and power back on, same band appears. If powered on immediately after powering off, no or much fainter band. Running the latest firmware.

    Disassembled the TV and lifted the LCD panel during testing. Band is on the LCD panel (can see the band on the panel as I lift it slightly) Backlight is perfectly even at the top edge. Double checked LCD panel alignment in the frame and is perfect but since band moved with the panel, its on...
    02-19-2023, 12:13 AM
  • triplefour
    SAMSUNG UN50TU8000F rebooting, backlight ok. No 12v to panel boards.
    by triplefour
    TV flashes backlight then reboots over and over. no image. Client said it used to have image for a bit before rebooting. Got worse over time.

    tcon is built into mainboard.
    Only one cable goes to panel boards.
    there is a cable from one panel board to the other that links them.
    cost cutting measure that results in us having harder time to diagnose.
    removing the link to the second panel board allows TV to stay on with stable backlight but no image.
    used cut off tape method to mask 1 maybe 2 pins on the side of the cable that goes to that second panel board....
    07-28-2022, 07:59 PM
  • Storyteller12
    QN55Q60R Service Menu Panel Help
    by Storyteller12
    I had a the above tv qn55q60r that had a bad panel but everything else good. I had another panel here from un55nu6900 with bad leds and melted diffusers.

    I put the nu6900 panel in and powered it up and it does work but there are lines vertical lines.

    I was trying to change the panel type in the service menu but don’t see my exact panel. Anyway to fix this or someone have similar experience.

    the clear picture is the panel type from the service menus on the nu6900. The other 1 is the panel type that was set for the q60r with the bad panel....
    01-13-2024, 01:57 PM
  • maneatingmonkey
    Missing LCD Panel Voltages VGH, VGL, VCOM (TCL 55P6US Sound & Backlight but NO Picture)
    by maneatingmonkey
    I have a TCL 55P6US with sound and backlight but no picture. This model does not have a T-CON board, and the right (rear perspective) panel board is fed from the left panel board. I have not been able to induce any change by disconnecting the secondary panel board or the tape cut-off method on the primary board.

    There are a bunch of voltages missing on the panel boards. I can't find any shorted caps of the panel boards, and all of the missing voltage rails read in the kiloohms, which leads me to suspect the issue may lie on the circuit board, rather than a short in the panel.
    ...
    03-27-2024, 07:17 AM
  • howardc64
    Samsung QN75Q6FNA backlight no display, red LED blink 2x, fault in panel
    by howardc64
    • Prior owner tried a replacement main board. No difference.
    • Samsung 2x red blinking standby LED = panel fault
    • Jumpered FB_TRDY_1 (pin 1 CN1300 left. main tcon->left side buffer boards) and FB_TRDY_3 (pin 95 CN1301 right. main tcon->right side buffer boards) This allows testing individual T-Con (on main board) connection to panel on this Samsung. Found fault on left side (viewing from rear of TV)
    • Each side has 2 buffer boards, disconnected left side flex between 2 buffer boards. Fault is on the left most board.
    • Tape masking eventually isolated to CN1300 pin 15 (CKV4_GOA) Display
    ...
    07-19-2025, 10:54 PM
  • Loading...
  • No more items.
Working...