My neighbor has a HVAC system and the outside unit will not turn on at the thermostat. I can manually push the relay at the outside unit and it will turn on normally, so it's a low voltage problem. There is 24 VDC from the transformer at the thermostat.
My neighbor's nephew is a retired HVAC repairman and he came by and condemn the thermostat, but after I (correctly) wired in the new one, the outside unit will still not turn on.
Against the outside wall, next to the unit, is a "J" box where all the low voltage wiring coming out of the house are connected to the low voltage wiring going (3 ft.) to the outside unit, using electrical screw cap connectors. The J-Box is at least 20 years old, has no weatherproofing whatsoever, and we have just had some rain for the first time in about 2 years.
The "professional" HVAC shorted wires at the outside unit and condemned the thermostat, but he never actually verified this AT the thermostat. I think there's an open, or a short, in the low-voltage wiring at this rusted, dirty J-box.
I need to know which two wires to short at the thermostat in order to bypass it, and verify that the outside unit either does, or does not, turn on.
If not, then a check by shorting the same wires at the J-Box should show that the problem is either before or after the J-Box in the wiring.
Transformer(24 VDC)--->---Thermostat--->----J-Box--->----Outside Unit Relay--- Ground
I think the problem is either just before, at, or just after the J-Box.
What two wires do I short to simulate the thermostat turning on?
FYI: According to the Customer Service person at Honeywell's 1-800 number, the thermostat is wired for a AC/Heat Pump with Emergency Heat as a secondary heat source. So there's 1 AC, 2 heat and a selector wire for the heat pump valve.
My neighbor's nephew is a retired HVAC repairman and he came by and condemn the thermostat, but after I (correctly) wired in the new one, the outside unit will still not turn on.
Against the outside wall, next to the unit, is a "J" box where all the low voltage wiring coming out of the house are connected to the low voltage wiring going (3 ft.) to the outside unit, using electrical screw cap connectors. The J-Box is at least 20 years old, has no weatherproofing whatsoever, and we have just had some rain for the first time in about 2 years.
The "professional" HVAC shorted wires at the outside unit and condemned the thermostat, but he never actually verified this AT the thermostat. I think there's an open, or a short, in the low-voltage wiring at this rusted, dirty J-box.
I need to know which two wires to short at the thermostat in order to bypass it, and verify that the outside unit either does, or does not, turn on.
If not, then a check by shorting the same wires at the J-Box should show that the problem is either before or after the J-Box in the wiring.
Transformer(24 VDC)--->---Thermostat--->----J-Box--->----Outside Unit Relay--- Ground
I think the problem is either just before, at, or just after the J-Box.
What two wires do I short to simulate the thermostat turning on?
FYI: According to the Customer Service person at Honeywell's 1-800 number, the thermostat is wired for a AC/Heat Pump with Emergency Heat as a secondary heat source. So there's 1 AC, 2 heat and a selector wire for the heat pump valve.
Comment