APC UPS units - troubleshooting
Anyone dealt with repairing these units? I have models 300-1400VA and would like to know if some of the models have inherent problems that show up after a few years. As you know APC is in the business to sell units not assist owners/customers in troubleshooting their units except to send it in for repair or refurb. Thought I might post to see if any of the veterans knew enough about these to offer some troubleshooting advice. These seem pretty straight forward in design, just not sure where to look for the faults. Might be a good section to add to the forum since it is a large part of a system these days. Some of these aren't that disposable for the $$. Thought since we got into PSUs so heavily why not take a look at the next step in the supply chain. How 'bout it Willa? Not sure what section to post this so move if necessary. Thanks 
|
|
|
05-06-2006, 12:22 PM
|
#2
|
|
Super Modulator
Join Date: Nov 2003
Location: Αθήνα
Posts: 7,609
|
Re: APC UPS units - troubleshooting
its ok better to keep the thread here.
here's some troubleshooting info
http://www.badcaps.net/forum/showthread.php?t=1611
i havent had any APC units fail though, whats the issue with your units?
|
|
|
05-06-2006, 03:11 PM
|
#3
|
|
Badcaps Veteran
Join Date: Jul 2005
Location: Sweden
Posts: 1,899
|
Re: APC UPS units - troubleshooting
Right today I've been fixing up an APC UPS, it will get it's own thread started because it was allot of work...
Anyway, the issue was simple; it had shorted batteries and was trying to power on in a loop, not very good design security wise because it was shutting AC on and off to the connected equipment...
Anyway this I think is the most common failure of a UPS... Elfa carries all the battery models that you need for a UPS, at more than half the price that APC wants for em...
One thing to remember; the UPS microprocessor will "learn" that the batteries are poor, so when you swap new ones in it might not work, what you do is give the UPS a load of atleast 30% and then create a brownout by cutting AC power (the UPS should still be grounded though!) it will run till the batteries are totally discharged and thereby will learn how good or bad they are... To clarify; the UPS management software should be disabled, a good way to do it is to have your computer idle in the BIOS or something...
|
|
|
05-06-2006, 04:26 PM
|
#4
|
|
Badcaps Veteran
Join Date: Mar 2006
Location: SoCal,USA
Posts: 472
|
Re: APC UPS units - troubleshooting
Quote:
|
Originally Posted by Per Hansson
One thing to remember; the UPS microprocessor will "learn" that the batteries are poor, so when you swap new ones in it might not work, what you do is give the UPS a load of atleast 30% and then create a brownout by cutting AC power (the UPS should still be grounded though!) it will run till the batteries are totally discharged and thereby will learn how good or bad they are... To clarify; the UPS management software should be disabled, a good way to do it is to have your computer idle in the BIOS or something...
|
Interesting. On a lark and to contribute to a thread, I tested a new 1500 Belkin after it charged for 24hours by loading it with a 500W halogen lamp. It supported it for 5.5 minuets. Some further testing was done with lower wattage bulbs to answer questions about flickering. I know that Belkin is a lower end unit but for home it seems to be OK.
The 1200 Belkin that got new batteries was tested the same way and went 4.25 minuets. Both units were shut down via the circuit breaker, not unplugged, so the ground circuit was maintained. Very good point to remember. 
|
|
|
05-07-2006, 02:10 AM
|
#5
|
|
Badcaps Veteran
Join Date: Jul 2005
Location: Sweden
Posts: 1,899
|
Re: APC UPS units - troubleshooting
This battery issue is the same with any device with "intelligent" batteries, like Laptops for example... Some have a calibration tool in the BIOS that does exactly what I described above...
|
|
|
04-20-2007, 04:08 AM
|
#6
|
|
Super Modulator
Join Date: Nov 2003
Location: Αθήνα
Posts: 7,609
|
Re: APC UPS units - troubleshooting
uuuuh.....crap
troubleshoot this then........first set of batteries CSB brand (made in guangzhou) with APC stickers. About 3 years of 24/7 service. The battery drawer is at the front of the unit and the batteries cannot exit because they have all expanded. OK but there is no provision for this situation, the battery compartment is folded steel and riveted.
Only way i see is to bend those folded edges up

Last edited by willawake; 04-20-2007 at 11:47 AM..
|
|
|
04-20-2007, 04:54 AM
|
#7
|
|
Super Modulator
Join Date: Nov 2003
Location: Αθήνα
Posts: 7,609
|
Re: APC UPS units - troubleshooting
yeah this is where computing meets engineering

|
|
|
04-20-2007, 05:50 AM
|
#8
|
|
Super Modulator
Join Date: Nov 2003
Location: Αθήνα
Posts: 7,609
|
Re: APC UPS units - troubleshooting
and we hope it fits in the rack again.....

|
|
|
04-20-2007, 08:19 AM
|
#9
|
|
Badcaps Veteran
Join Date: Jul 2006
Location: Genesee County, Michigan
Posts: 774
|
Re: APC UPS units - troubleshooting
Daaaaaammmmnnnn, those batteries are toasted  I had a Panasonic battery for a Smart-UPS 600 that looked bad , but not that bad!
How good are the Powersonic batteries? I have a stack of UPS units to rebuild. The only ones I really bother with anymore are APC, unless I find a really big one >2500VA.
Quote:
|
Originally Posted by willawake
uuuuh.....crap
troubleshoot this then........first set of batteries CSI brand with APC stickers. About 3 years of 24/7 service. The battery drawer is at the front of the unit and the batteries cannot exit because they have all expanded. OK but there is no provision for this situation, the battery compartment is folded steel and riveted.
Only way i see is to bend those folded edges up 
|
Last edited by willawake; 04-20-2007 at 12:35 PM..
Reason: remove pics from quote
|
|
|
04-20-2007, 08:36 AM
|
#10
|
|
Badcaps Veteran
Join Date: Jul 2005
Location: Sweden
Posts: 1,899
|
Re: APC UPS units - troubleshooting
Wow Willa, that's some bad failure!
I don't ever think I made a thread about that APC I was talking about above but one of it's batteries where also in pretty bad shape, not like that tho...
Intelligent UPS my ass
|
|
|
04-20-2007, 11:44 AM
|
#11
|
|
Super Modulator
Join Date: Nov 2003
Location: Αθήνα
Posts: 7,609
|
Re: APC UPS units - troubleshooting
Quote:
|
How good are the Powersonic batteries?
|
they do similar failures but there is not much choice here. I have come to the conclusion that everything is crap nowadays anyway.
mine too. yesterday there was a smell in the server room which i could not locate (i think we know what that was now) and only today the battery alarm was sounding.......the casing was very hot.  how about a case temperature sensor APC?????
Last edited by willawake; 04-20-2007 at 11:49 AM..
|
|
|
04-20-2007, 12:21 PM
|
#12
|
|
Badcaps Veteran
Join Date: Jul 2006
Location: Genesee County, Michigan
Posts: 774
|
Re: APC UPS units - troubleshooting
But as stupid as it is to not have some safety features, I think I'd still take an APC over another type of UPS. Usually the batteries are all that I ever need to replace in them.
|
|
|
04-20-2007, 12:42 PM
|
#13
|
|
Super Modulator
Join Date: Nov 2003
Location: Αθήνα
Posts: 7,609
|
Re: APC UPS units - troubleshooting
Quote:
|
I had a Panasonic battery for a Smart-UPS 600 that looked bad
|
some powersonic i replaced in another smart-ups
http://www.badcaps.net/forum/showthread.php?t=2752
|
|
|
04-20-2007, 12:55 PM
|
#14
|
|
Badcaps Veteran
Join Date: Jul 2006
Location: Genesee County, Michigan
Posts: 774
|
Re: APC UPS units - troubleshooting
I think Yausa is pretty good also, but didn't they get bought out?
|
|
|
04-20-2007, 01:05 PM
|
#15
|
|
Super Modulator
Join Date: Nov 2003
Location: Αθήνα
Posts: 7,609
|
Re: APC UPS units - troubleshooting
i saw some new batteries in the shop (smaller ones) which looked like the fujistu logo but said fuji(something) cant seem to locate it on the internet on the fujitsu site. i wouldnt be surprised if they were fujitsu cos they have some fujitsu flashlights in the shop, perfect for the ships. I would like to try some fujitsu batteries.
|
|
|
04-21-2007, 07:06 AM
|
#16
|
|
Badcaps Veteran
Join Date: Aug 2005
Location: Slovakia
Posts: 1,079
|
Re: APC UPS units - troubleshooting
Batteries shouldn't fail like this.
I have an APC SmartUPS v/s 650 where the battery failed three times this way. Now it's on the shelf as I suspect that it overcharges the battery.
I changed dead batteries in old (maybe 1994) BackUPS 600 (non-user-replaceable batteries - I had to completely disassemble it) at work. The batteries (two 6V in series) had no bulging at all, just increased internal resistance - I think this is the way they should fail because of age.
|
|
|
04-21-2007, 08:26 AM
|
#17
|
|
Super Modulator
Join Date: Nov 2003
Location: Αθήνα
Posts: 7,609
|
Re: APC UPS units - troubleshooting
Quote:
|
have an APC SmartUPS v/s 650 where the battery failed three times this way
|
now its getting interesting. who else has a smartups where the batteries failed this way.
personally i have only seen bulging in smartups.
in other ups have seen failed batteries which were hot but with no bulging and one time i saw one powersonic leaking from a terminal. but otherwise just batteries not holding a charge and no other signs.
|
|
|
04-21-2007, 12:59 PM
|
#18
|
|
Badcaps Veteran
Join Date: Jul 2005
Location: Sweden
Posts: 1,899
|
Re: APC UPS units - troubleshooting
willa; in the thread you linked above
One of the batteries had cracked open, nothing bad though. The UPS was still running fine, just 0 seconds runtime of course...
This was the Italan Riello 6kW UPS...
|
|
|
04-22-2007, 11:22 AM
|
#19
|
|
Super Modulator
Join Date: Nov 2003
Location: Αθήνα
Posts: 7,609
|
Re: APC UPS units - troubleshooting
Quote:
willa; in the thread you linked above
One of the batteries had cracked open, nothing bad though. The UPS was still running fine, just 0 seconds runtime of course...
This was the Italan Riello 6kW UPS...
|
lower down in the thread i posted a cracked battery from a smart-ups.
I checked the other UPS today, same model and the batteries are showing some bulging, not as bad as the first though. i will replace those tomorrow as well.
heres a pic of the batts before i dispose of them in a (cough) environmental way.

|
|
|
04-22-2007, 11:29 AM
|
#20
|
|
Super Modulator
Join Date: Nov 2003
Location: Αθήνα
Posts: 7,609
|
Re: APC UPS units - troubleshooting
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
All times are GMT -6. The time now is 09:37 AM.
|