Understanding air conditioner PSU logic

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Gjackson
    Senior Member
    • Aug 2021
    • 134
    • Malta

    #1

    Understanding air conditioner PSU logic

    Hi all,

    I have an air conditioner outdoor control board that I'm trying to understand how it functions. In short, the board takes in 240VAC and splits it into 4 other wires, 2 of these go to power the indoor unit and another 2 go to power the outdoor unit module board. the 310VDC capacitor bank on the outdoor control board get charged up from a rectifier on the outdoor module board. Now what I can't wrap my mind around is the fact that there is a relay in between the 2 mains wires that go from the outdoor control board to the outdoor module board which is normally open, what this means in theory is that the relay can never close as the 12v needed for it's winding to energize is generated only when there is sufficient 310VDC. Unless of course the 12v needed is generated on the control board itself however I could not find a separate supply from the schematics.

    Any help would be greatly appreciated. I have also included the schematics below.

    https://cdn.badcaps-static.com/pdfs/...2306ad82cb.pdf

    pgs.14-15 show PCB(1) -outdoor control board- AND PCB(2) -outdoor module board-
    pgs.71-73 show the respective schematics

    terminals P and N in the schematics are the capacitor bank terminals (310VDC)

    I'm interested in this as the module board had a short on it causing the control board to go into what I presume is short circuit protection mode and I'm trying to figure out how to reset it as currently the main caps are not charging up.

    Thanks!
  • R_J
    Badcaps Legend
    • Jun 2012
    • 9555
    • Canada

    #2
    Re: Understanding air conditioner PSU logic

    +12volts and +5 volts are supplied by the smps on page 72, likely bad ic1 and shorted M1. The schematic is hard to read but I suspect PTC1 could be open. If PTC1 is open I suspect K5 relay contacts could be bad.
    Also check RS1
    If there was a short on the module board it was likely IC8 shorted or the main drive ic PM1
    Last edited by R_J; 11-25-2022, 03:29 PM.

    Comment

    • Gjackson
      Senior Member
      • Aug 2021
      • 134
      • Malta

      #3
      Re: Understanding air conditioner PSU logic

      Thanks for your reply, PTC1 is not open and is in fact 40ohm I'm not sure if that's a good reading as it seems a little high. RS1 checks out fine too. I'm getting 160VAC after PTC1 which I'm not sure should be the case I would expect it to be closer to 220. This results in 220VDC after rectification which is still too low. Am I looking at a fault PTC relay?

      thank you

      Comment

      • lotas
        Badcaps Legend
        • Jan 2016
        • 4649
        • Russia

        #4
        Re: Understanding air conditioner PSU logic

        Is the circuit more like an inverter, is the inductor connected to the board? Power passes through it to the diode bridge (sometimes there are two bridges) and a powerful IGBT transistor and to power capacitors, and the main power supply is already powered from them (check the IGBT for a short circuit).

        Comment

        • R_J
          Badcaps Legend
          • Jun 2012
          • 9555
          • Canada

          #5
          Re: Understanding air conditioner PSU logic

          What is the a/c voltage before the ptc? You need to check between Neutral CN6 and CN5, then check between CN6 and CN9
          CN8 and CN9 supply the bridge rectifier BG1, The ac could be low because it is dropped by PTC1 until K5 shorts it out.
          You should have around 220 VDC across CN5 (N, ground) and CN1 P
          This voltage will be enough to power the smps circuit for the low voltage +5, +12, +15
          Last edited by R_J; 11-25-2022, 03:52 PM.

          Comment

          • Gjackson
            Senior Member
            • Aug 2021
            • 134
            • Malta

            #6
            Re: Understanding air conditioner PSU logic

            voltage at input of bridge is 160VAC which as you said is caused because of PTC voltage drop and between CN7 and CN5 which are the bridge outputs is 220VDC, currently this never reaches the P and N terminals as I have the inductor between CN7 and CN6 removed as it is inside the air conditioner housing and is disconnected, However going off of what you said, once I reconnect that inductor relay K5 should switch and short out the PTC giving full 310 to the caps. My main concern really was that the initial 220VDC would not be enough to generate the 12v 15v 5v rails needed for K5 to switch but you have answered that
            I'll try it out when I get the chance to mount the boards back into the housing.

            Thank you!
            Last edited by Gjackson; 11-25-2022, 04:08 PM.

            Comment

            • R_J
              Badcaps Legend
              • Jun 2012
              • 9555
              • Canada

              #7
              Re: Understanding air conditioner PSU logic

              Yes, you will need to connect the inductor to get voltage across P and N. Page 72 shows the smps, it will operate with a wide range of dc input.
              You will need the smps to be working before K5 will operate
              Last edited by R_J; 11-25-2022, 04:18 PM.

              Comment

              • lotas
                Badcaps Legend
                • Jan 2016
                • 4649
                • Russia

                #8
                Re: Understanding air conditioner PSU logic

                Well, instead of an inductor, you can put a jumper for diagnostics, you won’t start some outdoor units until you briefly apply the “L” phase to the control “S” (signal, interconnect output).

                Comment

                • sam_sam_sam
                  Badcaps Legend
                  • Jul 2011
                  • 6041
                  • USA

                  #9
                  Re: Understanding air conditioner PSU logic

                  I am surprised that this manual has this information in it most of them do not

                  Comment

                  • Gjackson
                    Senior Member
                    • Aug 2021
                    • 134
                    • Malta

                    #10
                    Re: Understanding air conditioner PSU logic

                    Originally posted by sam_sam_sam
                    I am surprised that this manual has this information in it most of them do not
                    Absolutely, I was surprised myself when I saw that schematics where available.
                    +1 for Haier

                    Comment

                    • Gjackson
                      Senior Member
                      • Aug 2021
                      • 134
                      • Malta

                      #11
                      Re: Understanding air conditioner PSU logic

                      Update: I attached both boards back into the outdoor unit and tried powering up but no luck voltage on main filter capacitors starts rising slowly and eventually plateaus at around 20VDC, at this point I'm suspecting the PTC relay and it's high resistance. Might not be important but I also hear a soft clicking occuring every 1/2 a second or so which might be the PTC relay? It's strange as this board stopped working after I replaced 3 capacitors on the output of the 15v smps which were clearly bloated and I don't know how I could have killed the board honestly. The board would still power on without the new caps just no 15v would be present.

                      Comment

                      • R_J
                        Badcaps Legend
                        • Jun 2012
                        • 9555
                        • Canada

                        #12
                        Re: Understanding air conditioner PSU logic

                        I could start by posting clear in focus pictures of both sides of the board. Is the board double sided? If it is you may have damaged a trace when removing the capacitors.
                        The ptc relay? high resistance? Do you mean K5 ? what resistance are you checking? the relays coil or across its contacts?
                        The inrush ptc1 is likely a PPL20400 (40Ω)
                        If you only get around 20 volts across the 680µf/400v caps, you may have damaged the smps and it is drawing too much current and dropping too much voltage across the ptc1 inrush thermistor
                        Last edited by R_J; 11-28-2022, 03:48 PM.

                        Comment

                        • Gjackson
                          Senior Member
                          • Aug 2021
                          • 134
                          • Malta

                          #13
                          Re: Understanding air conditioner PSU logic

                          No traces were damaged I made sure of that. Apparently PTC1 is what's called a PTC relay mainly used in HVAC, never heard of it before but it's the only thing in the way of 240VAC mains reaching the module board. the 40ohm I measured where across it's contacts.

                          it looks exactly like the one here and is soldered on the PCB: https://www.indiamart.com/proddetail...113490830.html

                          as for pictures I currently don't have the board on hand.
                          Attached Files

                          Comment

                          • R_J
                            Badcaps Legend
                            • Jun 2012
                            • 9555
                            • Canada

                            #14
                            Re: Understanding air conditioner PSU logic

                            PTC1 is an INRUSH THERMISTOR, it is NOT a relay. I know the hvac people call it one. K5 is the relay
                            Inside that black case is a thermistor disk mounted between two contacts

                            Have you checked if you get +15v, +5VD or +5V on the smps with CN22 removed?
                            I'm interested in this as the module board had a short on it
                            Did you replace the module board and if not, what was shorted?
                            Attached Files
                            Last edited by R_J; 11-28-2022, 04:11 PM.

                            Comment

                            • Gjackson
                              Senior Member
                              • Aug 2021
                              • 134
                              • Malta

                              #15
                              Re: Understanding air conditioner PSU logic

                              I see, that clears up a lot of questions. Highly possible that I killed something from the heat of the soldering iron. The smps is not the most well designed part of the board and it operates at way too high temps. All images I found online as well as my unit have clear discoloration due to heat so it was probably on the brink of dying. I have checked if I get voltage without the module board connected and I still don't so it's definitely a fault on the larger control board.

                              thanks for helping me out.
                              Last edited by Gjackson; 11-28-2022, 04:11 PM.

                              Comment

                              • R_J
                                Badcaps Legend
                                • Jun 2012
                                • 9555
                                • Canada

                                #16
                                Re: Understanding air conditioner PSU logic

                                If I could see the pictures you are referring to...

                                Comment

                                • lotas
                                  Badcaps Legend
                                  • Jan 2016
                                  • 4649
                                  • Russia

                                  #17
                                  Re: Understanding air conditioner PSU logic

                                  Check the IGBT transistor for a short circuit (and +15v power is important for it).
                                  Attached Files

                                  Comment

                                  • Gjackson
                                    Senior Member
                                    • Aug 2021
                                    • 134
                                    • Malta

                                    #18
                                    Re: Understanding air conditioner PSU logic

                                    https://www.youtube.com/watch?v=dFvxQvKanUc&t=186s

                                    this video shows same boards, couldn't find one in english.

                                    below is a pic of the smps circuit as well as the 3 caps I replaced circled in blue.
                                    I suspect IC is dead as I didn't find a short on the FET, no short on the IGBT lotas mentioned either
                                    Attached Files
                                    Last edited by Gjackson; 11-28-2022, 04:24 PM.

                                    Comment

                                    • R_J
                                      Badcaps Legend
                                      • Jun 2012
                                      • 9555
                                      • Canada

                                      #19
                                      Re: Understanding air conditioner PSU logic

                                      If the 3 caps were bulged I would also replace E3 22µf/25v as it is most likely bad causing the smps not to start.
                                      Measure the DC voltage across E3 it could give an indication of the state of the ic.
                                      Last edited by R_J; 11-28-2022, 04:44 PM.

                                      Comment

                                      • Gjackson
                                        Senior Member
                                        • Aug 2021
                                        • 134
                                        • Malta

                                        #20
                                        Re: Understanding air conditioner PSU logic

                                        I suspected E3 initially also so I removed it and checked it but it tested fine so I put it back in. I did not measure the voltage on it however so that will be the next step. According to IC datasheet VCC is generated by the IC from the HV so if that's not present then the chip is dead
                                        Last edited by Gjackson; 11-28-2022, 04:59 PM.

                                        Comment