Samsung 215tw display cuts out
  • almoodie
    • Jan 2010
    • 66
    Samsung 215tw.
    When I turn the monitor on the video displays for a couple of seconds, then the screen goes blank. Power light glows continuously.
    I opened it up. There are no bulging caps, but I replaced them all with the exception of the large 180 microF 450V.
    Reconnected everything and turned it on again but problem remains.
    No burned or charred components, and I can't see any bad solder joints.
    Images of the power/inverter board are attached.
    What should I do now?
  • Razzy
    • Jan 2010
    • 11
    Re: Samsung 215tw display cuts out
    Can you barely see the image on the monitor? Could be inverter issue.
    • PlainBill
      • Feb 2009
      • 7034
      Originally posted by almoodie
      Samsung 215tw.
      Razzy is probably right, it's most likely an inverter / backlight issue. Try hooking it up to a working computer, then shining a bright light on the screen while viewing it from an angle. If you can see the desktop or whatever the computer is displaying, that confirms it.
      There are several approaches to troubleshooting this problem, all with varying degrees of risk and chances of success.
      The safest is to measure the resistance of the primaries and secondaries of the transformers. I would GUESS that the primaries will be under 10 ohms, the secondaries about 1K, but there is a LOT of guessing involved in that. With luck you can work from the top of the board, the output pins (labeled O1-O6) are covered with insulation. Do this with power off, of course.
      A second approach is to hook everything together in some manner that you can access the bottom of the board while it is hooked to the monitor. While the monitor is displaying an image and the backlights are on, measure the ACvoltage from the returns lines (labeled R1 - R6) to ground (labeled GND).
      A third approach requires the same approach as the second, but measure the AC voltage at points V1 - V6 to ground while the backlights are on.
      In all three cases we are looking for a reading that is different from the rest.
      Good pictures, by the way.
      PlainBill
      • almoodie
        • Jan 2010
        • 66
        [QUOTE=PlainBill]Razzy is probably right, it's most likely an inverter / backlight issue. Try hooking it up to a working computer, then shining a bright light on the screen while viewing it from an angle. If you can see the desktop or whatever the computer is displaying, that confirms it.
        Hooked it up to a working PC and turned it on. I cannot see any image on the screen when I illuminate it with a flashlight.
        Should I perform the tests outlined above or do I go in another direction?
        • PlainBill
          • Feb 2009
          • 7034
          [QUOTE=almoodie]
          I would say you may have to go in a different direction. However, there are a few things to try first. On most LCD panels you can see if the backlights are on from the back of the panel. If they are off, look at the back of the power supply / inverter. Notice the label by the cable that goes to the logic board. One of those lines controls the brightness of the backlights, the other turns them on and off. It APPEARS the two lines are the ones on the extreme left in the picture. Check if either of those lines changes state when the backlights goes off. If they don't, it IS a backlight / inverter issue, and follow the asteps in the previous post.
          PlainBill
          • almoodie
            • Jan 2010
            • 66
            Blacklight comes on when monitor is first switched on but only for a second or so. This process can be repeated over and over.
            Transformers
            All values relative to ground
            Primary resistances (to each of the three legs or the transformer primary)
            1.6 ohm 9.0M ohm 9.0M ohm
            1.5 ohm 9.0M ohm 9.0M ohm
            1.0 ohm 8.13M ohm 8.6M ohm
            19 ohm 9.0M ohm 9.0M ohm
            7 ohm 7.2M ohm 7.5M ohm
            1.4 ohm 7.5M ohm 7.7M ohm
            All secondary resistances = 0.89k ohm
            All return voltages R1 – R6 = 0.2 V AC
            V1 = 0.012 V AC
            V2 = 0.012 V AC
            V3 = 0.012 V AC
            V4 = 0.012 V AC
            V5 = 0.012 V AC
            V6 = 0.025 V AC
            Connector to logic board voltages. Power on, all boards and display connected
            ADJ = 0.9 V
            GND
            GND
            GND
            13 V = 13.35 V backlight on or not
            Analog = 0.6V at switch on, rises to 3V when backlight dies
            ON/OFF = 11V at switch on, drops to 3V when backlight dies
            Al.
            • PlainBill
              • Feb 2009
              • 7034
              Transformers
              V1 = 0.012 V AC
              V2 = 0.012 V AC
              V3 = 0.012 V AC
              V4 = 0.012 V AC
              V5 = 0.012 V AC
              V6 = 0.025 V AC
              ADJ = 0.9 V
              GND
              GND
              GND
              Al.
              That seems to confirm it. The logic board is shutting down the backlights.
              PlainBill
              • almoodie
                • Jan 2010
                • 66
                PlainBill
                What can I do now.
                • PlainBill
                  • Feb 2009
                  • 7034
                  What can I do now.
                  Post pictures of the logic board. But things aren't looking very good.
                  PlainBill
                  • almoodie
                    • Jan 2010
                    • 66
                    PlainBill
                    Images of logic board are attached.
                    I have another, known-to-be-working, Samsung 215tw, so I took the logic board out and put it in the non-working monitor, results were the same, back light shuts down after a second or so.
                    Next I put the screen from the non-working monitor in the chassis of the working monitor, so that all components are known to be good with the exception of the screen. Same result, backlight turns on for a second or so then shuts down.
                    I deduce from this that the screen/backlight of the non-working monitor has a backlight problem.
                    Do you agree?
                    I have looked at taking the screen apart to access the CCFL tubes but it is not obvious how it comes apart, any advice.
                    Al.
                    • PlainBill
                      • Feb 2009
                      • 7034
                      Do you agree?
                      Al.
                      Good job of troubleshooting. I wish more people were that thorough.
                      As far as taking the LCD panel apart, same advice as before - post pictures. The disassembly process is often non-intuitive. After all, they really aren't designed to be taken apart.
                      One final point: Given that the logic card seems to be shutting the backlights down, the most likely source of the problem is the LCD panel, not the CCFLs.
                      PlainBill
                      • almoodie
                        • Jan 2010
                        • 66
                        PlainBill
                        I have the screen assembly apart, lots of pieces.
                        The CCFL tubes look OK as far as I can tell, no breaks or blackening.
                        I had thought that the screen driver board and the LCD panel would separate but that does not appear to be the case, image attached. If they will not separate then I guess I am out of luck with this LCD panel. I Googled replacement screens but they are priced so high it makes repair uneconomic.
                        Selling the good boards on Ebay looks the way to go.
                        Al.
                        • almoodie
                          • Jan 2010
                          • 66
                          If I connect power/inverter board to the CCFLs, and to the logic board, but do not connect the logic board to the panel (actually the board fused to he panel), and switch on, I get the same backlight on for two seconds the off.
                          Why does the power/inverter board shut down the CCFLs?
                          1) Because the CCFLs show over voltage or over current. Makes sense since the power/inverter board IS connected to the CCFLs. This would mean there is a problem with the CCFLs or associated wiring. Is that correct.
                          2) OR is the the power/inverter board able to detect that that the logic board is not connected to panel board, and hence can shut down for that reason.
                          I ask because I can't see and problem with the CCFL lamps, no breaks or blackening, and the wiring shows no faults.
                          If there is no problem with the CCFLs and their wiring, does that mean their must be a problem with the board fused to the LCD panel.
                          Help, I'm trying to educate myself.
                          • PlainBill
                            • Feb 2009
                            • 7034
                            Assuming I understand how everything works, that is correct. I don't understand what information passes from the panel board back to the logic card, but assuming there is some sort of status information passed that way would account for your observations.
                            PlainBill
                            • freelander
                              • Apr 2009
                              • 109
                              The Samsung 215TW shares the same Samsung LTM210M2 panel as Gateway FPD2185W and HP F2105 monitors that I have worked on. Based on your problem description, you almost definitely have one or more dead bulbs in your panel. I'm not sure if this model has the -01 or the -02 variation but the only difference is the connector style. Do you have three individual connectors for each bulb bank? I had a troublesome monitor like this that didn't have any obvious signs of blackening etc but when I individually tested the bulbs, one was indeed dead and causing the shutdown. Upon disassembly, I discovered that the reason I couldn't see any obvious issues is because the solder joint on the bulb failed within the rubber sleeve on the end. Quite unusual failure mode but it happened to me with this panel.
                              By the way, I have never been able to see an image with a functioning power board and dead bulbs with this panel. I'm not sure if there is some kind of film but just an observation.
                              I didn't notice if you said that you took the known-to-be-working panel and tried it in the recently repaired monitor. Confirm that your repair is good and you know that you have isolated it.
                              • almoodie
                                • Jan 2010
                                • 66
                                The panel is indeed LTM210M2 L02. Only 2 individual connectors per bank, image attached. I will examine the bulbs carefully tomorrow and report back.
                                • freelander
                                  • Apr 2009
                                  • 109
                                  The small connector makes it easy to test one connector at a time but you may need to become a little creative with the big one. I have used little pins to make it easy to use aligator clip leads to connect the panel when it is not in place. To verify that you have one or more failed bulbs, you will need to take advantage of your second panel. you can connect disconnect one connector at a time and connect with the similar (known good) connector for a bulb bank in your good monitor. There is a methodical approach here and all that it will do is narrow down your bulbs without removing them yet. Make sure that you power down in between re-arranging your connections and be sure not to short anything out.
                                  You can also remove the larger connector if need be to bare the wire ends. You will notice little tabs that you can push in and very carefully pull the wire out of the connector. Of course, if you can rig something up with what you have on hand without doing that, that works too.
                                  • almoodie
                                    • Jan 2010
                                    • 66
                                    Sorry I posted this mesage to the wrong thread last night!!!!!!!!!!!!
                                    Freelander, you are correct, exactly as you said, one of the solder joints at the end of one of the CCFL tubes had failed, presumably leading to arcing. Images are attached.
                                    For those who have never seen the guts of a panel here goes:
                                    Image 1: Essentially a metal tray with a sheet of white glossy plastic in the bottom. The angled pieces (wires attached) lying to the side each carry 3 CCFL tubes. These angled pieces slot in top and bottom in the tray creating a wall of light
                                    Image 2: One of the two angle pieces which carry the CCFLs
                                    Image 3: A 3/8 inch slab of clear plastic which sits in the main panel tray. On top of this sit 3 layers of plastic sheet (not shown). I guess they are polarizers, diffusers, or the like.
                                    Image 4: The failed CCFL return wiring
                                    Image 5: A bank of 3 CCFL tubes with wiring
                                    Image: 6 Closeup of CCFL ends with charring. White end piece is rubber and broken up somewhat with the charring.
                                    All the pieces are quite robust but I had to get my 17 year old daughter with her small hands to disassemble to CCFLs from the angle pieces. Have to go get some wire fine enough to rewire the CCFLs tomorrow, together with a can of compressed air and a microfiber cloth, the poor man's answer to a clean room.
                                    This is all very interesting but probably an uneconomic exercise. Plus the big question is whether I can put this thing back together in an acceptable state of cleanliness such that I get a usable monitor.
                                    • freelander
                                      • Apr 2009
                                      • 109
                                      Glad to see that you found it. Since you are about to move this to the bone pile, you should consider trimming the end of the lead and re-solder to the tube bank. It certainly isn't an ideal solution but I brought one back to life this way and it's still running.
                                      • almoodie
                                        • Jan 2010
                                        • 66
                                        I need to rewire the return leads to the CCFLs, shown in attached image. I've tried Radio Shack my only local retailer but can find anything of suitable gauge. Can anyone tell me what gauge wire I need and where I might order it, a part number would be of great help.
                                        Al.
                                          by momaka
                                          03-15-2023, 10:17 PM
                                        • MaxDerVerpeilte
                                          A repair of my Samsung C32G53T Monitor
                                          by MaxDerVerpeilte
                                          Hello everyone!
                                          Since I didn't find it anywhere and only found some YouTube videos on other monitors, I'd like to show you how I "repaired" my monitor.
                                          I put the word repaired quotation marks because I really dont know if this is a permanent fix, since I just removed some resistors and did not really replace anything.
                                          It was all about my monitor only showing weird vertical lines.
                                          In my research I found out that some CKV lines seemed to be shorted. The recommended way to fix this was disconnecting them.
                                          09-12-2023, 07:20 PM
                                        • CptChronic
                                          Samsung LU32J590UQUXEN Monitor display problem
                                          by CptChronic
                                          I have an intermittent display problem with my monitor, when I plug in the HDMI cable to my (or any) laptop, you see the connection screen shrink on the laptop as it usually would before displaying on the monitor but 95% of the time the monitor display stays black.
                                          Before it cut out all together, tapping the monitor control button a fair few times would make the screen display, and everything work fine.
                                          But now it never does it. Not sure what's going on, hoping someone can help. I'm capable of stripping the thing down and soldering in new parts if needed, or programming...
                                          04-24-2023, 04:33 PM
                                          Wise Wing F199 19'' LCD monitor - recapped
                                          by momaka
                                          Looking through my repair pictures and notes, it's been a long time since I posted anything in the LCD monitors section. So here goes that.
                                          I'm dedicating this thread to one of the very first LCD monitors I repaired (if not the first one), which was more than 10 years ago now. The monitor is a Wise Wing, model F199. It's a 19” CFL-backlit LCD. I got it for free off of Craigslist in 2009 from a guy, who said he bought it for cheap from Wallmart and the monitor worked only for a little less than 2 years before quitting.
                                          When I saw the Craigslist post, I wasn't...
                                          08-24-2020, 10:58 AM
                                        • sew333
                                          Pc shutdown, monitor flickered with no signal after 10 seconds
                                          by sew333
                                          My pc:
                                          10850K stock 4800mhz stock Kraken X73 good temps
                                          2x16 GB DDR4 GSKILL 3000mhz XMP
                                          Seasonic Tx-850 Ultra Titanium
                                          Gigabyte Rtx 3090 Gaming OC
                                          Aorus Z490 Pro Gaming
                                          1 TB SSD
                                          4 weeks ago i launched Metro Exodus Enhanced and during cinematic advertisement part ( 30 fps ), pc just shutdown.
                                          Also monitor flickered with NO SIGNAL 10 seconds after shutdown. So only monitor and pc was affected.
                                          Next i pressed only power button, rebooted again and its fine again. Happened once and i cant reproduce.
                                          Power...
                                          02-22-2022, 10:27 AM
