    Cyberpower BNT-600AP UPS

    Hello everybody.
    I have very interesting issue. Six months ago I have replaced battery in Cyberpower BNT-600AP UPS and everything was working OK. Few days ago i noticed that UPS won't hold when is switched to battery mode.
    What I was noticed that I have open device is that C18 was bad. I have replace it, but i still have same issue..

    I have tested battery, and it is OK. I have used another one with same result. IN the end i used DC power, and with 12V i have exact same behavior as with battery. When i change voltage to 13V, UPS can hold low power device (up to 5W)..

    My understanding is that problem can be related to part who is responsible for checking of battery state.. I'm thinking to replace also LM324N and LM317.

    Did somebody had similar issue? Any opinions about this situation? Thank you..


    #2
    Re: Cyberpower BNT-600AP UPS

    Are you sure that you do not have problems with the micro controller ic chip because the chip you are referring is connected to and it looks like this micro controller ic chip controls the charging function

    I am not sure how you can check and see if the micro controller ic chip is working correctly

    Me personally I do not know if I would spend much time trying to fix it
    Last edited by sam_sam_sam; 08-21-2020, 06:16 PM.
    9 PC LCD Monitor
    6 LCD Flat Screen TV
    30 Desk Top Switching Power Supply
    10 Battery Charger Switching Power Supply for Power Tool
    6 18v Lithium Battery Power Boards for Tool Battery Packs
    1 XBox 360 Switching Power Supply and M Board
    25 Servo Drives 220/460 3 Phase
    6 De-soldering Station Switching Power Supply 1 Power Supply
    1 Dell Mother Board
    15 Computer Power Supply
    1 HP Printer Supply & Control Board * lighting finished it *


    These two repairs where found with a ESR meter...> Temp at 50*F then at 90*F the ESR reading more than 10%

    1 Over Head Crane Current Sensing Board ( VFD Failure Five Years Later )
    2 Hem Saw Computer Stack Board

    All of these had CAPs POOF
    All of the mosfet that are taken out by bad caps

    Comment


      #3
      Re: Cyberpower BNT-600AP UPS

      Do you have the rest of the schematic?
      Without battery connected, what DC Voltage do you have on the Red and Black wires when you plug UPS into the AC outlet?
      Fuse F1 is good?
      What is connected to connector CN2-4, CN2-5?
      Q21 is connected strangely.

      Be careful not to touch the conductors when making the measurement since the charger circuit may not be isolated type.
      Last edited by budm; 08-21-2020, 06:43 PM.
      Never stop learning
      Basic LCD TV and Monitor troubleshooting guides.
      http://www.badcaps.net/forum/showthr...956#post305956

      Voltage Regulator (LDO) testing:
      http://www.badcaps.net/forum/showthr...999#post300999

      Inverter testing using old CFL:
      http://www.badcaps.net/forum/showthr...er+testing+cfl

      Tear down pictures : Hit the ">" Show Albums and stories" on the left side
      http://s807.photobucket.com/user/budm/library/

      TV Factory reset codes listing:
      http://www.badcaps.net/forum/showthread.php?t=24809

      Comment


        #4
        Re: Cyberpower BNT-600AP UPS

        Originally posted by budm View Post
        Do you have the rest of the schematic?
        Without battery connected, what DC Voltage do you have on the Red and Black wires when you plug UPS into the AC outlet?
        Fuse F1 is good?
        What is connected to connector CN2-4, CN2-5?
        Q21 is connected strangely.

        Be careful not to touch the conductors when making the measurement since the charger circuit may not be isolated type.
        1. No. That is all that i have. Except transformer everything else is at schematic.
        2. I have to double-check, but i think that i had 13.7V
        3. Yes. Tested.
        4. I have to check.
        5. Please can you explain in your opinion why is strangely connected?

        Thank you..

        Comment


          #5
          Re: Cyberpower BNT-600AP UPS

          Originally posted by sam_sam_sam View Post
          Are you sure that you do not have problems with the micro controller ic chip because the chip you are referring is connected to and it looks like this micro controller ic chip controls the charging function

          I am not sure how you can check and see if the micro controller ic chip is working correctly

          Me personally I do not know if I would spend much time trying to fix it
          I'm not sure that micro-controller is not issue. At this point i think that reading of battery level are wrong.
          I ordered few components that are in my opinion problematic, and i will check.

          Thank you..