Broken transformer on Carlsbro GRX7

Collapse
X
 
  • Time
  • Show
Clear All
new posts

  • OrganiK
    replied
    Re: Broken transformer on Carlsbro GRX7

    Thanks for all the help! much appreciated

    Leave a comment:


  • budm
    replied
    Re: Broken transformer on Carlsbro GRX7

    Yes you can, just wire them up with correct phase.

    Leave a comment:


  • OrganiK
    replied
    Re: Broken transformer on Carlsbro GRX7

    Originally posted by R_J
    You don't need 2 secondaries, you need a center tapped secondary
    I know but can't i make one with a a center tap with a transformer that has 2 identical secondary windings?

    Leave a comment:


  • budm
    replied
    Re: Broken transformer on Carlsbro GRX7

    Originally posted by r_j
    you don't need 2 secondaries, you need a center tapped secondary
    +1

    Leave a comment:


  • R_J
    replied
    Re: Broken transformer on Carlsbro GRX7

    You don't need 2 secondaries, you need a center tapped secondary

    Leave a comment:


  • OrganiK
    replied
    Re: Broken transformer on Carlsbro GRX7

    Originally posted by petehall347
    Nice one, so then i would need a transformer that has 2 secondarys with an output of about 50Vac each correct?

    Leave a comment:


  • petehall347
    replied
    Re: Broken transformer on Carlsbro GRX7

    + and - 70v for that amp .....https://music-electronics-forum.com/...ad.php?t=19136

    Leave a comment:


  • OrganiK
    replied
    Re: Broken transformer on Carlsbro GRX7

    Originally posted by R_J
    You should try and find out what the voltage should be, if that is not the original transformer, 43vac is meaningless. What is the voltage on the main caps?
    If the 43vac is correct you would have 60 vdc across the + of one capacitor and the - of the other, so about 30 volts across each capacitor to ground.
    This must be the way they are using the transformer.

    The second picture is how it is normally done, so maybe the customer broke the center tap wire completely off the transformer?
    The caps are rated at 80VDC so its a bit high for 30 right? but maybe since its old school they like to over engineer stuff a lot, dunno.

    If it was 43Vac on either side it would give about 56Vdc for each cap that makes more sence for the 80VDC on the caps. we also know that its a 150W x2 amp at 2omh so that would need a voltage of about 17Vac = 24.5Vp so that fits better with it being 43Vac total.

    Thanks a lot for you time and patients by the way
    Last edited by OrganiK; 05-16-2019, 11:58 AM.

    Leave a comment:


  • R_J
    replied
    Re: Broken transformer on Carlsbro GRX7

    You should try and find out what the voltage should be, if that is not the original transformer, 43vac is meaningless. What is the voltage on the main caps?
    If the 43vac is correct you would have 60 vdc across the + of one capacitor and the - of the other, so about 30 volts across each capacitor to ground.
    This must be the way they are using the transformer.

    The second picture is how it is normally done, so maybe the customer broke the center tap wire completely off the transformer?
    Attached Files
    Last edited by R_J; 05-16-2019, 09:20 AM.

    Leave a comment:


  • OrganiK
    replied
    Re: Broken transformer on Carlsbro GRX7

    Originally posted by R_J
    I see two wires had spade connectors on them, I am guessing they connected to the power switch originally, What about the larger secondary wires, were they just floating around in the mixer and not connected to the bridge? too bad the customer played with it first, that's never a good sign. I wonder if this is the original transformer?
    Non of the wires where connected, I put the connectors on them wire.

    Yer I also wondered if someone had put a different transformer in it.

    So where did you get the 43V on the secondary before? was it just a guess?

    Edit: Sorry my bad i was just being stupid and could not read the sticker properly it says 43V 3 Amps on it...

    and the caps are doble that, so could well be the right voltage. So do you think i should just try and fit a 2x 43V 150VA Transformer and cross my fingers? lol
    Last edited by OrganiK; 05-16-2019, 01:56 AM.

    Leave a comment:


  • R_J
    replied
    Re: Broken transformer on Carlsbro GRX7

    I see two wires had spade connectors on them, I am guessing they connected to the power switch originally, What about the larger secondary wires, were they just floating around in the mixer and not connected to the bridge? too bad the customer played with it first, that's never a good sign. I wonder if this is the original transformer?

    Leave a comment:


  • OrganiK
    replied
    Re: Broken transformer on Carlsbro GRX7

    Originally posted by petehall347
    are those caps in parallel ?
    no they are, there is one for each power rail

    Leave a comment:


  • OrganiK
    replied
    Re: Broken transformer on Carlsbro GRX7

    Originally posted by petehall347
    would spike the secondary then blow the fuse most likely .
    what from the inrush current? i though that only happend on caps or motors, im really not sure so please correct me if im rong

    Leave a comment:


  • OrganiK
    replied
    Re: Broken transformer on Carlsbro GRX7

    Originally posted by R_J
    I would guess blue and green are the secondary 43 volts, Brown and pink 240vac with the orange and (yellow/red???) connected together. and now the winding between the pink and orange is open. You could supply 120vac to brown and orange to see if you get 43vac for the secondary
    yer that's what i thought, Still i recon you right about there should be a center tap on the secondary tho...

    Havent got means of getting 120vac... i might be able to borrow an old building transformer, that should do right?.

    Still dont quite understand why it would blow the fuse by putting more volts on it if there isn't any load on the secondary

    Leave a comment:


  • petehall347
    replied
    Re: Broken transformer on Carlsbro GRX7

    would spike the secondary then blow the fuse most likely .

    Leave a comment:


  • OrganiK
    replied
    Re: Broken transformer on Carlsbro GRX7

    Originally posted by redwire
    The thinner wiring should be the primary, if it's got a dual 120VAC primary and putting 220V on one of course it would blow the fuse.
    Even if there is no load on the secondary? would a single primary winding not have a high impedance when there is no current flowing though the secondary?

    Leave a comment:


  • petehall347
    replied
    Re: Broken transformer on Carlsbro GRX7

    i would do the 120v also to find secondary voltage and further testing . been there done that .

    Leave a comment:


  • R_J
    replied
    Re: Broken transformer on Carlsbro GRX7

    I would guess blue and green are the secondary 43 volts, Brown and pink 240vac with the orange and (yellow/red???) connected together. and now the winding between the pink and orange is open. You could supply 120vac to brown and orange to see if you get 43vac for the secondary
    Last edited by R_J; 05-15-2019, 06:00 PM.

    Leave a comment:


  • petehall347
    replied
    Re: Broken transformer on Carlsbro GRX7

    pic 2 post 5 should clear it up .spades go to bridge .

    Leave a comment:


  • petehall347
    replied
    Re: Broken transformer on Carlsbro GRX7

    are those caps in parallel ?

    Leave a comment:

Related Topics

Collapse

  • Wolf1977
    general question when a mosfet on primary of transformer is burned
    by Wolf1977
    hi
    in a welding machine i had a mosfet and four components wich connect with it burned
    i ordered all the damaged components and replace it but when i put the device on the plug all the components burned again i had tested before and i had not shunts
    i dont understand whats happen wrong
    more particular on the schematic q11p01 mosfet q11p02 tranzistor
    three paralel resistors had burned q11p07 zener shunt q11p08 open
    when i changed all these shunts q11po7 mosfet and tranzistors
    maby the transformer has problem on your opinion or something on...
    08-19-2023, 01:27 PM
  • momaka
    KingWin ABT-650MM 650 Watt ATX PSU [PCB: SW8835REV:A]
    by momaka
    For today's thread, I have a KingWin ABT-650MM ATX PSU. Official web page with the PSU specs is still up and can be found here:
    http://www.rmac.kingwin.com/products.../abt_650MM.asp

    I just can't help it when I see a broken / for parts PSU on eBay that's listed for cheap and looks at least somewhat interesting. Well, OK, I won't lie – on the outside, this PSU looks anything but interesting. It's a plain gray box with colorful “spaghetti cables”.




    What mostly drew me into buying it is its 2x PCI-E power connectors...
    03-29-2022, 11:34 PM
  • mikey5791
    Is it possible for transformer substitution?
    by mikey5791
    Hi all,
    Got this local made DC power supply (12/14V) given free as the transformer has melted. There is no marking or indication to identify what type or rating of transformer used.
    Fyi,. I had a busted autogate mainboard with transformer with marking 13-0-13 . Is this the 13v dc type transformer?
    My questions are
    1. How do i test to see if the transformer is in good working condition?
    2. Can this transformer (marking 13-0-13) be used to replace the melted transformer on the DC power supply?
    Hope you guys understand what i was asking. My intention is...
    11-03-2022, 02:11 AM
  • ttmi100x
    HANNSG Hi221 -- 2 secs to black feat. CCFL flicker & "burn" marks on power board
    by ttmi100x
    Greetings everyone,


    I have a HANNSG Hi221 monitor that exhibits two seconds to black issues (backlight goes off, display is still on as confirmed by shining a flashlight on it) with some additional oddities...


    The monitor failed on me with a standard "2 seconds to black" some time ago prompting me to initially replace most of the electrolytic capacitors (some of them were bulging/leaking).
    Things kinda sorta worked for a night, then the problem returned along with some flickering and "buzzing" noises.

    Upon closer inspection...
    07-31-2024, 06:36 PM
  • angelos
    Technics Transformer question.
    by angelos
    Hi there,
    I have this CD player from a Technics Component unit whose mains transformer is blown. The primary winding is open circuit. This transformer has many secondary windings on its secondary side. This transformer is obviously obsolete.
    I need to know if my trick for a alternative transformer will work. Please check the attachment for explanation.
    I want to use three separate transformers to be equivalent like the original transformer.
    The only thing a bit dodgy is the connection of the 9.6V and 12V outputs of which there is a interconnection between the two windings....
    09-14-2022, 02:14 AM
  • Loading...
  • No more items.
Working...