    Running temp in open air is 27.5C to the touch (the part that is iron), ambient temp is a 15.9
    this thing as always ram warm, not sure if it has a bad component or is designed that way, you can imaging how hot it gets when the unit is closed
    I know the APC units do not run close to this warm
    the battery is cool to the touch, UPC is running on mains power
    I was not sure if i needed a load on the system, so i hooked up my heated blanket, needless to say that made the cat happy
    Attached Files
  • petehall347
    Badcaps Legend
    • Jan 2015
    • 4428
    • United Kingdom

    #2
    Re: Transformer in UPS runs warm for no apparent reason

    how much current is the battery drawing ?

    Comment

    • evilkitty
      Badcaps Veteran
      • Nov 2017
      • 299
      • USA

      #3
      Re: Transformer in UPS runs warm for no apparent reason

      my clamp on meter shows 0.8A on the large red wire, 0.7A on the black wire (0.6 if i flip it around on the black wire)
      may be worth noting this meter read 0.3A just sitting all by it self
      *my other meter needs fuses (on order)
      Last edited by evilkitty; 01-05-2018, 05:10 PM.

      Comment

      • momaka
        master hoarder
        • May 2008
        • 12175
        • Bulgaria

        #4
        Re: Transformer in UPS runs warm for no apparent reason

        30C doesn't seem that hot, even with 16C ambient. Your transformer will always draw a few Watts for itself, even when not loaded.

        I have a pair of computer speakers whose transformer runs so hot that you can't even touch it (over 60C). This is regardless if the speakers are used or not, and with an average ambient temperature in my home at around 22-24C.

        Most Class B -rated transformers are rated for up to 120 or 130C case temperature, if I remember correctly. So 30C really is nothing.

        Nice cat, by the way! Always useful to have a pair of helping hands (or paws) around.
        Last edited by momaka; 01-05-2018, 05:39 PM.

        Comment

        • ben7
          Capaholic
          • Jan 2011
          • 4059
          • USA

          #5
          Re: Transformer in UPS runs warm for no apparent reason

          That sounds normal to me. It's normal for a transformer to be warm even when unloaded, due to the "eddy current" losses in the iron core.

          This is why environmentalists don't like iron-core transformer (mains frequency transformers) based power bricks, because the standby power draw is higher compared to that of a switch-mode power supply.

          My guess is that the transformer is staying energized by the mains input in order to provide power to charge the battery.

          -Ben
          Muh-soggy-knee

          Comment

          • budm
            Badcaps Legend
            • Feb 2010
            • 40746
            • USA

            #6
            Re: Transformer in UPS runs warm for no apparent reason

            You have DC Clamp on amp meter?
            "Running temp in open air is 27.5C to the touch (the part that is iron), ambient temp is a 15.9" Do mean that is the temperature during running on batteries mode WITH LOAD? That is only about 15 deg rise.

            "my clamp on meter shows 0.8A on the large red wire, 0.7A on the black wire (0.6 if i flip it around on the black wire)" How much load is that on the batteries backup AC outlet? The get the power from 12V batteries and convert it to 120VAC, it will draws a lot more than 0.8A.
            Last edited by budm; 01-05-2018, 05:45 PM.
            Never stop learning
            Basic LCD TV and Monitor troubleshooting guides.
            http://www.badcaps.net/forum/showthr...956#post305956

            Voltage Regulator (LDO) testing:
            http://www.badcaps.net/forum/showthr...999#post300999

            Inverter testing using old CFL:
            http://www.badcaps.net/forum/showthr...er+testing+cfl

            Tear down pictures : Hit the ">" Show Albums and stories" on the left side
            http://s807.photobucket.com/user/budm/library/

            TV Factory reset codes listing:
            http://www.badcaps.net/forum/showthread.php?t=24809

            Comment

            • evilkitty
              Badcaps Veteran
              • Nov 2017
              • 299
              • USA

              #7
              Re: Transformer in UPS runs warm for no apparent reason

              Yep my camp on has AC and DC support, lowest setting is 40A, southwire 21050T
              the AC load was about 65W (based on device setting and wattage label)
              temp reads are when running on mains, heat is expected when running off battery and it makes far more than that
              Last edited by evilkitty; 01-05-2018, 06:00 PM.

              Comment

              • evilkitty
                Badcaps Veteran
                • Nov 2017
                • 299
                • USA

                #8
                Re: Transformer in UPS runs warm for no apparent reason

                Originally posted by momaka
                30C doesn't seem that hot, even with 16C ambient. Your transformer will always draw a few Watts for itself, even when not loaded.

                I have a pair of computer speakers whose transformer runs so hot that you can't even touch it (over 60C). This is regardless if the speakers are used or not, and with an average ambient temperature in my home at around 22-24C.

                Most Class B -rated transformers are rated for up to 120 or 130C case temperature, if I remember correctly. So 30C really is nothing.

                Nice cat, by the way! Always useful to have a pair of helping hands (or paws) around.
                120C that will kill the caps!!!


                this UPC also has a input voltage meter on it, it shows alot more fluctuation than any meter i have, anywhere from 105 to 126

                Comment

                • budm
                  Badcaps Legend
                  • Feb 2010
                  • 40746
                  • USA

                  #9
                  Re: Transformer in UPS runs warm for no apparent reason

                  Originally posted by evilkitty
                  Yep my camp on has AC and DC support, lowest setting is 40A, southwire 21050T
                  the AC load was about 65W (based on device setting and wattage label)
                  temp reads are when running on mains, heat is expected when running off battery and it makes far more than that
                  At 120VAC 65W load, if the batteries is 12V system then the current draw from batteries will be more than 5A. I cannot tell form the pictures as to how many 12V batteries are being used.
                  http://office.manualsonline.com/manu...000ub.html?p=2
                  Last edited by budm; 01-05-2018, 06:26 PM.
                  Never stop learning
                  Basic LCD TV and Monitor troubleshooting guides.
                  http://www.badcaps.net/forum/showthr...956#post305956

                  Voltage Regulator (LDO) testing:
                  http://www.badcaps.net/forum/showthr...999#post300999

                  Inverter testing using old CFL:
                  http://www.badcaps.net/forum/showthr...er+testing+cfl

                  Tear down pictures : Hit the ">" Show Albums and stories" on the left side
                  http://s807.photobucket.com/user/budm/library/

                  TV Factory reset codes listing:
                  http://www.badcaps.net/forum/showthread.php?t=24809

                  Comment

                  • evilkitty
                    Badcaps Veteran
                    • Nov 2017
                    • 299
                    • USA

                    #10
                    Re: Transformer in UPS runs warm for no apparent reason

                    The Single battery is NOT UNDER LOAD, the unit is running on AC input, not DC output
                    in other words IF the battery needed charging the unit SHOULD be charging the battery not discharging it
                    i thought i made that clear in the original post, but hopefully this will clear that up
                    Last edited by evilkitty; 01-05-2018, 06:34 PM.

                    Comment

                    • budm
                      Badcaps Legend
                      • Feb 2010
                      • 40746
                      • USA

                      #11
                      Re: Transformer in UPS runs warm for no apparent reason

                      So the 65W load is NOT in UPS mode then, that is an interactive UPS so the load is basically connected directly to the incoming AC through the tap switching of that power transformer (also for charging the battery) to do simple AC out regulation when it is not in battery mode.
                      You need to use REL button to ZERO out your meter before making the current measurement.
                      The really verify the temp rise you will have to be in battery mode with full load which per spec, it will only run for about 3 minutes so the the temp rise will not be that fast to get to 120c (doubted that), the battery will run down by then.
                      Last edited by budm; 01-05-2018, 07:08 PM.
                      Never stop learning
                      Basic LCD TV and Monitor troubleshooting guides.
                      http://www.badcaps.net/forum/showthr...956#post305956

                      Voltage Regulator (LDO) testing:
                      http://www.badcaps.net/forum/showthr...999#post300999

                      Inverter testing using old CFL:
                      http://www.badcaps.net/forum/showthr...er+testing+cfl

                      Tear down pictures : Hit the ">" Show Albums and stories" on the left side
                      http://s807.photobucket.com/user/budm/library/

                      TV Factory reset codes listing:
                      http://www.badcaps.net/forum/showthread.php?t=24809

                      Comment

                      • petehall347
                        Badcaps Legend
                        • Jan 2015
                        • 4428
                        • United Kingdom

                        #12
                        Re: Transformer in UPS runs warm for no apparent reason

                        on AC the battery is charging .
                        is there a min max setting for input voltage ?

                        Comment

                        • evilkitty
                          Badcaps Veteran
                          • Nov 2017
                          • 299
                          • USA

                          #13
                          Re: Transformer in UPS runs warm for no apparent reason

                          You mean a tolerance, sure
                          multimeter shows my mains at 116.5v variation of +0.1
                          battery is getting 13.5v

                          Comment

                          • evilkitty
                            Badcaps Veteran
                            • Nov 2017
                            • 299
                            • USA

                            #14
                            Re: Transformer in UPS runs warm for no apparent reason

                            With it in the case the air temp in the case is about 50C, this is just running off mains at with no AC load

                            Comment

                            • redwire
                              Badcaps Legend
                              • Dec 2010
                              • 3912
                              • Canada

                              #15
                              Re: Transformer in UPS runs warm for no apparent reason

                              I find these low cost UPS just run really warm when doing nothing. Then the batteries don't last, due to the heat and high charging voltage for the warmer battery.

                              The transformer design is low cost with high flux density near saturation, so the core runs hot. Especially if your mains voltage is high >120VAC. It may have a shorted turn though.

                              The only other time I've seen these run hot and cook is if there is a shorted cell in the battery, it goes full tilt charging a 10V battery.


                              WINSSON ZHONGAING Transformer 62-1256 Tripp-Lite G1000UB UPS
                              Guy rips apart similar Winsson 62-1225 teardown

                              Comment

                              • Curious.George
                                Badcaps Legend
                                • Nov 2011
                                • 2305
                                • Unknown

                                #16
                                Re: Transformer in UPS runs warm for no apparent reason

                                Originally posted by evilkitty
                                With it in the case the air temp in the case is about 50C, this is just running off mains at with no AC load
                                Put a 10W light bulb in a similar case and I bet you find a similar rise in temperature!

                                Most consumer UPS's play the role of "toilet paper dispensers" in that toilet paper dispensers are generally cheaply made (to keep sell price low) and designed primarily to sell toilet paper (batteries, in the case of UPS's).

                                Amusingly, the commercial kit isn't that much better -- possibly because the IT departments have "battery budgets" and you can always play on their fear of a battery failing when it is most needed (so best err on the side of replacement!)

                                Comment

                                • momaka
                                  master hoarder
                                  • May 2008
                                  • 12175
                                  • Bulgaria

                                  #17
                                  Re: Transformer in UPS runs warm for no apparent reason

                                  Originally posted by Curious.George
                                  Put a 10W light bulb in a similar case and I bet you find a similar rise in temperature!

                                  Most consumer UPS's play the role of "toilet paper dispensers" in that toilet paper dispensers are generally cheaply made (to keep sell price low) and designed primarily to sell toilet paper (batteries, in the case of UPS's).
                                  Exactly.
                                  Although, I do want to explicitly mention that not all toilet paper dispensers are cheap. If you go to a "boutique"/home furniture store, you may find some really really expensive TP dispensers... like $40+ for a piece of stainless-steel rod with a funky shape.

                                  Originally posted by ben7
                                  This is why environmentalists don't like iron-core transformer (mains frequency transformers) based power bricks, because the standby power draw is higher compared to that of a switch-mode power supply.
                                  For a well-designed transformer, it's not that high. But still likely to be more than 10 times that of a SMPS.

                                  What I like about iron-core transformers is they don't introduce any EMI/RFI and distortion on the mains. Also, being inductive in nature, they may offset some of the poor capacitative PF from smaller switch-mode power adapters/chargers.

                                  Comment

                                  • Curious.George
                                    Badcaps Legend
                                    • Nov 2011
                                    • 2305
                                    • Unknown

                                    #18
                                    Re: Transformer in UPS runs warm for no apparent reason

                                    Originally posted by momaka
                                    Exactly.
                                    Although, I do want to explicitly mention that not all toilet paper dispensers are cheap. If you go to a "boutique"/home furniture store, you may find some really really expensive TP dispensers... like $40+ for a piece of stainless-steel rod with a funky shape.
                                    I designed a piece of medical (lab) equipment many years ago. Did my best to drive the product cost down to the lowest practical -- about $300 IIRC.

                                    Customer "sold" the device for $6,000/each!

                                    But, in practice, never collected any money for any of those sales -- instead, they were "toilet paper dispenser" designed to sell the "consumables" related to their use. By pricing it so high, THEIR customers thought they were getting a deal!

                                    Comment

                                    Related Topics

                                    Collapse

                                    • ahmedtou
                                      HOW CAN I UPDATE HL-DT-ST BD-RE GGW-H20N XA02
                                      by ahmedtou
                                      Hi everyone,
                                      help me please


                                      I have an HL-DT-ST BD-RE GGW-H20N with ROM version: XA02.




                                      When I tried to burn a 25GB Blu-ray disc using ImgBurn, I got an error.
                                      I will share all the details with you, including the disc information.




                                      Code:
                                      HL-DT-ST BD-RE  GGW-H20N XA02 (ATA)
                                      Current Profile: BD-R
                                      
                                      Disc Information:
                                      Status: Empty
                                      State of Last Session: Empty
                                      Erasable: No
                                      Free Sectors: 12,219,392
                                      Free Space: 25,025,314,816 bytes
                                      Free Time: 2715:27:17 (MM:SS:FF)
                                      Next
                                      ...
                                      08-27-2025, 08:49 AM
                                    • ohren
                                      Original Xbox 1.0 PSU: Foxlink FTPS-0002 Rev. B. — 12 V low, 5 V high — transformer?
                                      by ohren
                                      Hello!

                                      I'm looking at an original Xbox PSU: Foxlink ftps-0002 rev. B. The 12 V output is too low, and the 5 V output is too (?) high. Unfortunately I don't have an oscilloscope but only a DMM for diagnosis.

                                      Measured voltages with no load:

                                      After rectifier diodes
                                      12V: 6.17 V
                                      5V: 5.67 V

                                      Secondary transformer pins AC measurement (really don't know if this says anything)
                                      12V: 2-2.5 V
                                      5V: 1.04 V


                                      I also have another (working) Xbox psu from Delta. The same measures there, in order, being: 10.79,...
                                      03-18-2023, 10:33 AM
                                    • mikey5791
                                      Is it possible for transformer substitution?
                                      by mikey5791
                                      Hi all,
                                      Got this local made DC power supply (12/14V) given free as the transformer has melted. There is no marking or indication to identify what type or rating of transformer used.
                                      Fyi,. I had a busted autogate mainboard with transformer with marking 13-0-13 . Is this the 13v dc type transformer?
                                      My questions are
                                      1. How do i test to see if the transformer is in good working condition?
                                      2. Can this transformer (marking 13-0-13) be used to replace the melted transformer on the DC power supply?
                                      Hope you guys understand what i was asking. My intention is...
                                      11-03-2022, 02:11 AM
                                    • dennis_elx33
                                      3PHASE STEP-DOWN Transformer in Check
                                      by dennis_elx33
                                      Hello All,

                                      i would like to post an interesting topic regarding 3-phase stepdown transformer which we suspect to cause an overcurrent (138A) which resulted to power tripped off of the HV power supply (80KV output).


                                      Problem statement: Power tripped Off

                                      Initial Problem: Found 2 IGBT and 2 rectifier diodes shorted (burnt).

                                      Action Done:
                                      1) Replaced the faulty parts with good spare.
                                      2) Measured impedance of the 3phase input lines and found that L2 to L3 has 23.3ohm while other pairs are 51Kohm. This pins will...
                                      12-02-2024, 06:52 AM
                                    • Document Archive
                                      ASUS Transformer T101HA - X5DHD Hybrid (2-in-1) Book Specification for Upgrade or Repair
                                      by Document Archive
                                      This specification for the ASUS Transformer T101HA - X5DHD Hybrid (2-in-1) can be useful for upgrading or repairing a laptop that is not working. As a community we are working through our specifications to add valuable data like the T101HA - X5DHD boardview and T101HA - X5DHD schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant badcaps forum. Please note that we offer no warranties that any specification, datasheet,...