    APC Back-UPS Pro BP1000I Issue.

    Hi there.

    I'm trying to troubleshoot an APC Back-UPS Pro 1000VA BP1000I that is not working correctly and I don't know where to start.

    If I turn it on without load it will start ok and switch to battery without issue, but if I put loads on it it will start beeping and the overload led will turn on despite the load being not even close the the maximum load this UPS can support. (I will try to access the maximum load it will withstand without overloading)

    This is a fairly old UPS, but I know it is good quality and it is better that most newer ones, specially the cheap ones.

    Any ideas where I should start troubleshooting this problem?

    Cheers.

    #2
    Re: APC Back-UPS Pro BP1000I Issue.

    check battery first

    Comment


      #3
      Re: APC Back-UPS Pro BP1000I Issue.

      They tend to do this when battery has high internal resistance. It will show you good voltage but won't have any grunt behind it.

      Comment


        #4
        Re: APC Back-UPS Pro BP1000I Issue.

        Always check battery with load, open (no load) Voltage may show good on the meter but it does not mean if the battery is good.
        Never stop learning
        Basic LCD TV and Monitor troubleshooting guides.
        http://www.badcaps.net/forum/showthr...956#post305956

        Voltage Regulator (LDO) testing:
        http://www.badcaps.net/forum/showthr...999#post300999

        Inverter testing using old CFL:
        http://www.badcaps.net/forum/showthr...er+testing+cfl

        Tear down pictures : Hit the ">" Show Albums and stories" on the left side
        http://s807.photobucket.com/user/budm/library/

        TV Factory reset codes listing:
        http://www.badcaps.net/forum/showthread.php?t=24809

        Comment

        Working...
        X