Announcement

Collapse

Forum Rules *ALL NEW MEMBERS, PLEASE READ!! UPDATED!!*

First and foremost, Welcome to the Badcaps Capacitor Search Engine & Forums!

New members that have activated their accounts have limited access to certain features of the site until established. Members with zero posts have no access to the private messaging system. Also, members with zero posts may not edit certain profile attributes, such as signatures. New members also may not create new threads. However, new members with zero posts have full access to all technical information contained on this forum, and that also includes attachments (images and files that other members have uploaded), and new members that have activated their accounts are free to post replies to existing threads. If you wish to create a new thread, the fix is simple! All you need is ONE post to be able to have full unrestricted access, and that can be simply posting an introduction of yourself or say hello in THIS THREAD. This may seem a little strange, but it helps keep spam and abuse curved. Please note, that it may take up to one hour from your first post for the limits to be removed. If you make a post and don't immediately see the restrictions gone, be patient. The promotion system updates every hour.

Please complete your profile after making your first post, with your name, locale, and other info. It's nice to know members on a first name basis, and know where they're from. Makes for a much friendlier environment!

Posting rules for this forum will be STRICTLY enforced by myself as the owner/administrator, and my moderator crew.

Badcaps.net IS A BUSINESS!!! If you are a servicer, service center, or vendor of any kind in the computer/capacitor industry, you are NOT permitted to advertise, link, promote, or plug your business on this forum in ANY way! NO EXCEPTIONS!! This includes asking for "donations" in exchange for BIOS passwords or tech advice for anything! If I see you doing that, your post will be edited or deleted, and you warned. If it happens again, you will be banned. The only exceptions are the references to the companies quoted in the FAQ which the administration have added for the convenience of those around the world who have difficulty to source caps for their repair.

This also includes using this forum's private message system to solicit business. Members, if you receive a PM from anyone offering repair services or components, please alert me immediately! Myself or any of my moderators, will never private message a user soliciting business, for Badcaps.net, or any other servicer/vendor. If you PM me about repairing your device, I will reply and take care of you, however, I will not message you first.

------------------------------------

Posting rules:

This forum was created to be a technical support forum primarily for the do-it-yourselfers who choose to repair their own boards. Any and all technical questions are welcome!

1) Please use the SEARCH feature!! Your question may have been answered in another thread! Please search first and see if it has!

2) When posting a technical question, be as detailed as possible in your thread. The more information we have about your specific problem, the better we can answer your question.

3) Please use COMPLETE sentences, punctuation, and grammar! Nobody is perfect, hence, a spelling error on occasion is no biggie. However, posts/threads that are unreadable will be deleted. This includes any and all forms of 'ebonics', leet, chatroom jargon, and 'text message' shorthand and slang. This forum is not a chatroom/text message, please use full words and complete sentences.

4) Keep discussion on topic!! DO NOT HIJACK THREADS! It's easy to do (I've done it myself a few times...) Lets try to keep it down to a minimal!! If you have something really off topic, that's what the lounge is for!

5) Keep things civil! There will be no tolerance for flaming, bashing, hateful remarks, racial remarks, adult material of ANY kind, and so on.

6) THE LOUNGE RULES! The lounge is a place for off topic chit-chat! If you post something that might be considered questionable or something you don't want kids to see, or something you can't view at work/school, etc, please label that thread *NWS* or NOT WORK SAFE in the thread title as a warning. The Lounge is NOT moderated, anything is welcome... Feel free to post rants, jokes, cars, hot women (remember the NWS warning in the title), or just about anything within reason. It's an open forum! Please refrain from participating in political topics if you have thin skin, they can get heated sometimes!! Remember that we have members here from all over the world, with many different views and cultures. Political debates can turn really ugly, and really fast, and if they degrade to personal attacks and useless banter/bashing, moderator action will ensue. I want this forum to be a safe haven for technical discussions from all walks of life, so lets keep off topic discussions civil and friendly.

7) Spamming and spammers will NOT be tolerated or accepted in any way, shape, or form! Spam bots are instantly and permanently banned, and their threads deleted! The mod crew is really quick to zap spammers, we typically pop them before they even get to post. This also includes regular members as well. be courteous and not post spam. This includes links to off-site information that's not relevant to the thread at hand. Do not plug other websites, forums, or businesses in your signatures. You may do so in a thread if the off-site link you're posting is relevant to the topic, but otherwise, don't do it. If you see a thread which clearly a spam bot posting that we have not removed yet, DO NOT click any links in it!! Simply click the 'report bad post' button, and it'll be taken care of, usually within minutes.

8) Account removals & closures: Since no personal information is given in the creation of your Badcaps.net Forum account, requests to remove and/or delete accounts will be declined. Any requests for removal of threads & posts you created will also be declined. The reason is the missing posts can/will leave threads incomplete and fragmented. For the threads to be of help to others later on, information can't and won't be missing. However, if you inadvertently posted personal identifiable information in a post (such as an email address, real name, or phone number), please contact a staff member. In those cases, the post may be edited or removed, at the staff members discretion.

That's about it for the rules, the setup here is pretty loose. However, if you're caught violating any of the rules above, here's what will happen:

First offense: Warning by me or a moderator
Second offense: Banning for 1 day
Third offense: Banning for 3 days
Fourth offense: Banned permanently.

If you do something really dumb, or are just a troll, I will skip the warning and the temporary banning, and ban you permanently!

The rules are pretty cut and dry... However, if you have any questions about this policy, feel free to contact me.
See more
See less

APC UPS units - troubleshooting

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

    #31
    Re: APC UPS units - troubleshooting

    Originally posted by Per Hansson
    Wanna play the "drop a wrench" game in there?

    Things go boom
    I like it when it goes boom!

    http://media.putfile.com/boom-42-78

    Comment


      #32
      Re: APC UPS units - troubleshooting

      anyone else notice the blatent ripoff on fujitsu?
      Originally posted by willawake


      another different china brand found in a brand new APC ups. the funny thing is they put all these APC stickers on the battery but it would probably cost nothing to get them APC branded at the factory....

      here is what they have in the shop today



      its a Fujitron FN-1272 12v 7.2Ah sealed lead-acid rechargeable battery
      the shopkeeper has put all his faith in Fujitron now........he says they are made in japan...my ass....anyway there is no reference in google for this model or company....except this post shortly......

      at the moment i am thinking the Back-ups RS are better at not overcharging the batteries than the smart-ups. i dont recall changing batteries in any RS yet and i have some over 3 years.

      Comment


        #33
        Re: APC UPS units - troubleshooting

        hmm one of the rack apc make battery warning
        all batteries test 13.33v though

        fucking POS
        Last edited by willawake; 09-18-2008, 01:55 AM.
        capacitor lab yachtmati techmati

        Comment


          #34
          Re: APC UPS units - troubleshooting

          I know that horrible baked battery smell.It's caustic yet suptle.
          All the APC's here have had sets of batteries,
          but it's cheap insurance for the protection value.
          Jim

          Comment


            #35
            Re: APC UPS units - troubleshooting

            Is there any case that a faulty/old battery can cause an "Internal Error" alarm (All indicators lit simultaneously) on an APC UPS?
            Has anyone experienced anything like that and maybe with a battery replacement things came back to normal?

            Comment


              #36
              Re: APC UPS units - troubleshooting

              All the manuals are here, check in the troubleshooting of your unit.
              The big ones can report internal fuses and breakers out.
              Very likely that it is just bad bats though.
              http://www.apc.com/
              Jim

              Comment


                #37
                Re: APC UPS units - troubleshooting

                Thank you for your reply, i have already looked in the hardcopy of the unit's manual...

                I contacted APC support and they answered that an "Internal Fault Error" is probably a board fault...I measured the battery voltage with my DMM and it is 13.6V, to exclude some battery originated trouble...

                After searching the inside of the ups unit for visible flaws, i discovered only this :





                Seems to me that 10Ω R150 resistor (left of the yellow cable) has a small crack in the middle, with a brownish colour...could be burnt ? I'm asking cause i haven't seen a burbt resistor, so i don't know how it would look like...


                In the meantime i'll try to borrow an almost out-of-the-box battery from a friend to exclude the battery fault...

                Thank you again

                Comment


                  #38
                  Re: APC UPS units - troubleshooting

                  This looks like it might be relevant to you: link

                  Comment


                    #39
                    Re: APC UPS units - troubleshooting

                    If that resistor bothers you just measure it with a DMM if it's within 10% tolerance it's fine.

                    If it's shorted or open it will be a pretty obvious reading.

                    There always is the chance that it is in circuit with other components so it may not read exactly in the 10 ohms area.

                    I have seen metal oxide resistors (on the convergence amps) on RPTVs break like that. Just a fine crack down the body but they are through hole components.

                    I would say in an given enough current in an overcurrent condition those puppies would vaporize or at least char pretty good.
                    Last edited by Krankshaft; 11-02-2008, 03:10 AM.
                    Elements of the past and the future combining to make something not quite as good as either.

                    Comment


                      #40
                      Re: APC UPS units - troubleshooting

                      just to recap, i had one rack APC Smart UPS make battery warning. the batteries measured 13.33v.

                      and to add

                      later i had a smart ups 1000 do the same shit. repeatedly.

                      both units were using powersonic batteries.

                      i made experiment with the 2x7ah of the 1000 ups. i put individually on a bright 12v bulb. one battery discharged in 1 hour ok. the other bulged after half an hour. these batteries are only 1 year old.

                      this leads me to believe the powersonic are not so good batteries.

                      on the other hand i recently replaced battery in an apc cs which i was pleased to see had done 4 years service. the battery was not bulged.

                      this is the same experience with my apc rs 1000 which i have at home. eventually i replaced the batteries at 3 years even though it was not necessary.

                      so in conclusion
                      i am not happy with powersonic presently
                      my experience over the years leads me to believe the smart ups units are not dealing with the batteries in a gentle manner whilst the other apc units are.

                      i would also like to add that ups backup in an office environment should be specified according to real requirements as batteries are expensive. ie two batteries is 2x the cost and maybe its not needed.

                      i have found another supplier which provides CSB batteries. there is not much choice here. i will go for those in order to continue the research.
                      capacitor lab yachtmati techmati

                      Comment


                        #41
                        Re: APC UPS units - troubleshooting

                        Originally posted by willawake
                        now its getting interesting. who else has a smartups where the batteries failed this way.
                        I have a couple of SmartUPS where the batteries were bulging. I got them that way (they were freebies). At least I was able to get the batteries out without metal work.

                        Comment


                          #42
                          Re: APC UPS units - troubleshooting

                          Originally posted by kc8adu
                          the constant voltage charger will happily dump current up to its preset limit into the batts even as cells short.
                          the remaining good cells hit thermal runaway and melt due to the overcharge.

                          Is this why the alternator on my old car died? I long suspected that the car battery with the shorted cell killed the alternator. The battery was replaced and the alternator died a couple of weeks later.

                          Comment


                            #43
                            Re: APC UPS units - troubleshooting

                            that can happen.could have just been its time to go.

                            Comment


                              #44
                              Re: APC UPS units - troubleshooting

                              we have already talked about using batteries with a larger capacity in ups units. but is it ok to use with a smaller capacity. say if the smart-ups is using 12ah. is it ok to use 7ah instead?
                              capacitor lab yachtmati techmati

                              Comment


                                #45
                                Re: APC UPS units - troubleshooting

                                should be ok.
                                it'll just won't last long while being powered from them...

                                ups doesn't have brains to figure out what battery is in(unless you do a fully drain/recharge cycle and ups has cpu that monitors it..then it knows) the main problem with too big batteries is if charger is smart, and if circuit itself can take such big currents abuse...

                                both things are just fine if you have ups that was mentioned here(better(more expensive) models from apc etc.)

                                to that extent smaller battery will make the charging load smaller(if nothing else shorter charging=smaller load on components), so no worries there...