A Central Air Heating Element, A PID and a Sauna
  • JayPoorJay
    • Jan 2022
    • 149
    Originally posted by diif
    Obviously there is heat loss when you open the door but due to your pressure idea, it all comes out all at once. Forcing air in is a waste of time and energy.
    "All"? How much air "pressure" do you think we are talking here? So, the reason for this isn't only the pre-heat, it's also the recovery too, after opening the door... I hear you though...
    • JayPoorJay
      • Jan 2022
      • 149
      You need to be careful about using the wrong type of “thermostat (capillary bulb style) is necessary and controls the on off”
      Two reasons one is the contacts of the switch part that can handle the current the other concern is the temperature range of the device plus and the dead zone of the thermostat sensitivity to temperature change these are different do not think that they are the same because they are not
      You could probably go with a digital thermostat however you will need to experiment with the temperature on and temperature off and the dead band to keep the system from short cycling which is a detrimental effect on mechanical switch type of contacts
      Now you use a sold state relay instead of a mechanical switch type but you still need to have a dead band where you have no ON/OFF state because even if it is digital type of switch you can still overheat the module even if you have a heat sink on it
      Now this would require a PID controller to have the best possible result you could possibly do it with out a PID controller but you would have to have the right type of temperature controller that can handle the current rating of the heater unit but if you are using this type you need to know the amount of dead band the temperature controller you plan on using not all of them are the same the best ones are the ones that you can set the ON temperature and you can set the OFF temperature of the heater unit this is the best type to use now some of them have what temperature off set which a predetermined difference between ON and OFF which still can be used but make sure that you have at least 20 degrees difference at a minimum for best results
      Now they do make thermostats switches that can adjust the dead band to certain extent but this type of thermostats are more accurate and more expensive to buy that is the reason the thermostat that is recommended is more expensive than a general use thermostat type switch is
      Here is something that I found on EBay that you might be interested in a non working heater unit
      https://www.ebay.com/itm/40453572545...Bk9SR9SMiOGmYw
      Ebay search “electric sauna heater 120 not working”
      I plan on one of these... But thanks. I'm just waiting for them to restock...
      https://m.vevor.com/sauna-heater-sto...28#goodsDetail
      Do you have a specific suggestion for the/a thermostat? That would help. I don't understand them very well. Are they just on off with 120v feed, depending on temperature?
      • JayPoorJay
        • Jan 2022
        • 149
        Maybe I just need to spend the $100 dollars and get the one that is original to the temperature/sauna control panel that I have coming? At the same time I cant imagine that a thermostat would react to very small changes in temp regularly to the point that it would cook itself or wear itself out...? More research.
        The thing i like most about doing alllllll kinds of DIY projects is the learning curve and all of the things that need to be figured out. The availability of so many devices (amazon) is pretty amazing, I must say. As much, the internet and all of the information that is at the tip of ones fingers...
        • diif
          • Feb 2014
          • 6978
          • England
          #44
          The fan you are proposing is 160 CFM, it's on from the start of heating up the sauna. There will only be so much pressure the sauna can take before the fan stops working.
          • JayPoorJay
            • Jan 2022
            • 149
            The new and improved wiring diagram,,,
            Thanks to the guys at Sauna360...
            Pg 9. The 1202-1-18 unit...
            Looks like the "contactor" (I was wondering about that) is built into the controller itself (unless I'm mistaken) which is good...
            I am a little confused about how and which wires will be run to the individual elements. I think I understand the load connections,,, but am uncertain about the the line back. Anyways, I'm a ways away from that stage.
            My elements are 2100watts each 😬
            • JayPoorJay
              • Jan 2022
              • 149
              Is it possible that this entire controller can function on one neutral wire for the heaters AND the light? I just don't understand where the neutral wire back from the elements wires in...or even comes from... headaches...
                • Jul 2011
                • 6070
                Originally posted by JayPoorJay View Post
                Could this be my guy?
                https://a.co/d/ab3gAph
                Here is the data sheet for the temperature switch
                https://parts.rheem.com/product/RPD-47-22861-01
                You are not doing your homework for devices that you are thinking about using
                https://www.vevor.com/sauna-heater-s...28#goodsDetail
                This is part of the description of the device did you miss this part
                • Adjust the Temp and Time: The home sauna heater features user-friendly mechanical knobs for temperature and time control, providing you the flexibility to personalize your sauna experience based on your comfort. With a maximum temperature of 230℉ and a timing capability of up to 3 hours, you have full control over your sauna session.
                This is not a good match at all not even for a maximum temperature thermo runaway situation you are asking for trouble without even knowing about this is not a good situation to be in
                I do not mean to come across rude but you need to read data sheets and understand what the information is telling you about the device that you are considering using do not assume anything when you do a proof of concept getting into bad habits for your first project is not a good way to start trust about this
                Me personally I think about doing a modification project that I do not know much about and I have been looking at data sheets and not really finding good matches jet so making progress is going to be very slow at best and at this point I not sure if it is worth going down this rabbit hole and it might be that I can not find all of the information at this point so not being able to completely understand how this device should work might keep me from doing this project
                  • Jul 2011
                  • 6070
                  See here is another example of the fact that what you do not realize is that this system has 3 120 volt circuits that should not be on the same breaker because of the amp draw that it has
                  To answer your other question as long as you only use one 120 volt circuit yes you can it is not a good practice to for more than one circuit
                  But to answer your question the contactor coil is 120 volts or 24 volts depending how what control voltage that decided to use
                  • JayPoorJay
                    • Jan 2022
                    • 149
                    Good Morning! Thanks Sam.
                    So what I discovered is that there is NO neutral to the heating elements. Each element leg (3 of them) gets 120v for a total of of 240 +/- in each of the 3. I was confused and then talked with a electrician at work who cleared things up for me. That N on the board is for the 120v light circuit only, on a separate line, and that is it.
                    My controller is the 1202-1-18 model/design. See manual.
                    Thru the controller, three element legs will get its 120v from the T1 connection, 3 will get 120v from the T2 connection.
                    I will be working with (see page 9 of the manual) the 1 phase layout. L3 and T3 are not used... Power input from the panel into L1 and L2, out to the coils on T1 and T2. It is a residential home and I don't have 3 phase capability.
                    Now I have to figure out my limiters...and how to place them in the circuit. See page 6 of the manual...
                    Have a good day
                      • Jul 2011
                      • 6070
                      Have a good day
                      Please post a website link to the manual that you are using so we are on the same exact page and we can get the same information together
                      • JayPoorJay
                        • Jan 2022
                        • 149
                        I got this from the company. It's an attachment. It was included in post 45...
                          • Jul 2011
                          • 6070
                          One thing I do not like about this manual is that it does not have how you hook up the three heater element are they jumpers plate or are they jumpers wires with eyelet terminals to the wire terminals because you are making the three heater elements in a parallel circuit configuration which 3 heater elements @ 7 amps each for a total of 21 amp current load
                          One note if your wiring runs are more than 100 feet go to the next wire gauge for best results because you do not want to have a high voltage drop to the system this is my personal opinion and what I go by when doing wiring up a device to a breaker panel
                          The circuit for light fixture does not need to go to the next wire gauge even if the run is more than 100 feet because your wattage is only 60 watt please make sure that you use a moisture tight light fixture for this space
                          One thing that is going to be very important thing to do is that you make all your connections to the heater elements are tight and the wires are not over tight enough to strip the thread out of the nuts of the connector board or connector block probably made out of Bakelite material if your connections are not tight enough you will destroy the terminal plate connectors and probably not replaceable so make sure that they are tight enough
                          Make sure that you use a GFCI type breaker for your sauna system for your safety yes they are more expensive than a conventional breaker but because having steam in this space I would recommend using this type of breaker
                          I just realized that the way that this system is setup is that one heater element is always on and the other two heater elements are going through the limiter which is interesting concept to do it this way so I am assuming that when the temperature is close to desired temperature it goes down to one heater element it is possible that this device has a two stage thermostat switch this not a common thermostat it is probably a special type of thermostat
                          The reason I know this is because of diagram number 5 shows how the control system and main system are connected to each other one note the contactor coil is 240 volts which is a little unusual for a control circuit to be using this voltage generally speaking it is 24 volts DC or AC sometimes it can be 120 volts AC
                          Also pay close attention to page number 14 and follow it very closely for best results how to construct the sauna room
                          Where you are planning on putting the sauna device that you put the studs in the wall to support it and plan ahead and accordingly so you do not have to redo a section because of poor planning this is not where you want to take shortcuts if you do you will regret it later trust me with this
                          We might be considering buying one but I not sure that I want to tackle this project myself because one I do not have the time to devote to it to make sure that this project is done correctly and properly this is the reason I have taken an interest in what you are planning on doing your self but when I hire someone or a company to come out to do this project I am going to have them explain exactly how and what they are going to do and if I have any questions or concerns about what and how they are going to do this I will speak up and if they have an issue with this then they are not the company that I will use
                          Now if I can find this in a kit form I might consider doing it myself but it will depend on how much more money it would to have it professional done versus getting it kit form and weather or not it worth the the extra money or not
                          • JayPoorJay
                            • Jan 2022
                            • 149
                            Great information! Thank you Sam.
                            Wire runs will not be more than 4ft.
                            Most likely, less than...
                            There will be NO steam or water near this set up. But there will be GFCI breakers/terminals used. If possible
                            If you would, from this ED,,, can you please provide an example of a limiter switch that can control the system, switching from 3 to 1 element(s)? I don't know what that is...
                            I appreciate your help (and warnings) with all this.
                              • Jul 2011
                              • 6070
                              Unfortunately the manual does not say anything about it so I am not sure exactly what type of device it is maybe someone on this forum might have an idea about what type of device this is
                              • JayPoorJay
                                • Jan 2022
                                • 149
                                Good Morning All...
                                Just to say, I got this thing working and working well. I built the fire brick chimney, got a nice fab'd shroud to direct air flow, a nice 36 inch grill/grate for inside the sauna and a surprisingly nice vevor fan to push air thru... And it works. Max temps I see coming out of the vent (without ceramic insulation on the ducting) is about 250F with fan running in medium... I'll be come forward with some pictures shortly.
                                Q: I want/need the fan to run WHENEVER the system is on. I have the relay you see and the wiring diagram (I'll attach a picture) and I am having trouble figuring out how to wire the coil side of the relay to trigger it when the power comes on. Can I just put the coil side in one of T1 or T2 circuits. That way when the elements are getting power, the relay will be triggered?
                                Help please.
ID:	3534746 Click image for larger version
Name:	Screenshot_20241224-100015_Microsoft 365 (Office).jpg
ID:	3534745 Click image for larger version
Name:	Screenshot_20241224-100043_Microsoft 365 (Office).jpg
                                • EasyGoing1
                                  The best way to drive a heating element?
                                  by EasyGoing1
                                  I've got this circuit that I've been playing with on a breadboard. I'm not happy with it mainly because the MOSFET gets too hot and generally controlling the temp of the heating element with the Arduino has proven to be a little more cumbersome than I would like.
                                  What I would like to know, is what is the best way to set up a circuit like this? The heating element is just a PCB and its going to be mounted under a 3D-printed enclosure that a lizard will use to warm his belly.
                                  This is the general setup that I have now.
                                  This is what the...
                                  01-25-2023, 11:29 AM
                                  Surface Mount Fuses Fundamentals Datasheet
                                  TE Circuit Protection offers the widest selection of surface-mount fuses available for addressing a broad range of overcurrent protection applications. Helping to prevent costly damage and promote a safe environment for electronic and electrical equipment, our single-use chip fuses provide performance stability to support applications with current ratings from .5A up to 20A.
                                  TE Circuit Protection also offers the telecom FT600 fuse for telecommunications applications. This telecom fuse helps comply with North American overcurrent protection requirements, including Telcordia, GR-1089,...
                                  10-07-2024, 06:07 AM
                                • bohaboha
                                  Queen coffee CQ MN-2 Heating element
                                  by bohaboha
                                  How to test this queen coffee maker heating element...
                                  07-18-2022, 09:01 PM
                                • dominik0801
                                  IR6500 problems, any tips?
                                  by dominik0801
                                  Hello everyone.
                                  Recently I bought the LY IR6500 machine, since I want to get into BGA rework to expand my business.
                                  I know it's a cheap machine to others, it was expensive to me, and I expected more.
                                  I have already removed the bottom heater glass, as others mentioned, and it helped a bit..
                                  But I have quite lot of problems with it so far.
                                  First of all, the default patterns are all garbage, too fast, all the boards got popcorned when I first tried to desolder BGA packages, even when I followed every step and instructions...
                                  03-31-2021, 02:24 PM
                                • CapLeaker
                                  AcuRite 5 in 1 temperature sensor replacement repair
                                  by CapLeaker
                                  Got a new victim:
                                  AcuRite 5 in 1 Iris outdoor weather station not updating the temperature / humidity anymore. The original sensor is a SHT21. Also there are identical other sensor manufacturers. I chose the HTU21D to replace the original SHT21. Both have identical specs. I've had two failure modes with these sensors.
                                  A: outside temp stuck at -40? It's cold here at times in Canada, but not that cold!
                                  B: stuck at some temperature and maybe updating once in 12 hrs or so.
                                  Easy solution is to go to AcuRite website and purchase the sensor. Right?...
                                  04-15-2025, 01:32 PM
